Search the Community

Showing results for tags 'remotely access fx series plc data'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 201 results

  1. stf and stop on at same time

    i have a 800 series vfd drive that when trying to start has the STF function and stop on at the same time, does this sound like a plc issue or a wiring issue?
  2. Read/Write data to PLC

    Goodmorning a question... I builded a simple monitor of plc. I need to read the data of the Mitsubishi FX3GE PLC. In example I should read: D14  FLOAT 32bit D16  FLOAT 32bit alarms from M100 to M119 and a bit of state M450 How can I do this? The PLC is connected via ethernet and the port il 5002.  I'm working with PHP and normally use modbus, opc-ua, etc. But here? Thanks in advance Carlo
  3. Does anyone know whether it is possible to edit a Omron NB screen remotely via modem. I know they can be monitored and activated remotely but can they actually be edited, ie change or add a screen. If not can any of the Omron screen range??   Thanks Don
  4. I have a Modicon NOM0200 unit connected to an access switch to send commands to various rs-232 devices. The Access switch requires a "disconnect string" to end communication with a particular port. The disconnect string is "CRTL+D", how can I send a "CRTL" keystroke from the NOM0200 unit? I know for carriage return it is "$R" is their a similar combination I can enter for "CTRL"?  
  5. FX3U Stop Reading Channel Data

    Hello Everyone,  Need help with reading channel data of FX2N-4AD with FX3U Cpu. I have added all the logic and it works also. Problem is that, FROM function stop reading/fetching data from FX2N-4AD after some time i.e couple of hours and value just hang. Like 502 or something, untill you reset the whole PLC. What could be the problem. For the further info, -I have connected the FX2N-4AD on the right of fX3U-64M. -There are two extension blocks FX2N-16EX and FX2N-16EYR also added to the right of FX3U-64M -Order of mounting....FX3U-64M > FX2N-16EX > FX2N-16EYR > FX2N-4AD > FX2N-4AD   I have tried using the 2nd special module connected at the end, but It showed similar problem after few hours of running. THis shows that both Special blocks fx2n-4ad are okay. There is something wrong with PLC maybe? Please help
  6. There have been many good discussions on the applicability of cloud-based solutions for manufacturing and process control systems. On one side, some people have concerns regarding security and control of the information, on the other side, there are identified benefits enabled by cloud systems. From VMS minicomputers to DOS and Windows, from ArcNet to Ethernet, it is inevitable the industrial automation systems shall adopt the technologies that are getting predominant in IT general use; the current environment that I am calling the “Cloud-iPad era” is no different; therefore the practical discussion is not if those new technologies will be applied in the industrial environment, but how. This paper is not intended to join the conceptual discussion about the cloud, but just to present a few simple practical examples, where cloud technologies are already enhancing industrial automation solutions and enabling new business opportunities. CloudPracticalApplications.pdf
  7. A1S68DAV parameter

    please can anyone tell me how to set A1S68DAV analog output module parameters , such as voltage output and resolution? or is the parameter can't be set at aLL (ie, fixed at -10V to 10V)?
  8. Hello people, I hope someone can help me with this. The system is connected with 8 PLC's. I want to transfer the data memory of a PLC to another like this: D850 from PLC2 to D900 PLC1 D850 from PLC3 to D901 PLC1 D850 from PLC4 to D902 PLC1 D850 from PLC5 to D903 PLC1 D850 from PLC6 to D904 PLC1 D850 from PLC7 to D905 PLC1 D850 from PLC8 to D906 PLC1 The data memory is an integer.
  9. Hello, Completely new to Mitsubishi PLCs and I need to use a date and time stamp for data collection purposes. We have a Siemens PLC as well and this has the data type "Date_And_Time" which is what I need to replicate. I have been attempting to write my own data type but am struggling with how to go about this as it is not straightforward and I cannot find anything about how the Siemens Date_And_Time is made up so I have nothing to go off. Does anyone have an example of a data type they have made that is the same? Or is there a data type which does this already in GX Works 2 that I just can't seem to find?  Please help!
  10. Hi Everyone, I would like to know  if two S7-300 CPU can exchange data via MPI protocol using X_Put and X_Get blocks. is it possible to test the data exchange via PLCSIM to verify. CPU1 = 313C-2DP CPU2 = 312 Please advise. Thank you.
  11. Hello! I am beginner in PLC world, also in SIEMENS PLCs. I managed communication over private network. Now I have a problem that I get same values on all inputs. Picture below shows my configuration of driver and data monitor. First picture shows values when input I0.0 is in state 0. Second picture shows values when input I0.0 is in state 1. Physically on PLC only input I0.0 is forced to 1, input I0.1 stays 0. But data monitor shows both inputs as state 1. Where is problem? Is problem in PLC program, TIA portal? I saw some guys using DataBlocks but I am not skilled enough to use it. Third picture shows simple PLC program on my PLC. Please help. Thanks in advance!
  12. Hi everyone; I want to communication Omron NB series HMI with Allen Bradley Micro 830 PLC. I don't know is it possible. İf its that possible, help me please..
  13. Lets say I worked in a factory that made multiple models of parts. I need to run data tracing on the off shift due to certain models only running on 2nd and 3rd shift. I want one data trace to capture one group of bits at Model 1, Then reset the Data Points and run again for Model 2, Model 3 and so on. So the Bits that I am mapping with the trace need to change.  I can change the trigger easy enough with my program. I see in the manual the CPU has a "separate memory area" for trace settings. Can this area be accessed from the Program so I can set my bit addresses to monitor to a word or E_?   See attached pic for clarification of what I aim to change through the program.   
  14. Good day to all, I am trying to establish DDE communication between my PLC (1769-L23ER) and MS Access via RSLinx Classic Gateway (3.9) over Windows Server 2012 R2.  On my developing PC (Windows 7), there isn't any issue at all. But when I port the codes over to Windows Server 2012 R2, MS Access is not able to establish DDE communications with the PLC.  I was wondering what went wrong. The error message from MS Access is "MS Access can't find the specified application and topic because it can't open the DDE channel, err.Number is 282. The code for getting the channel is as follow OpenRSLinx = Application.DDEInitiate("RSLinx","PLC-D") I was wondering was there anything I have miss out. eg. Configuration of the server, path settings, etc.. Any help is welcome. TIA Cheers CY
  15. Device point error between Parameter and PLC

    Hello all, I am a beginner with PLCs programming. I have an issue on GX Developer programming software from Melsoft trying to program my Mitsubishi Q-series PLC. CPU is Q03UDCPU. When the program is written and I try to upload it to the PLC, with the write to PLC window, I check -Program -- MAIN and -Prameter -- PLC/Network/Remote, click EXECUTE and a message appears : "Device point that is set in parameter is not match the device point in PLC". I can't fix it. In Parameter - PLC Parameter - Q parameter setting (window) - I/O assignment tab : I have (see image). Whe I use CHECK button it says there is no error. The X41 input device is plugged on slot 1/00. I am making this folowing the instructions a PDF I found on the Mitsubishi electric's wesite : Q-series basic course (for GX Developer). Thanks for the help, A. S.
  16. Hi, I have a a few substations and I´d like to have a local SCADA in each of them. What is the best scada to use with reasonable price? Does anyone know if there is a solution without the need to have a PC for each substation? Thanx
  17. Dear Everyone can help     i have a batching system of about 12 materials and i need to generate a report for all batches in the day in runtime, i tried using SQL with Cicode but sometimes i can't find some material's data or to be Zeros. did any one here know a way to do that?? vijeo citect 7.4 thank you
  18. Modbus Addressing in Weintek HMI

    Modbus addressing in Weintek HMI to poll data from Temperature sensor through RS485. In my system i have connected Temperature sensor to I/O Scanner has output in terms of RS-485 which directly connected to COM3 Port pin. No. 6 (as Negative) & 9 (as Positive) of HMI (Model No: MT8071iE) and HMI connected to PC via ETHERNET. I want to read temp on HMI screen via MODBUS protocol. So, can you please provide me instruction about addressing of MODBUS register in Easy-Builder Software so can read data of corresponding register. Because when i do compile i got an error like " Device no Response". I hope i will get reply from your side as Fast as possible to overcome this problem. Thank you.
  19. Delta eserver problem

    Hi Guys, Im using delta eserver to get data from access and there is an error. How do you solve this? Eserver is installed on windows server 8  
  20. Cimplicity Auto Report Generation

    Dear All, I am having a problem with my cimplicity Auto Report Generation, When I Click on Generate Report, it shows "0 values collected" does anyone knows what's possibly could gone wrong here ??
  21. Hey everyone! New member here, and this site has always been a big help!  I try to help other folks too, but a lot of guys are super quick on here.   I've got a problem using some obscure components. I inherited a sensor network at work that uses Panasonic S-Link and I need to read them from a Q-Series. Panasonic makes a module that slots into the Q Series called an SL-VMEL-Q that I have.   My question is:  Did I do everything correctly on my Mitsubishi side? I put it into the parameters as an intelligent module with 64 points and I put the correct address in for the start I/O. Is that all I have to do?  This is the first time I used a module that wasn't on the drop down list when you add one in GX Works 2.   I can read and write to the buffer memory, but I can't get the unit to send to or receive from the sensors. I think the problem is that there is no end unit on the S-Link line (I don't know if it's just a terminating resistor or what), but it previously worked without one, so I can't be certain.
  22. Dear sir, i want sample program for modbus tcp for q series plc
  23. Hi everyone,  I am trying to use Kepware to communicate with my PLC setup which is the iQ-R Series R08PCPU.  I read the documentation which is available at https://www.kepware.com/getattachment/3daf1ac3-5c76-49ce-bbfe-f0fb1015f6cc/mitsubishi-ethernet-manual.pdf I read through the setup for Kepware and the setup procedure for iQ-R series but it still didn't work.  From the documentation, it said something about "using special ladder logic to enable ethernet communications is required.", I couldn't find anything about this online.  Here what I did in addition to the documentation: - Enabled IP Packet Transfer - Ping the PLC's IP Address which was successful Does anyone have any idea what I didn't do to establish that communication between Kepware and R08PCPU?  Thank you in advance. 
  24. Mitsubishi GX Developer

    Hello all ... i am a new plc user.. i am using D500 for taking value as it is a latched register.  i am taking value for a flow meter. i have two questions. 1. how totalizer is calculated from flow rate as my flow rate is in m3/h. 2. the value of register is gone upto 32000 approximately... i want that this value to go on.. i mean how 32 bit register is declared in plc .. a
  25. Please assist me with the following; regarding the ME96SSHA-MB Power meter data transition with Melsec-Q series PLC; We acquire to read various values on dedicated Modbus storage address registers at the simultaneous into a Melsec-Q series PLC via Modbus (TCP or RTU)  for calculation purposes. Naturally, since the reading of these variables are to provide accurate instantaneous results, it is a requirement that these values are to be read at one scan.   However, as can be seen below, there is a gap in address register range – of which, if all of these are scanned simultaneously, yields an exception error when read. This error is only avoided by scanning these data sets separately – which is not ideal for our application – since accuracy in calculations is imperative.