Search the Community
Showing results for tags 'output'.
Found 42 results
-
My Powerflex 525 VFD “Output Frequency” starts to drop out (20, 19, 18, 17, 16, 15, 14, 14, 0, 13, 0, 12, 11, 10, 0, 9, etc.) when the Command Frequency approaches and falls below approx. 14HZ. The “Command Frequency” however does hold steady and does not drop out (20, 19, 18, 17, 16, 15 14, 13, 12, 11, 10, 9, etc.). The Pulse In Scale is set to 64. I'm using the Pulse Train Input, and as a test started the frequency of the Pulse Train Input at a frequency such that the Command Frequency started at 20HZ, and then slowly adjusted the frequency of the Pulse Train Input down such that the Command Frequency decreased down towards 0Hz. I did notice that this apparent drop out point is exactly one tenth of the Max Hz value. So for example, with Max Hz set to 140, the dropout starts to occur at approx. 14 (140 x 0.1 = 14). This apparent one tenth drop out point held true for other Max Hz values we tried, including: Max Hz set at 60 started dropping out at 6 Max Hz set at 100 started dropping out at 10 Max Hz set at 140 started dropping out at 14 Max Hz set at 180 started dropping out at 18 Max Hz set at 190 started dropping out at 19 Max Hz set at 200 started dropping out at 20 Max Hz set at 250 started dropping out at 25 Max Hz set at 400 started dropping out at 40
-
Hi, New to the forum and pretty new to PLC programming. I took the 3-day Sysmac training a couple months ago, but just recently set up one of the NX1P2 units that we'll eventually use for a robotics application. Right now I've got it set up just to experiment with, so I have 3 physical switches (1 momentary, the other 2 toggle) and 4 indicator lights hooked up. Ladder program is set up to light up different LED's when the momentary contact switch I_SW1 is pressed, based on the position of the other 2 switches. Here's the issue: When both of the toggle switches are ON (see lines 4 thru 8), all of the LED's light up as expected as soon as the momentary switch I_SW1 is pressed. However, if either or both of the toggle switches are OFF (see lines 0 thru 3), even though it seems like the logic is correct, nothing happens on the output. Lines 0&1 were modified as shown to see if using the variable O_Light1 instead of going directly to O_L1 output would work, but it didn't make any difference. See attached images for example of working and not working ladder sections as the momentary switch is pressed. In the "working" image, both the toggle switches are on. In the "not working" image, both toggle switches are off. PLC's input & output indicator lights match what Sysmac is showing in the monitor screen, so I'm pretty sure it's in the ladder logic and not the physical wiring. Thanks for any advice.
-
Hi I have servo motor controlled by smartstep 2 and controlled by PLC with pulse output. Origin search I have set as below Sometimes I have problem with correct home position. Normally when original Input signals become ON drive slows and after 1 cm I have home position due to slowning ramp, but somtimes drive stops immediately on the edge of original input sensor. I have no idea why it is like that. Maybe you can advise sth or get some clue thanks in advance for any help
-
Hi One of my friend want use more analog output on his vfd. Its a Mitsubishi FR-A740 type. Currently the AM signal is for current, but he needs the speed and frequency too. As we saw its only one analog output is avaiable, but you guys might know better. Can someone confims our theory. Thank you.
-
Micrologix 1400 1766-L32BWA-"Burnt" Output
robmx57 posted a topic in Allen Bradley / Rockwell Automation
Hello, I am trying to flash an indicator light (Banner K70LBGYRPQ ) every .5 seconds. The PLC manual says 2.5A per channel. The light uses roughly 113mA max current @ 24vdc. I am using output 0 to do this (O:0/0). I think I may have ruined the output by flashing the indicator light. Has anyone ever experienced this before? Is there a minimum pulse time for this PLC? What do people normally do when wanting to flash an indicator light such as this? This is not the first time I have seen this happen. Thanks in advance!- 7 replies
-
- relay output
- welded
-
(and 3 more)
Tagged with:
-
Hi,I want to read transducer signal on PLC.I am using 7kg60008ab/nn transducer and it's analog (4-20mA) output is connected with analog meter.Can I connect the transducer current output (4-20mA) signal to PLC analog input in series with analog meter display???So that I can read the value on PLC simultaneously with analog meter?
- 3 replies
-
- analog input
- analog output
-
(and 3 more)
Tagged with:
-
Hello to everyone. Nice to meet you all. How are you? I hope you are doing well. I’m developing a program with the purpose of make something similar to a pulse train in the output. However, sometimes I need the output to be a “positive” pulse and sometimes a “negative” one. By positive and negative I mean the polarity in relation to the pulse train source. I’m trying to use a pair of bits in order to switch between the two choices of polarities. I attach a simplified version of the ladder diagram I’ve made. When I thought about the logic, it seemed logical to me, however, it isn’t working as supposed. SM0.4 is a pulse train source. According to the software manual, it is a pulse train with 50% duty cycle and a cycle time of 2 s. That it to say it says at TRUE for one second and return to FALSE for another second. I assign the value of that variable bit to the M0.0 memory bit. I get the negative version of the pulse train logically negating it in the Network #2. I assign the value of two inputs, I0.0 and I0.1, to other two memory bits, M0.1 and M0.2. · When both inputs are in a FALSE state, the output stays FALSE, disregarding the state of SM0.4. (Case #1) · When I0.0 is TRUE, M0.1 is TRUE. However, Q0.0 stays at FALSE no matter SM0.4 is TRUE or FALSE. I attach a pair of pictures. (Case #2) · On the other side, when I0.1 is TRUE, M0.2 is TRUE. In this case, the output shows the correct behavior. It is the negated version of the pulse train source. (Case #3) Has any of you experienced something similar? Is there a better way to execute my purpose? I’m not executing the program, just simulating it with KincoBuilder from Kinco. However, it has always worked fine for me. Thanks for you attention. I look forward for your responses. Kind regards!
-
how many (maximum) analog inputs/outputs can CPU 1215C can reach without any issue?
Jairus posted a topic in Siemens
Hello guys, how many (maximum) analog inputs/outputs can CPU 1215C can reach without any issue? I try to search in google but can't find convincing answer. Thanks for your help. -
NX1P2 Motion Control change output device with code
BrunoRamos posted a topic in NJ Series / Sysmac Studio
Hi everyone, To explain the problem a little bit: I have 2 systems that are equal, they have 1 PLC, 1 Inverter and 1 Servo Axis (Image01). The devices are connected via EtherCat. The thing here is tht in these systems the PLC and Servo Axis is the same but the inverter is different. My goal is to have the same project on both systems and depending on the inverter detected use the correct program. What worked: If I add the 2 Inverters and 2 Servo Axis on the project on different nodes (Image02), I can detect which is present using the variable _EC_EntrySlavTb[n]. My issue is that if I want to make more replicas of the systems using different inverters I will eventually hit the Axis Number limit for the PLC while in reality I am only using on Servo Axis at a time. What I wanted: I would like to be able to control 1 Servo Axis with 2 different inverters (only one active per PLC) (Image03). What I tried: The axis parameters can be set using a variable of the type _sAXIS_PARAM, however it seems that the option to change the axis basic settings is not available (Manual: NJ/NX-series Motion Control Instructions Reference Manual (W508) page 5-58) (Image04). The axis basic settings is where the definition of the output device plus control words are set (Image05). Is there a work around to solve this issue? I would really like to avoid having to manually change the output device for the Servo Axis every time I make an update on all the systems. Best Regards, BR -
I have an analog output card 1734-OE2V. As a default, there is selected fault mode as 'Go to Low Clamp'. I am using output range -10V to 10V. What is the value for Low Clamp. Is it 0V or -10V? If I want it to be 0, do I need to select 'use fault value' and set the fault value to '0'.
-
Hi, we have a FX3U 128 PLC. I connect 24V to COM and all the output in the partition Y0, Y1,.. have 24V even if some output are ON and some are OFF. Why?
- 3 replies
-
- mitsubishi
- fx3u
-
(and 1 more)
Tagged with:
-
I need to use digital outputs of PF527 drive. Controlling the outputs, it does not do anything. Relay outputs are working fine, but opto outputs do not work. For the outputs, there are relays connected, using pin 6,7 and 17.
- 3 replies
-
- pf527
- opto output
-
(and 1 more)
Tagged with:
-
Activating PLC Output at the specific time - please help
MRPLC82 posted a topic in Allen Bradley / Rockwell Automation
Evening, I struggle with simple task... I need to activate PLC Output at the specific time of a day. I`m using GSV to obtain PLC time, data is being moved to DIN[7] registers. Then I have three EQU (Hour / Minute / Second) and at the end of rung there is OTL for output. Rung below I have two EQU (Hour / Minute) to disable output at different time - OTU. However every time OTL is energised , OTU on rung below is fired too. What am I doing wrong here ? -
Using NX-PG0232-5 to control Stepper Motor (NJ PLC)
ragzz1995 posted a topic in NJ Series / Sysmac Studio
Hello, I need to control a stepper motor(have stepper driver) using NX-PG0232-5 with NJ301 PLC. The function is simple, i need to run the stepper motor continuously at a specified velocity. So, in NX-PG module I've made the settings (Ch1 output mode as "Velocity continuous pulse output") and given the tags to IO (as shown below, sorry i'm not able to attach image). I've also added the initialization program to switch on the vfd. Now to move continuously i should should just give speed in pps in "PG_Ch1_Command_Velocity" right? Ch1 Controlword Control word 1 W WORD Ch1 Switch On Switch ON for pulse output 1 W BOOL PG_Ch1_SwitchOn Global Variables Ch1 Enable Voltage Start turning on the power for pulse output 1. W BOOL PG_Ch1_Enable_Voltage Global Variables Ch1 Quick Stop Immediate stop for pulse output 1 W BOOL PG_Ch1_QuickStop Global Variables Ch1 Enable Operation Start operation for pulse output 1 W BOOL PG_Ch1_EnableOperation Global Variables Ch1 Fault Reset Reset errors for pulse output 1 W BOOL Ch1 External Output Aggregated data of external outputs for pulse output 1 W BYTE Ch1 Command Position Command position of pulse output 1 W DINT PG_Ch1_Command_Position Global Variables Ch1 Command Velocity Command velocity of pulse output 1 W DINT PG_Ch1_Command_Velocity Global Variables- 6 replies
-
- nx-pg0232-5
- nj
-
(and 1 more)
Tagged with:
-
RSLogix 5000 BOOL Base tag not activating output
Kris Salmons posted a topic in Allen Bradley / Rockwell Automation
I have a Base tag of BOOL logic that will not activate the MOV output. The Base tag is paralleled with an Alias tag for a NO pushbutton. When the pushbutton is actuated it produces the desired output. Has anyone encountered this issue from a togglebit base tag before? Why would a base tag produce a different outcome from that of an alias tag that function properly? -
Hi every body, could you please help me; i have a mitsubishi plc serie iq-rwith the followings modules:powersupply r61p, r01cpu , rx40c7 inputs , ry10r2 outputs , r60adv8 analoginputs and r60da4 analog outputs. i am newbe with mitsubishi plc ;i would like to learn using the analog output of the R60DA4.for exemple i would send a digital value to the ch1 and convert it a voltage that i can mesure on the output of channel1.i have tried but i didn't succeed.i am using gxwork3.i have configured channel1 as +10v -10v output, normal mode , normal output;then i made a simple program in sfc to try this conversion but i get nothing in the output of channel1. i found that the digital value should be sent to the adress D11 wich is the adress of channel1.here you will find the file i made with gxworks3.could you please help me. ANALOGOUTPUTSCF.gx3
-
Comparison of Mitsubishi, Allen Bradley & Siemens
Gibblet posted a topic in General Topics - The Lounge
Hi all, I am in the process of doing a project for some school work and need to do a SWOT analysis of the latest modular PLCs from Mitsubishi (R series), Siemens (S7-1500) and Allen Bradley (ControlLogix). So I thought what better way than to ask the people on what they think are the pros and cons of each! Thanks for your responses in advance!- 10 replies
-
- swot
- comparison
-
(and 9 more)
Tagged with:
-
Is there any reason not to have input and output modules on the same rack as the processor and Ethernet cards? We have RIO’s and sometimes have networking outages, I want to move critical IO to Rack0 the same rack as the processor, is this bad practice? I've seen architecture for BMS that only have Ethernet cards and processors in Rack 0...
- 9 replies
-
- controllogix
- rio
-
(and 2 more)
Tagged with:
-
Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software? I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously. Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
- 7 replies
-
- cx-programmer
- control
- (and 12 more)
-
Hi, I'm using a CJ2M CPU 33, and also a CJ1m Ad-041-V1 Analog Input and DA-041 Analog Output card. I am using the Analog input to measure my current in my one heating application and Ihave that reading and scaled correctly, but now I want to use my Analog output to replace the Rheostat we have in the system. I'm having some issues setting the range and getting voltage to vary. I also am a little new to Analog Outputs and don't know what I'm doing wrong. I have attached my program here. Any help would be greatly appreciated. Analog Heat.cxp
-
Please let me know if it is allowed to sell PLC hardware on your forum. I accumulated lots of Omron hardware that I want to get rid off. Here is the list, I have several of each type, asking $12 each plus shipping. All in working condition. Base Unit C200HW-BI051 Base Unit C200HW-BC101 16 Point DC Input Module C200H-ID212 16 Point Digital Output Module 24VDC C200H-OD212 Power Supply Module C200-PA204
-
Hello! I'm running into a problem with a malfunctioning OD212 output card on my PLC. I figure the problem has something to do with my wiring, because I've put 2 different cards in with the same results. The card is unable to switch any of the relays I have as outputs although the indicator lights on it are functioning as expected. The setup it is in is: A PA202 power supply, followed by a CJ1M CPU13 CPU, 2 ID211 input cards, and 3 OD212 output cards. The bad card is the second OD212. All of the other cards work fine, it's just this one that's been having problems. 8 of the terminals on the bad card are hooked up to relays that each draw 0.02A and two more are attached to relays that draw 0.05A. So in total that's 0.26A if all the outputs are on at the same time (which they never will be.) I saw someone was having a similar problem to me on the forum, which was solved by switching out the PA202 supply, but that didn't work in my case. I don't think the problem lies with the PLC or the card's placement in the rack because I switched the card's position with the one next to it (output card 2 switched with output card 3) and tested that card (output card 3 in output card 2's place) without hooking it up to the original wiring and it worked just fine. However, I was still getting the same issue with the bad card even though it was in a different position, leading me to believe that I fried it somehow. Some other quirks of the bad card are that its outputs do not turn on and off with the indicator lights like how the other OD212s do. Below is a link to a video that shows this. The bad card has already been switched with the one next to it in the video - so it's on the end, but it's original position was second to last. https://youtu.be/wTvvGCHFpsc ( you may want to watch it at half speed ) So what I'm wondering is: how am I frying these cards / Is the problem easy to fix or will I have to send them to Omron? Thanks in advance!
-
Hi there, is somebody experience whereby the output of the 1769-OF4Ci is not responding on the value entered?. Setting: 4-20mA Res: 0- 32767 - PID set whatever value I key in the output current remained. please help. Ganie
-
I am new to Automation Direct software and how the programs are written. Can anyone explain how they handle the analog outputs? My processor does not support the IBox that makes life easier, so I am having to do it the old hard way. I understand most of the logic of how its done for sending data to one channel but I don't understand how the channel selecting works. Can someone give me a programming example or explain how that works? I am looking at the online manual that Automation Direct provides for you for the analog module but I am having a difficult time trying to wrap my brain around how they do their analog stuff ><
-
ML1400: Manipulate output through modbus/tcp
MikosMotta posted a topic in Allen Bradley / Rockwell Automation
Hello I have a scenario that's been bugging me for some time now. The scenario consists of a Micrologix 1400 that I need to control it's output from modbus/tcp. In detail what I really need is to be able to manipulate the O0:0 through modbus/tcp. The PLC would be the master and I would be the slave that triggers the connection to the master. I'm using a Modbus-Client on my PC and that should be the slave. Any idea as to how I can manage that? Currently I can send data to the master but everything is "stored" on B10 and I have no idea how I could write directly on O0. Thanks a bunch guys. PS: I'm borderline noob.