Search the Community
Showing results for tags 'cp1l'.
Found 77 results
-
Hello. I have CP1L EM30 with unknown IP. I have tried to use "Direct Ethernet Connection" with "Network Browser" but with no success. I have manually set the ethernet IP4 address to 192.168.20.20 / 255.255.255.0 I've got error: "The OMRON Ethernet Direct Connection Manager service is starting in Safe Mode because Windows APIPA is enabled. (0x82020003)Omron.Cxmw.Modules.SystemLibrary.SysLibException" The PLC does NOT have default ip 192.168.250.1. What Can I do? Please help. Thanks. BR, Andrej.
- 9 replies
-
- cp1l
- unknown ip
-
(and 1 more)
Tagged with:
-
From @SamuelT Please, I want to know if you know how to communicate two plcs omron CP1H (master) and one CP1L (slave). The master CP1H will send 10 DM memories to slave CP1L. Now I have this configuration: CP1H MASTER PORT: CP1W-MODTCP61 MASTER IP: 10.150.1.5 SLOCK: 1, DIP SWITCH PLC # 4 = OFF CP1L SLAVE PORT: CP1W-MODTCP61 SLAVE IP: 10.150.1.1 SLOCK: 1, DIP SWITCH PLC # 4 = ON I use the modbus RTU function blocks, but the master PLC does not communicate or send the DM memory values to the slave PLC Thank you very much for your reply if you have any example program it helps me a lot MRTU_CP1L SLAVE.cxp MTCP CP1H_MASTER.cxp
- 2 replies
-
1
-
- modbus tcp
- cp1h
-
(and 1 more)
Tagged with:
-
Following my post from yesterday and the fix proposed by @chelton, I went ahead and expanded the solution to multiple PLCs in the shop. Now I'm stumbling on another layer of difficulty : I have to RECV in a CP1L-E (10.1.14.214) from a NJ-301 (10.1.46.118). Both PLC's are physically connected to the same Ethernet Switch in the shop, but the IT guys decided to add a new subnet for PLCs and equipment some time ago. I read Michael Walsh's answer on this post but I couldn't figure out how to set things up properly with 2 subnets that are not consecutive. What do I need to setup in the CP1L-E to be able to RECV properly? There is certainly a routing table setup that I need to add but I cannot figure it out by myself. Here is the current setup : In the NJ, I have a UINT variable mapped At %W0, Network Publish set to "Output" The RECV command in the CP1L-E is as follows: C0 = 0001 (1 word) C1 = 0001 (Port 0, network 1) C2 = 7600 (node 118, unit address 0) C3 = 0203 (port 2, 3 retries) C4 = 0032 (5 sec timeout) The Built-in Ethernet parameters in the CP1L-E are attached Thanks !
- 10 replies
-
- communication
- cp1l
-
(and 2 more)
Tagged with:
-
Hello. What is the best option using TCP/UDP communication to use CP1L-EM40 as SLAVE / IO Expansion? For MASTER I’m using CJ2M-CPU31. Since now I’ve used FINS _CPU010_SendData and _CPU011_ReceiveData function blocks. The problem is, that I’m communicating with 6 slave IO units and to read/write all 6 units it takes up to 1 – 2 seconds. I’ve tried Ethernet/IP protocol but CP1L units doesn’t support this protocol. Is there some kind of different TCP/UDP protocol which is faster than FINS? In older days you could use PC Link but this protocol is for RS232 / RS485 comm. I know I could use CP1W-EIP61 but I don't have this adapter and I can't afford to buy one Thanks.
-
I'm trying to simply send 1 word of data from 1 CP1L-E to another one, on the same subnet. I dont have any CP1W-EIP61 adapters and wish to know if it's possible to do it using only the built-in Ethernet Port on the PLCs. Setup: Sender PLC's IP address is 10.1.14.62 Receiver PLC's IP address is 10.1.14.214 1 word of data needs to be sent from W20 in the sender to W20 in the receiver Both PLC's are connected to the same network switch in the plant My current control word parameters : C = 0001 (1 word of data) C+1 = XX00 (XX = which port number should I use?) (00 = local network) C+2 = D6FA (D6 hex = 214 decimal, which is the node address of the receiver PLC) (FA = Unit address setting for CPEL-E Built in ethernet port) C+3 = 0005 (0 = Response required, 0 = port #0, 05 = 5 retries) C+4 = 0064 (10 sec monitoring time) In the receiver PLC, the W20 word never changes. In the sender PLC, the Error flag (A202.00) always turns on. What am I doing wrong?
-
Hi, I have a problem with serial communication (no protocol) using rs485 module, the received data is error. I'm using CP1L CPU, CP1W-CIF11 module as transmitter, and USB to RS485 converter as receiver. When I check the received data on PC, it's incorrect (bit error?). I just send 2 bytes data, 0x61 ('a') and 0x62 ('b'). My configuration: DIP switch CPU 4 = off, DIP switch CIF11 1 to 6 = on,on,on,off,off,off, 2 wire RS485. (I also attached the program and settings) https://postimg.cc/gallery/pr293Jc Could you help me to solve this problem? Thanks Program and Settings: Result:
-
Sorry its long !! I am recieving text from a GSM modem for text msg Send and receive (SMS) works ok but would be better if I could make use of the start code and end code. This way I could cut down on all the crap that is received when a text arrives. I get this CMTI: "SM",0 I have it stored into D80 and I have that trigger a TXD that sends AT+CMGRD=0 and that tells the GSM to send the msg (The 0 is the current msg in memory) ------ The problem is that there is Carriage Return and Line Feeds in the received msg ---- AS below ((AT+CMGRD=0 +CMGRD: "REC UNREAD","+19028991212","","22/10/20,16:57:54-16" Hello this is the msg OK)) When the PLC sees the carriage return it stops receiving data. And I have no start code or end code setup. (I am using characters received) The way around this is to set a high character count in the RXD (More than the actual msg (More than the msg length) The main issue with that is I get garbage in as the msg gets bigger. Its unreliable. I clear the port after each receive and that helps but still get the odd garbage. (Never get garbage when connected to a terminal prg). Any Ideas???? ps Even the Start Code is unreliable as it will start receiving a few characters late. Rob
-
Hello there. How to transfer data from one memory area to another using macro ? Data Type - Double Word Length - 4 Format - BIN Integer - 3, Decimal - 1 From Area - D To Area - LW
- 6 replies
-
- nb
- nbdesigner
- (and 11 more)
-
I am trying to change the subnet of this CP1L plc. Currently it is at 192.168.250.*** and I would like to change it to 192.168.54.***. I already tried starting fresh by writing to the controller with ip 0.0.0.0 and then putting my desired ip address after. When I try to write to the controller with a subnet other than .250 for example 192.168.54.13, the controller saves the node address(.13) but keeps the same .250 subnet which results in me being able to ping 192.168.250.13 successfully but get no response from pinging 192.168.54.13. Yes I did change my local network card when pinging different subnets and also did a network reset in CX-P after every ip change. Let me know if there is anything I am missing!!
-
hi i am tryning to make a program that takes 4-20ma signals from a pressure sensor and converting it to show ML on a hmi screan. im using a CP1L with a CP1W-Ad041. but i cant figurout how to set up the setings in cx programer correctly. any tips?
-
Please Help me, I want to connect aczet brand weighing machine CG203L to PLC CP1L-M. But several times I tried it didn't work, I've tried repeatedly in the settings section to adjust the baud rate and mode and have tried one by one but to no avail. Can any of your friends help? thank you
- 2 replies
-
- weighing machine
- plc
-
(and 2 more)
Tagged with:
-
Hello every one in this video, you will learn about Omron PLC PID Control (CX-Programmer) you could download as free by using the below referral link: Omron PLC PID Control (CX-Programmer) | Udemy I marked free download for 1000 people. I hope it will be useful for you. Regards Mehdi
-
Hi, I have a CP1L and CP1E Omron PLC, and I try to make communication between my PLCs and my system (raspberry pi with Linux OS) using Node-red and specifically using the OMRON-FINS node ( https://flows.nodered.org/node/node-red-contrib-omron-fins) and more detail ( https://github.com/ptrks/node-omron-fins ). So I’m looking for a module to create an Ethernet port for my PLCs. ( both PLCs have RS232 port) . Can you please guide me to find a compatible RS232 to Ethernet module for my PLCs? Thank you
-
how to sett up cx programer settings to use hmi/nb5q-tw00b with a CP1L-L14DR-A? and what address do i use for I/O on the hmi?
-
Hi, I have a project including 32 digital outputs, 8 Pt100 probes, 4 thermocouples, and 4 analog inputs so I have to choose an OMRON PLC. The supplier in my country has only CP2E and CP1E PLCs. Is there a way to connect more than three expansion modules to the PLC? On the website is stated that the maximum number of expansion units is 3, if the answer is no, is there a solution to this problem? Thank you
-
Hi there! I'm programming a CP1L-E CPU to control 3 3G3MX2 inverters via Modbus. It got some things right, like the INV002_Refresh_X31 block and its parameters. The thing is, I also want to read some parameters from the inverter using the INV206_ReadParameter block. My doubt is, do I need to be careful so both blocks don't execute at the same time and use the serial port at the same time? Is it better to use one INV206_ReadParameter block for each parameter I want to read? Thanks in advance!
-
Hi all im back to trying to get my inverter to work but this time with modbus, from this post http://forums.mrplc.com/index.php?/topic/38445-controlling-mx2-inverter-without-modbus/ and im stumped, im sure its just one thing somewhere messing it up i have a cp1l-el20 with a cp1w-cif11 and a 3g3mx2 inverter and am attempting to control it via modbus, it is wired up as follows, sp+ to RDB+, sn- to RDA-, common to the plc pin and plc output pin 100.00 to logic input 1. im using 100.00 to put it into run mode the paremeters ive put in are a1=3,a2=1, a4=50, c070=3, c071=5,c072=1, c074=00, c075=1, b27=1. im using MOV to set my speed to d1001 attached is my inv002_refresh x31 fb thanks to any1 who can see my silly mistake
-
I am trying to get a NT 21 to link to a CPL1 I have both set to Host link 9600/7e2 I have it set to read a DM All I get is system initialzing I am using the same cable i used to build the screens with NT Series Support tool I sent and recieved the screens so the cable works The com port on thee PLC is flashing I have tried starting the PLC in run mode and Monitor Mode What did i forget to do ??????? Rob
-
Hello everyone I am working on modbus TCP protocols to communicate between SEW drive and Omron PLC CP1L-EM. I am following modbus TCP function block from Omron, But i have updated that block because of is not fit to SEW modbus communication. Currently, I am sending a control work to SEW but I am getting error on Modbus TCP from SEW drive, which is invalid data. So I am looking your help is you work with SEW drive before and communicate over modbus, then please let me know how to make a data string for read and write (SEW Drive function 23). I am using 3PD data structure. Thank you
-
Hello friends, I am an Omron PLC user, but have never used modbus before. I have to connect an Omron CP1L-m to Beckhoff bk7300 via modbus serial gateway. 2-wire RS-485 connection (CP1W-CIF11). I have seen an easy to use Modbus RTU master for CP1L CP1H CJ1 CJ2 CS1 but the examples are not for dual port CP1L-m. If I change the PLC model "CP1HCP1LModbusDualPort" to "CP1L-M", the compiler tells me a lot of warnings about variable types. Is Modbus RTU Master easy to use for CP1L CP1H CJ1 CJ2 CS1 compatible with CP1L-M dual port (port 2)? I have tried to use it but it didn't work, error 02, illegal function code. Somebody could help me? Thank you Enric
-
Hello all, I have a master PLC(CJ2M) which is communicating with slave 4 slave PLCs(CP1L). one of the PLC have communication error, upon checking in cx-intergrator it shows that all the other slave PLCs and other components are connected to network-1 and faulty PLC is connected to network-0. Unfortunately, I couldn't change it as cx-intergrator doesn't allow me to change download the changes. So anyone can please help me with this issue. If you know the troubleshooting way then please reply. Thanks in advance. -Yash
- 1 reply
-
- cp1l omron plc
- cx programmer
-
(and 1 more)
Tagged with:
-
Hello All, Please Help Me.. How I can to connect Omron CP1L-M + CP1W-Cif11 with Mitsubishi Inverter D700? Thank you. Omron modbus belum fix.cxp
-
Hi, I may need your help. What particular Wonderware Intouch driver needed to hook with Omron CP1L-EM ? Thanks for your help. Regards, Jay :)
-
Hello guys I am a beginner in FINS UDP communication and I am trying to do a FINS UDP communication between an omron PLC CP1L-E in client mode to communicate with my PC that is in server mode, I am using the SocketTest v3.0.0 program that is in listening mode and still was unable to receive any information from the CLP, can you help me? The program and some images of the simulation are attached Thanks for reading SERVER PC IP ADDRESS 192.168.15.160 CLIENT PLC IP ADDRESS 192.168.15.10 tcp socket (1).cxp
-
Hello there, Today i have commissioned my first project with OMRON make PLC. Model: CP1L-EM40DT1D. (CX-Programmer) I have 2 built in 0-10V Analog Inputs on the plc. for analog input no-1 i get the digital value of 0-1000 in specific plc register address corresponding the 0-10V. (Factory setup) But today on site, i have noticed that some miner value of 0 to 50 is always coming and fluctuating very fast in that register, however the transmitter are genetaring 0.0V only (I have checked using digital multimeter with high precision) PLC and Transmitter are already grounded and all the cable connections are tight as well. so how to overcome this high fluctuating value ? is there any setting to filter the input ?