Search the Community

Showing results for tags 'no of simultanious connection'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 33 results

  1. TCP connection

    I need to connect a A/B 5370 or 1756 to a PC and communicate over TCP/IP and be able to read and write input/outputs. What features does A/B provide? I would prefer to write in C/C++ but can also consider Structured Text - if it supports the standard socket type functions.
  2. UNABLE TO MAKE CONNECTION

    TRENDS ARE NOT SHOWING ON MY FTVIEW SE V8 . AS DATALOG MODEL STARTS IT SHOWS UNABLE TO MAKE CONNECTION IN DIAGNOSTIC VIEWER .  YOU CAN CHECK THE SCREENSHOT FOR THE SAME . I THINK DATALOG MODEL IS NOT ABLE TO CONNECT TO SQL DATABASE . WHAT MIGHT BE THE PROBLEM ? Please Help Guys .....
  3. Hello All,  Am a bit new to practical PLC applications. I was trying to configure a Phoenix Contact I/O module (1452916) on a MicroLogix 1100 PLC but it kept faulting out with the fault light RED. It would say "Major Error Halt S:1/13". The error description says I/O mismatch. The error code is 187h (see attachment). The Phoenix module has a cable with 19 pin positions for the 8 input. I connected the pin 17 and 18 to 24 volts and  0 volts respectively. Then because I was using input 5 I connected the pink wire to PLC input (I/1) 24volts and the White/Yellow wire to the PLC common.  On the I/O configuration on RSLogix 500, I used "Other" ( See attachment) but did not know the vendor details. Could anyone help me with the steps on how to communicate with the module? I have also attached the PLC program I was running. Thanks        
  4. Hi dears i have one client and 21 servers i want to eatablish a connection between this client and servers is there limitation for access servers? i read that one client can access to 12 servers only is it true? what is the best way to connect this client to 21 servers? best regards
  5. Genst,   Could You please advise how can I connect to CJ1M CPU12 - shown in attached picture. DB9 port is used for communication with remote input/outpus rack. There is this small portabove DB9, but first I don't know what cable should I use and seconde I don't know if it is possible to usi this port when PLC talks on DB9 with remote input/output rack. I want to connect to CX-programmer to be able to online troubleshoot PLc program.   thanks in advance. tomasz  
  6. Janitza UMG96RM RS485 Bus

    Dear All.     i'm a new user for Janitza. and i have issue related to RS485 actually, not to Janitza itself. i have one device (UMG 96RM), where there is only RS485 (2 pin only), no RS232, no USB, No Ethernet port. i'm trying simply to connect the device to the PC, via (USB to RS485) convertor, but i'm not able to do it. for me, this is the first time i'm see (RS485 2 Pins), usually there is Ground signal also. anyway, could you please somebody help how to connect? shall i add a pull up & pull down resistors at the device? and what is the power supply i must use? noting that, i tried many things, but still nothing happened.   Appreciate if somebody can help   Best regards.  
  7. Cannot get Online - CPM2C

    Hello Ladies and Gents, Im quite new to working with Omron. I am struggling very much to get online with an Omron CPM2C-S110C. It has a CIF01 card also. I hear this PLC is quite an old one. I have referenced the manual on 'connecting a computer running support software' and double checked I have the correct cables. The ones I am using and the way I am connecting is:-   PLC Peripheral slot >> CS1W-CN118 >> XW2Z-200S-CV >> serial to USB >> Laptop Checking on Device Manager, I have all the drivers installed, the comms ports are correctly numbered yet I still cannot connect. There are 4 dip switches on the top right hand side of the CPU and all are swiched off. I have called Omron Tech Support and they said to ignore them in this instance. The RS232C port on the CIF01 is used by a barcode scanner so there is no means to connect through that (I have been told) I feel that I have been through setting and checked in CX-Programmer and nothing looks obscure. Please offer me any ideas you may have. I would greatly appreciate it. Thank you.
  8. Good Evening, using the Ethernet Built-in LAN I need to program 4 power supply. I'm tryng to program the firstone but even if I can send the correct command to the power supply I always recive a 2006 error on SKTTCPRCP function Is there someone that can help me in order to not receive the 2006 error code? Have I to respect a procedure? It seems that at the second connection time the socket remain closed. Thank you!
  9. So I need to find a way for a Mitsubishi PLC to communicate with a PC - ideally sending a binary number through ethernet to a PC program that reads it and tells the PC which files to open. I think I can create the PC program with C++ or Visual Basic without too much struggle. But I am unsure of how to get that binary ID from the PLC and into the PC program. I have done a little bit of research on MX Component and MX Sheet, and also MC Protocol but all seem a bit outdated and/or just over my head and I need some better explanation - I'm pretty new to PLC and programming. I feel like it shouldn't be terribly difficult to get 1 external binary number into a PC program. I'm sure someone has done essentially the same transfer and I just want some ideas. -What kind of connection support do I need to transfer data (Likely just a D-bit) from a PLC to PC? -How would that/those bit(s) be accessed in Visual Basic or C++? I'm assuming some type of library function that will call the value
  10. Is there any way of viewing a remote Proface GP or LT screen inside a second GP or LT screen? I want to do this to avoid creating and loading duplicate screens. Essentially it would be like using GP Viewer-EX where the PC is replaced with another GP or LT unit.
  11. I have a cpu33 that I had issues with a bad battery and it loaded from memory card.  The version on the card was old so I decided to download the latest version from 2 days ago to it.  When I did, I lost communication through ethernet.   Can't connect through usb either.   The thing that baffles me is that I can ping the plc at the address and I get a reply.   Any help/suggestions would be greatly appreciated as I am not familiar with omron plc's at all.  Also on the display it cycles through Er HE 1P 07.
  12. PC-PLC CP1E - USB-to-SERIAL cable

    Hi,   I have a self-bought usb-serial cable converter for CP1E. Currently can't connect to my PLC using PC. CX-One says "Failed to the PLC". I am supposedly to use "SYSMAC WAY" as my Network Type in PLC settings?   EDIT: The CPU type is N30   I've checked the following settings: 1) COM number is correct ( as checked from windows Device Manager side) 2) Cable driver is installed, there is no "unknown" driver in my windows Device Manager 3) My RS232C LED in PLC is not lighted up.   Any other suggestions to check settings ive missed out would help, other than buying a new cable for the moment.   Regards, Summerstone
  13. I recently purchased the SIEMENS CONNECTION KIT (6ES6400-1PC00-0AA0) with its corresponding serial cable to connect to a MICROMASTER 440. I connect my RS232-USB cable to the serial cable. But I can not connect in any way! What do I do wrong? 1. In the micromaster 440 I put the following USS configuration parameters (USS = serial communication):    p2010 = 6    p2011 = 0    p2012 = 2    p2013 = 127 2. I put the DIP of the Connection Kit (Ref. 6ES6400-1PC00-0AA0)  1 ON, 2 OFF, as indicated in the manual.    I connect the connection kit module with its serial cable to my RS232-USB cable. And I connect the USB to my PC. 3. Open "Set PG / PC interface" and select PC COM-Port.USS.1 4. I go to the properties and I am selected COM1 without problems. 5. But I do the transmission speed test and can not find anything. 6. Also in the diagnosis of PC COM-Port.USS.1 I do the test and can not find anything. Supposedly my RS232 cable is correct (I have tried several tests). And the configuration of the COM port in "device manager" also looks correct. What am I doing wrong?? Zhanks!
  14. Hey guys,   I have worked on the FTView ME platform many of times.  I am now working on a FTView SE (Local Station) application, and I am having trouble connecting an Offline .ACD file to my program so that I can design.   If someone could help me with this it would be greatly appreciated.   Thanks in advance!
  15. Profibus Function Blocks for Q2ASCPU for Melsec ST Lite RIO inter-connection. Please assist in advising the attainment of such blocks - if any existing. Thanks
  16. Hi all, I will be starting on my MSc in automation in a couple of days so for that reason i have obtained a S7-1200 series 1211AC/DC/RLY PLC. This is a new area for me as i have been working in offshore since i graduated from my BSc a couple of years ago. I watched some Youtube tutorials on how the programming is done and i am ready to try it out for myself, but i have encountered a little problem.   Problem: I am using the X1 P1 PROFINET (LAN) port as a connection to my PC, this turns the Green Link light on and the Rx/Tx lights blinks orange. Now to the problem, i cannot connect to the PLC through the TIA portal, no matter what settings and connection types i use in the PG/PC interface box. I have had no luck finding leturature adressing how to configure the PC/software and get a connection to the PLC. Do any of you have a PDF or link which can help me through this problem?  Hardware: S7-1200 series 1211AC/DC/RLY 6ES7 211-BE40-0XB0 S C-J5PN 1614 2017 FS:05 Software: TIA Portal Version 13 STEP 7 Professional V13 WinCC Basic V13   Thanks   Best regards   Dennis    
  17. Hi all, I have a S7-1200 CPU 1214 DC DC DC and Cm 1241 6ES7241-1AH32-0XB0 communication module.I'm using TIA Portal 14 and i connected cpu but i couldn't connect cm 1241 communication module.When i looked diagnostic i saw" Diagnostics data are not available because the current online configuration data differ from the offline configuration data.".Then i looked for what was the difference.But i didn't see.Are there anyone can help me? Thank you
  18. Is CP1H with Ethernet option board (CP1W-CIF41) is capable to communicate More than one client? If yes what settings I need to be Done?  
  19. Dear all I am new please help me to find out how i can do electrical connection plus control of softstarter ATS48C48Q Schneider brand.I am using this softstarter for 200kw motor heavy duty.i need control this motor beacuse it is taking high torque at starting time.
  20. Good day  I require some assistance with the configuration setup (GX Works 3) for FX5u PLC inter-communication (PLC to PLC), over Ethernet (using the built-in Ethernet port). The purpose of the inter-connection is data exchange. (Values stored within the PLC storage registers such as words and bits).  Does anyone perhaps support files on this such as a procedure or example? Thanks
  21. In general, this control PLC program is written in GX Works. I did a simple visualization on TIA Portal v14 (WinCC RT Advanced) and I would like to now test it on Mitsubishi FX3U driver with ENET Module. I do not have much experience in this kind of thing, I'm still learning. I know that someone previously made a visualization in LabView and downloaded the tags from the PLC using NI OPC Server. Someone also did visualization in iFix and also downloaded tags through server opc. I do not know just how or what program to download tags in PLC so that I can no longer use it in visualization in TIA Portal. Unfortunately I still have a connection problem. The driver is connected to the router. From the connection options with RT Advanced I chose in the connections tab Mitsubishi and entered the appropriate IP. Still nothing. I do not know if the lack of a connection can be related to a virtual machine (VM Vare Workstation 12) on which I have TIA Portal installed. The driver pings but can not connect. I also tried using KEPServer EX to connect and unfortunately also failed. (I have information about the can not connect). Anyone know what program I should use? or had contact with such a problem? I attach a photo of communication from my station to more visualize the problem. Thanks  
  22. Hi, I was wondering if there is a way to limit the number of allowed on-line connections at a time to a PLC? Like can you somehow set in the PLC parameters that only 1 'connection' can be on-line in the device at a time? Thanks Edit: I'm referring to connections from the TIA portal - not HMI / ethernet connections and so forth
  23. TIA Portal v13 - GOT1000

    Hello! Is there a driver GOT1000 for tia portal v13. I would like to do scada for GOT1000 GT14 using the Tia Portal v13. There is a possibility at all?
  24. q04udeh&qj71c24n-r4

    Hello everyone. i use q04udeh cpu and     rs-485 qj71c24n-r4 communication module. I  try to receive information from external device(2000amp power supply). im not a professional plc guy. On that moment i get MSG_RECV_String[7],  and store them in separate buffer from K1B108 to K1B120. i skip one because i do not need that k4B100 , and start from k1B108. I want to show value Voltsx10, but i need some help to do it. when i change value i see numbers from each separate MOV block function, but i can not convert them to decimal.(or i do not know how to do it). When i try BIN command i have error message 4100. Thank you for any suggestions.    
  25. Dear, i am doing one project on Omron PLC with VB.net.  i am using Ethernet communication  with  VB to PLC but i am unable to show analog value on VB page please guide me how to get data of analog value in vb and show in VB.net for DI/DO i am using CIO &H0  forreading   and  &H1 for write but for analog value how i will show on VB.net.