Search the Community

Showing results for tags 'i have problem to connect 2 temperature device with him delta with plc delta by rs485..when i run plc i can see the temperature change on pc but the problem in him its'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 165 results

  1. We currently have Delta DVP60ES2 and DVP32ES3 PLC's doing positioning control on Inovance IS 620PS2R8I 400w Servo Drives by Pulse/Direction. Under both of these environments our pulse count read on the Inovance drives are reading higher than what the PLC is outputting. We also have Mitsubishi & Inovance PLCs, which when connected to the same Inovance drives dont have any discrepancies in the pulse count. We also have Delta ASDA servo drives, which when connected to the Delta DVP PLC's also don't have any discrepancies. Given we have tested these combinations, it has led us to believe there is something unique about the pulse train output from the DVP PLC's that is causing the Inovance drives to read additional pulses. Has anyone experinced a similar issue with Delta PLC pulse output? If so what was the solution? 
  2. I am using DVP-ES2 PLC with DVP04AD-E2. I connected the flowmeter to the analog input module (4-20mA). And I noticed something weird, when the flowmeter shows 4mA value (no water flow at all) the data in the PLC keeps coming like 20-30 (0-32000). And when I change to the other port of the analog input , it even reaches value like 100 although there is no water flow at all. Note: I have done proper scaling to Liter/second and do proper grounding. Do you know what is the cause of this?
  3. RSLinx and PLC 1747-l553

      Good afternoon, dear specialists. Recently, only without preparation, I began to set up communication between the scada and the PLC. The problem is that RSLINX LITE (v3.90.01 CPR 9 SR9) sees both PLCs on the network, but one of them gives a problem with reading data, or rather, the data monitor does not load at all (or shows a red cross (which means there is no physical connection to the PLC)). But it responds perfectly = 1ms. Nearby is an old PC with an old RSLINX LITE (v2.41.00) that perfectly reads data from both PLCs. What is the problem? why doesn't the more recent program read the data? There is an even older PC on Windows XP on the Intouch scad, via OPC the "SMC" application also reads data without problems New PC:                                               Old PC:                                                still the third ancient PC: Windows 10                                         Windows 7                                            Windows XP RSLINX LITE v3.90                             RSLINX LITE v 2.41                             SMC (intouch) Status Not working                              Status Working                                      Status Workinп It was also connected via the "Ethernet" and "Ethernet / IP" drivers. I directly connected a new PC to the PLC and set up only one connection, still the result is negative. I would be grateful for any help! If I apologize for my English, I did it through a translator.    
  4. Hi all, New to the forum. I've been pretty much able to do the things I wanted with Beckhoff, but now I'm finally running into a problem I can't seem to solve alone. I'm trying to set-up Modbus RTU RS485 communication in Twincat3, using an EL6021. I've implemented a sample program from the Beckhoff website, but can't get it to work. I've got the feeling I need to properly set up the EL6021 but most information on the Beckhoff website is about the KL-series IO. Does anybody have experience with this? The strange thing is that, when I enable the function to read some slave's registers, BUSY is set and remains set. No timeout is triggered. I don't have a slave connected yet but I would at least expect to see something on the output of the terminal, and then a timeout. I've bridged TxD+ and RxD+, and TxD- and RxD- and set 8000:06 of the EL6021 TRUE, half duplex mode enabled). A scope connected to TxD+ and TxD- shows nothing. Code added below. I've added a GVL called 'Variable_Configuration' with the following: VAR_CONFIG     Main.MB.InData AT %IB0 : MB_KL6inData5B;     Main.MB.OutData AT %QB0 : MB_KL6outData5B; END_VAR And then the MAIN: PROGRAM MAIN VAR     bIoSyncMaster AT %I* : BOOL;     MB : ModbusRTUmaster_KL6x5B;     MBLedDriver : ARRAY[1..10] OF WORD;     tmpExecute : BOOL;     bError : BOOL;     bBusy : BOOL;     iErrorId: MODBUS_ERRORS;     iNoDatByteRead: UINT;     count: INT;     freebyte: INT;     TxError: INT;     TxBlocked: BOOL; END_VAR MB(     UnitID:= 41,     Quantity:= 4,     MBAddr:= 16#0020,     cbLength:= SIZEOF(MBLedDriver),     pMemoryAddr:= ADR(MBLedDriver),     Execute:= tmpExecute,     Timeout:= T#5S ,     BUSY=> bBusy,     Error=> bError,     ErrorId=> iErrorId,     cbRead=> iNoDatByteRead);      MB.ReadRegs(); count := MB.MBMaster.com.Buffer.Tx.count; freebyte := MB.MBMaster.com.Buffer.Tx.FreeByte; TxError := MB.MBMaster.com.Buffer.Tx.Error; TxBlocked := MB.MBMaster.com.Buffer.Tx.Blocked; tmpExecute:=FALSE;    
  5. Hello all, I need to read device memory mostly I need to read R registers from PLC L26. I read device data, but inside of table, I can't find R or ZR registers. Can you help me?  What I did wrong?   BR KS  
  6. I have a Siemens HMI 6AV2 124-0MC01-0AX0 in my machine. I want to clone the display on the HMI to PC/Laptop. My question is: 1. What software that I need for this task? 2. What kind of interface that I need between the HMI and PC/Laptop (for example ethernet cable, etc)? 3. Do I need to communicate with PLC connected with HMI or can I just connect with the HMI? Thanks in advance for the answer.
  7. Hello !  The idea is to heat greenhouse with stable temp at 13*C.  Heating method is with circulating hot water(80*C) true pipe, and open/close three-way valve. Output 1 is for open big circul Output 2 is for close big circul valve is 50 mm , step is 10 mm per minute In theory water heater start at temp 15*C to be prepear and for about 40 min is ready with 80*C .  Temp is continue droping and at 14*C three-way valve start to open circul 1(big one) and need to open 10 mm  After 0.2*C drop down open 10mm again ...  and when temp is drop to 13*C 3-way valve need to be open at all 50mm ...  So the greenhouse is big ( arount 10.000 sq.m. )  And temp continue drop(or not) but in fact is drop to arount 12,5*C to 12*C and stop.  When greenhouse start heating. Temp is start to go up.  3-way valve need to start closeing,and at temp 13*C need to be fully close.  Problem is that : when temp is going up  Delta DT320 is operating at the same time OUT1(because temp is lower then 13) and the same time OUT2 is try to close, so the 3-way valve stay at the same place and not closing because is have "line" on open and "line" for close.  setting from Delta DT320 Control  Ctrl Method : PID RUN/STOP : RUN  Heat/Cool : Heat(out1)/Cool(out2) Com Write : enable Lock status : normal  AT : Stop SV control : Const SV Input  Type : 4-20mA Unit : EU SV : 13.0 Range Hi : 50 Range LO : -20 Pointer : 1  PID Parametyer  Pb : 0.2  Ti : 787 Td : 196 Ctrl Period : 20  I offset : 0.0  PID set : AUTO PID SV(auto) : 100.0    
  8. Delta Plc Solenoid Pulse

    Hi there, I'm working on a project on a cupcake machine. I have to throw empty wrappers so I'm using a photoelectric sensor to sense the empty cupcake and after 2.5-sec air solenoid activated with delta PLC to throw that empty wrapper. The thing which I want to discuss here is that I want to operate my solenoid with pulse means when the empty wrapper comes to the solenoid through the conveyor then the solenoid gives a pulse of air so the upcoming filled wrapped will not disturb with this air. how Should I program my delta plc it is a transistor base. Can I use PWM? Best Regards, Asad Raza
  9. Hello I have a wago PLC and i try to communicate to a device through RS485 using the module 750-652. I tried using the WagoAppCom library and came up with this code But i always get errors regarding FB_init block. I though the instance would be automatically matched. I still can't see how to resolve this as Wago library documentation is very poor and contains 0 examples. Has anyone else solved serial comms problems?  
  10. Good day everyone!   I have some question relate with above subject. While i try make protocol for the CJ2M PLC.  i found out "Primary Expression (yN+x)" function but i cannt understand what`s this for. even i tried to find in the reference manual. i can not.  you can find it "Message Editor" -> "Message Variable" -> "Variable" sorry i tried to upload picture many times but it kept showing failed to upload.    hope so i could find the answer. thank you!
  11. connection to omron CJ1M PLC

    I have an omron PLC (CJ1M type) at home which I would like to connect to, however, lately, I can't anymore.  I'm trying on two different PC's a newer and an older one, both running on windows 10. 1 is just mentioning a DLL error and I can't even start cx-programmer, the other one seems to work, however, when I try to go online it always fails I'm using a usb to serial device and after some searching on the net, I thought the issue was with the prolific driver.  I tried all kind of fixes, but nothing seemed to work.  I have now purchased another device, the XS8801 from usconverters and installed the latest driver.  I have checked if cx programmer is set to work with the correct port and this is the case. My knowledge is very limited but I would really want to connect to that PLC again, so hoping someone out here is able to help me. Thanks a lot    
  12. Delta PLC Analog Wiring

    Good day all, I recently working an assignment to read analog data from sensors. I connected everything just as what the manual for sensor stated. My PLC is DVP20SX2 and the sensor data i want is 4-20mA. The analog sensor has two wires, Analog Output + and Analog Output GND. I connected the + to I0+ and the GND to the VI0-, but when I work online using the ISPSoft, I can't get any data. My doubt is the wiring. Can anyone guide me on this? Is my wiring wrong? does analog works the same as digital, where we have to connect to same COM?
  13. Hey, I have a project which one part involves using a RTD PT100 (0-100 Deg.C 4-20mA) connected to a CJ1W AD041 (ATD input card), the PLC is a CJ2M Basically the PLC needs to read the RTD and display the temperature on a Omron HMI (NS10), via Ethernet, Could someone please help me out with a basic example program - to read and convert the RTD - ATD value to store in memory. Your help would be most appreciated. Thanks  Richard       
  14. Hmi temperature delta

    I have connected 2 temperature devices with him delta with plc delta by rs485. When I run plc I can see the temperature change on pc but the problem in hmi  it's give errors. Com 2 errors  I need someone help me to connect these devices please 
  15. FTP from OMRON NX1P PLC to a Delta HMI

    Hi all, I'm looking to try and send data from the SD Card on my OMRON PLC to a flash drive on my Delta HMI - DOP107WV using FTP. So essentially I need to use the HMI as a FTP host. Is this possible? And if not, is there another way of doing this?  Thanks, Ibrahim
  16. Hello everyone, I have a Kinetix 6000 CIP drive (unwind) and I need to control its speed by a PID controller. I have everything working except the MCD instruction doesn't pick up on the PID output value change. It changes the JOG speed, which I use to control the unwind, if I set the speed manually, which is slow. The PID changes the speed almost continuously. Any suggestions are welcome. This is how I'm attempting to control the speed: A1_r_JogSpeed = PID output value   Thank you    
  17. Good day all. I have an application which is running an Allen-Bradley SMC-Flex and the client would like to get the monitor the current of the soft-starter via an HMI connected to a Delta DVP-12SE. Is the SMC able to output a current and with what communications medium would I use?   Thanks.
  18. Folks, we have a set of Mitsubishi Q12PRHCPU (redundant) running effortless since many years. CPU-A as standby and CPU-B as Control. Recently we noticed BATT low alarm on CPU-B. So we arranged for a spare battery Q6BAT and started the procedure as per manual(attached procedure and flow chart). We did memory copy from Control to standby (as prescribed precaution) and did the Reset of Standby PLC CPU-A. Memory copy from B to A completed successfully 100%. But the BACKUP LED did not turn Green from Red & Error LED kept flickering on standby CPU-A. CPU-B remain in Control but backup LED turned RED. From system monitoring we found that there is a Error 6000 (FILE DIFF.) observed in One of the .QPG (program 00-MDBUS.QPG). We tried to reset it but were not successful. We are surprised that why does the program differs when it was copied from CPU-B to CPU-A using the memory copy. Still we did the VERIFY and found no difference between the programs in CPU-A & CPU-B.  Can anyone explain the cause of this issue and the solution. Please note that the CPU-B is still in control and plant is running. Backup LED on both CPU are red which means (redundancy loss) and error LED on standby CPU-A is flickering RED. There is no error in the CPU-A (Control) -we checked this using the GX Developer. Also attached here are the image of the error and error help. Thanks in advance. Battery Replacement procedure.pdf Battery Replacement procedure-Flow Chart.pdf Error.pdf MELSEC QCPU ERROR CODE 6000 FILE DIFF.pdf
  19. HMI Selection

      Hi,All I am new to PLC  Programming,started own experiment for learning at home. I have an Delta  DVP32EHOOT2 PLC, And I need to make a project on three water TANK Controlling  and one pump with VFD connected. I need your help for Selecting Cheap HMI and Analog card for same. It will be helpful anybody provide me  scond hand HMI availability in India or anywhere
  20. Hi All First ever post so forgive me if I do anything wrong. My customer has given me an FX5Uc PLC and a Delta DOP-B03S211 HMI. Comms need to be via serial. Ethernet not an option. I have configured the HMI as the Delta DOP datasheet(see attached) I have configured the PLC as: - MC-Protocol - 19200,8,1,Odd I however get an HMI error: - ########################################## COM 1 STATION 0: COMMUNICATION ERROR 3. READ ERROR No Response from Controller ######################################### I have created a simple page on the HMI  consisting of a push button (M reg) and a numeric display (D reg). When pressing the push button I can see the change in the PLC. (Transmission good) Any change of the D reg in the PLC is not reflected on the HMI. Confirms the message. I have tried all combinations of settings on both side but no joy. The PLC seems to be happy as it receives and transmits ok with no errors. Can any one see what I am doing wrong? DELTA_IA-HMI_Mitsubishi FX5U_CM_ENG_20170728.pdf
  21. Hi all:   Hope somebody will help me with the below error encounter on the NA. I mapped a external device (NJ PLC) variable (which is a structure) to a NA Global variable and the structure is automatically created in the NA data type as expected. I then create a new NA global variable and defined its data type as the auto created structure. However i observe the created new NA global variable is highlighted with an error "a data type cannot be used by both mapped and unmapped variable ....." ( pls refer to the attached screen).  I have found and view on the Youtube this video :"Introduction To The NA DataTypes" (link: https://www.youtube.com/watch?v=VZxWnVn1CSY). that clearly show the "imported" structure can be used for unmapped NA global variable even there is some variable already mapped to external device variable (starting from the 3:50minutes mark of the video). In my NA program i would need to create such unmapped variable for my logic use. Also i observe that i was unable to delete the auto created structure from the NA Data Types even after i deleted all variables that are defined with that specific structure. How can i delete such auto created structure in case i want to clear off some of those unused data types. I am using Sysmac Studio version 1.30.0.17. The HMI Device created is the NA5-9W00 (version 1.11)          
  22. Unrecognized Device

    Hey all - I am stumped and looking for some assistance. I have a project in studio 5000, v.32 where I have some ABB drives that are not recognized. I've installed the EDS files, exact same one my co-worker besides me did, and mine will not go recognized and it is driving me crazy! I've done it while online with the PLC and offline, still to no avail. I've also installed the EDS files by going through Tools>EDS Hardware Installation and by right-clicking on the ABB drive in the controller organization tree and registering EDS file. Thanks for any assistance, -k
  23. modbus_fb_11.pdfHello to everybody. I'm new I download from Omron France the FB to read form one or more instrument some register by Mod Bus RTU Every things is working well, but some register from the Instrument are on REAL. How i can get a REAL word with the FB on the attachment? Thank you   Modbus_03_Read_Holding_Regs.cxf
  24. Mitsubishi FX5-4LC

    Hello Guys,                      can anyone help me programming of FX5-4LC temperature control module with FX-5U80MT PLC. I want to Read present temperature value of each channel and want to set Temperature Set value from PLC.