Search the Community

Showing results for tags 'First event logic Alarm'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 65 results

  1. Hi all, I am using alarms to generate reports through sql . But sometimes my alarms are getting missed and due to that my reports are not getting proper expected output. My alarm bit is almost high for 3 to 6 seconds , however i have observed that its getting missed . I dont know why . In below image after @22.41.03 the next snap should have been captured around @22.41.33 Instead of that it captured @22.42.03 have anyone faced issue with alarm missing issue? Any suggestions would be very helpful.   Thank you.
  2. MITSUBISHI A2SH-S1 CPU

    Hey i want to know that in mitsubishi A2SH-S1 CPU how can i determine that battery voltage is what and if battery voltage is low then i want to on an output so that i can change the battery with the new one so that my program does not gets erased. 
  3. So I have a plc program where most of the outputs are based on a counter that goes from 0 to 1000. The counter speed is adjustable and is generally set to run through a full cycle (count from 0 to 1000) anywhere between 0.5 to 2 seconds. The problem is, when I try to energize an output by using an EQU instruction, it will almost always skip the count because the scan time is not fast enough. I've been using a LIM instruction which has been working, but its not quite as accurate as it needs to be. I switched the counter logic to be continuous to try to make it faster which made it almost perfectly accurate... But only in the continuous task; it made the other periodic task significantly less accurate. I was curious if any of you had any tips on how to remedy this or just general help. I am still relatively new to PLCs and ladder logic so any advice would be awesome, Thanks in advance! Edit: The purpose of the counter is to cycle through from 0 to 1000 over and over again. My outputs actuate during a certain interval within this cycle (For example I would say actuate from 300 to 800 and it would stop and end once it hit those values via an EQU or LIM instruction). I wrote the logic as follows: First I calculate how many cycles per minute I want to perform, using that value I calculate how many times I want to increment my counter per millisecond. Then a timer is given a preset of the total cycle time. While that timer is running I continuously multiply the timer's accumulated value by the "cycle count per millisecond" that I calculated earlier; the resulting value is the current count that all my outputs are based on... Hopefully that makes sense, I know it's not the best but I could not figure out a better way of doing it and I know rounding is certainly making the accuracy worse. My hardware is: Allen Bradely PLC (5069 l306erms2), 5069-ob16, 5069-ib16, and a Kinetix 5500s2 Driver for my motor(s)
  4. Hi there, I am fairly new to programming serial communications, especially with Mitsubishi PLCs. Can someone walk me through in ladder logic how to bring in ASCII to the PLC, store the data in the data registers. Then send the data out to another PC once an 'X' input is satisfied? ASCII code would go like the following: C2,0,1,123,2,ABC,3,456,CR
  5. Hello Sirs! I have a problem with PF527. I get alarms 'control sync alarm' and 'module sync alarm' occasionally. I suppose this meaning that PLC is missing some data from the PF527 device. How to confirm this or what should I do with the problem? Any ideas? Motion group update period is 8ms. Also this device is the last device in the ethernet line. I am thinking to pull the cable directly to the switch near PLC. I am not sure does it help?  
  6. Hello, I am new to Scada Programming. I am using Citect scada V7.50. I have completed whole project, but I am unable to generate Excel report for Alarms generated during run time. Please help me for this issue. Thanks...
  7. How do you test PLC logic?

    We have been working with PLCs for long time. We used to develop PLC logic, partly test it on an emulator and test the rest on the partly energised equipment. From time to time working with computer software development (C# and JavaScript) I was always looking for something similar to unit testing in the PLC world. As I couldn't find anything at that time I've started developing own automated testing tool. Now we use this tool, which basically simulates PLC inputs in defined actions and checks expected behaviour of internal tags or/and PLC outputs. If it behaved the way we expected, it's PASS, otherwise it's FAIL. We break complex logic into small parts and create unit tests for it. By creating more of these unit tests we can test PLC logic of any complexity. The software called PLC Logic Prover and it's free at https://www.controlx.io Recently, I've been told that there is no point to develop anything new if there are already great tools on the market. Honestly, I didn't do proper research earlier, so I'm here asking the experts. What do you use to test PLC logic? What automated testing tools do you use? Is it using IO simulation or it can test logic by other means? Your replies are appreciated. Thanks, Alex
  8. E-Designer

    I have E-Designer 7.52 Build 344 installed on 3 windows 7 laptops the 2 that the problem is on are Pro 64 and the 1 thats working is Home Premium 64 but I seem to recall having this problem on the the Home one 9 years ago and getting it sorted but cant remember how The problem In Alarms,  Alarms New Alarm Alarm text: When typing cursor stays at left side and can only be moved to the right by the arrow key then jumps to left side after letter is pressed or you can type in reverse Signal:        Typing works normal OK:             Entry is not valid ;May not be blank Copy: Ok: Same result Properties:Ok:Same again Is there anyone who can help me with this as the laptop that works is on its last legs Thanks  
  9. Sysmac Cj2m Cpu35

    Dear All,  Need your help. I have problem with plc cj2m cpu35. After power trip plc error. Err HE Ip 01..what is mean? plc also connected with one pc using ethernet cable. Any suggestion need to do... 
  10. Sysmac Cj2m Cpu35

    Dear All,  Need your help. I have problem with plc cj2m cpu35. After power trip plc error. Err HE Ip 01..what is mean? plc also connected with one pc using ethernet cable. Any suggestion need to do... 
  11. Hello Dear Colegues. I am using historian 7.0SP6 (enterprise license). I have installed OPCAE collector to collect alarm and events data from a project in cimplicity in order to have an historical data of it. Also I have checked the Historian OPCAE interface box in the cimplicity project´s properties. The problem is that when I try to see the tags from OPCAE collector on historian administrator I have the following error "No Tags Matched The Criteria You Have Entered. Please Try again or Cancel your Search". Also, I am not able to see the "last 10 alarms in the collector´s configuration tab. What could causing this problem?
  12. Deleting Alarm Logs Wincc HMI

    Hi, how can I get rid of those alarms with status I(O) ? They are simply something like duplicates and they re making it hard to read the logs.
  13. AVE instruction Error

    A little background information here, I am trying to create a moving average so I accomplished it with the code (imaged attached) The problem i am having is the AVE instruction error bit goes true. it leaved me with a result of 1.#QAN  I did some googling and it said this is typically done when dividing by zero?? so i added a NEQ to 0 prior to loading the array. then it happened again. so i put the error bit in front of the FFL so it will stop loading the array when i get the error bit so i can see what values are in the array when it errors out. Has anyone else had this issue and what could you do to resolve it? I haven't had any luck find something that points me in the right direction. Thanks in advance for your help.
  14. I am using a Label as a Message Display with Resource Group.  I want to do the same thing with my User Alarms, I do not like the Alarm View Popup.....The image is how I assume it needs to be setup.  It compiles and downloads without fault, but messages do not display. Any thoughts on what I am doing wrong?  I could retype all the User Alarms in a Message Resource folder, but I have a lot of User Alarms.... Thanks,
  15. Hi, Could anyone help me out on how to extract the digits present in a string in sysmac studio... Thanks in advance !!!
  16. Hi, I've been having a problem with my Schneider setup, and I can't seem to figure out the problem. I'm using Machine Expert Logic Builder and Vijeo 6.2, and I can't seem to download to my PLC. I can download to my HMI just fine, but my HMI comes back with the message as mentioned in the title. Also when I perform a full download, machine expert comes up with the message "Could not connect to the device for item "xx", selected target system "PLC name" is different from the connected device "HMI name". The weirdest thing is that machine expert shows my PLC just fine, but doesn't show my HMI. I have no idea what to do, as I feel like I've tried everything. The IP range is fine, subnet is fine. The driver in IO manager in Vijeo has the PLC nodename in it, so that shouldn't be the problem either. Does anyone know what to do in a situation like this? Thank you in advance!
  17. TIA Portal V13- Alarm for Bool Data type

    IN TIA Portal V13 HMI Alarm Setup, Discrete Alarm Not allowing Bool Tags in "Tag Trigger". Please help how to set Bool Alarms?
  18. Please could you assist with the software required to download data tables from 4 off DIRIS A10 Multifunction Meters into TM221CE40R Logic Controller via TMC2SL1 Comms Cartridge using Modbus Protocol over RS485. I have downloaded the Modbus tables from Socomec but not sure how to get these into the PLC. I would really appreciate your help in achieving this. I am using EcoStruxure Machine Expert - Basic to program the PLC & DAQ Factory Developer Release for my Touchscreen. Link to Socomec Modbus tables: https://www.socomec.com/files/live/sites/systemsite/files/SCP/6_gestion_energie/diris/diris_a10/DIRIS-A-10_COMMUNICATION-TABLE_2018-01_DCG01013_MULTI.html#General
  19. Control Panel

    Is it possible to view the values / states of all inputs, outputs and workbits (e.g. 64.00 through 64.15 on Omron CQM1 PLC) on a single screen or control panel within CX-Programmer software?  I'm trying to troubleshoot some ladder logic that I wrote and need to know the values of 5 or 6 inputs/outputs/workbits simultaneously.  Having to scroll up and down through my ladder logic repeatedly does not work well with code that changes state every 5-10 seconds or so. Any help is welcome.
  20. Q03UDVCPU

    I am new with PLC's and I am learning how to work with GX Works 2. I have two questions, 1st Question: Using a Q series PLC (Q03UDVCPU) Is it possible to convert the language of a project from ladder logic to structured text? 2nd Question: If I read a project from a PLC why is it always ladder logic? Is there any way to read out structured text?
  21. I am trying to use the Event "SaveUserAlarmLogToFile" tied to my F1 button to save my alarm history to my SD card installed in my screen, but I can not find any details on how to specify the file name for the save...can someone please clarify what should be entered for the file name?     Thank you!!!!
  22. Hi I'm looking for Ladder Logic code that I could use for a plastic injection molding machine.  I am willing to purchase and/or modify existing code to meet our specifications.  We have lost the Ladder Logic out of the TI/Siemens Controller on our Newbury 100 Plastic Machine so we're looking at replacing both the PLC and the HMI interface with an Automation Direct Controller.  We have the HMI Basic Code for the Newbury but not the ladder.  I've pasted the manual below for our machine.  Any assistance would be much appreicated.  The manual was too large for me to post but I've posted a document with information about how we intend to upgrade which has a little information about the machine also. Newbury 100 upgrade logging.docx
  23. Hello! I have a project where I need to use Allen Bradley PLC, it might be one of CompactLogic series. In scope of the project I need to transfer few real values to DirectLogic PLC that installed on customer side. DirectLogic PLC has installed ethernet card that support Modbus TCP, TCP/IP and UDP/IP protocols as it says on automationdirect website. I start looking for Allen Bradley PLC that support Modbus TCP or TCP/UDP protocol and did find clear information. Could you help me to find out a way how I can pass the data to directlogic PLC from CompactLogic?   Thank you in advance!   Regards, Scotty
  24. Panasonic FP0 C14RS

    Hi All, I am new to the forum and new to programming PLC and like every newbie I have a lot of questions - Brief History of me - I had been a Manufacturing Technician for 20 years and recently got my BS on Electrical Engineering and now working as an Equipment Engineer. The main reason that got me interested in PLC's is my degree,  the field that I would like to get into and a recent problem that arise at work. My experience with PLC is very small in programming, some in TS I/O- However I had been studying by my self to the point that I built a test bench to understand it better and in the future create different project for learning purposes Currently I am putting together a tool Alarm delay program - Basically my exhaust sensors trigger an alarm (input signal turns OFF) before its send  the signal to my tool for abort, I want to create a different Alarm which will cause a different response from my tool and delay the original Alarm by 10 min and then trigger the original Alarm - PLC = Panasonic FP0C14RS  Reasons: Create a different Alarm: The response from my tool to this alarm will allow me to return my material back from the tool and put it in a safe spot. Delay the Alarm: Use a timer to perform this tasks - This the time that approx. it takes the to return the material. Trigger the original Alarm: I need to know which sensor was the problem in order to properly TS- So after my timer is complete - I want to know which sensor created the original Alarm My Current problem: I created the LD program, and while the original alarm stays OFF the program works fine - but since my exhaust sensor are always on - If my original alarm is trigger for  a few seconds, just enough to start my Delay Alarm: I dont have a way to know which sensor trigger after my Delay(Timer)is complete,  I reset my relays in order to be ready for new alarm.   Please provide feedback to my program - I know currently is not the best way or efficient way to do this and there are better ways, but my plan is to get it to work and then later revisions improve the way the program can be written   Thanks in advanced for your feedback and help Exh_delay_inv_rev1.pro
  25. Every time my rsview32 project starts up all the alarms which are set up to alarm on 0 tag value show up on the screen even though the bit in the PLC is not in alarm condition. I believe this is because the communication between RSView32 and PLCs is not established yet and the tags are seen as having value of 0 in the HMI. Is there a way to disable or suppress these tags at startup to give enough time for the RSView to update the values so the false alarms are not being displayed?