Search the Community

Showing results for tags 'servo motor kinetix compactlogix'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 163 results

  1. Is there a way to monitor the Temperature of a Servo Motor on Allen Bradley Servo motors... MPL? PLC: CompactLogix 1769-L30ERM Drive: Kinetix 6500   Motors: MPL-B310P-MJ72AA, and  MPL-B560F-MJ72AA I would like to be able to monitor the temperature, and flash a warning screen on the HMI if the Motor gets too hot, or perhaps shut down the operation before the Motor overload trips. The drive and PLC are connected through Ethernet IP What I don’t know is if that Motor heatsink temperature information is available to the PLC.
  2. ACD file to PDF

    Hello, I have an .ACD file but do not have any software to read the controller tags. Can anyone please help me convert the file into a pdf? I can see from Notepad that is was made using RSLogix 5000 V21.   Thanks! G Pump_17_11_09.ACD
  3. Hello, Have this error come up constantly and can't be reset. Motor hasn't tried to drive at all. Second motor showing same problem. This is a new configuration on new machine. Other inverters configured without any problems. Anyone seen this before or any ideas what could be the issue.
  4. Hi Every one, I have two 2198-P070 bus power supplies for that I’m using for four Kinetix drives, 2 drives per power supply, all controlled by one processor (5069-L350ERMS2). I have an enable contactor setup for each power supply for each set of drives. I have them configured as DC bus groups 1 and 2 respectively. I had the first set of drives working, setup inside the motion group, with no issues. When I added the second power supply and drives. I found that when I added them to the motion group I couldn’t get the enable contactor to close for the first set of drives. I f I took them out of the motion group and made them ungrouped then the first contactor would close but then I couldn’t get the contactor on the second set to close. Do you have any thoughts as to what I might be missing to get these to work? See the screen shots for more detail. Let me know what you think.  Also, I have heard that only one motion group is allowed per PLC, but my question is : Can I use  sevral axes and Power units in the same motion group? 
  5. This is a bizarre one... CompactLogix, 1769-IF8 with 1492-AIFM8-F-5 wiring system. My client has reported several instances where one of his flow rate displays is frozen at its maximum value.  Each time, I have gone to the site, found that the value in the analog input tag is at full scale, and measured more than 20mA at the input - as much as 28mA!  I measure it using a clamp-on meter and I measure it at the input module (1769-IF8) and the external, pre-wired terminal block (1492-AIFM8-F-5).  I cycle power to the PLC.  No change.  I cycle power on the transmitting device.  No change.  I disconnect and reconnect the input (signal wire at the module or the terminal block) and everything goes back to normal.  This has happened on multiple channels on multiple input modules and with two different types of transmitters. I didn't install this system, but it seems to have been done properly and it had been running fine for many years.  These problems just started happening out of the blue. Has anyone out there had any similar experience?  This is a new one for me after more than 25 years in the business.
  6. converting rs232 data

    Hello, I am trying to receive data from a scale via rs232. my setup; compact logix l18er with a 1734-rs232ascii point IO module to receive the data. I am receiving data from the scale, but I have very little understanding of ascii, so I do not know how to convert the data I am receiving to something use-able. any help on how to convert the data to something I can use or where to even start would be much appreciated. using a scientech ZSA 210 scale https://scientech-inc.com/media/downloadable/files/links/1/2/12222-d_rev-f_instruction_manual.pdf
  7. Hello guys, I am running an application for packaging measurement using a sick DFS60B incremental encoder (programmable from 1 to 10000 PPR). In more detail, it passes packaging on a conveyor belt and we have created an inspection station and an expulsion station (defective packaging), so we use the encoder to check at specific points of the packaging for defects (we use special sensors to check defects). ) (there are four in total). However, the problem we are having is the following: When reading the encoder in the PLC, the same means that performs "jumps" and does not enter the windows (GRT and LES) created on the ladder, ie, as if it were not continuous. . I understand that because the VHSC24 card works at 1 MHz in counter mode, this type of problem should not occur according to our application is not even 100 KHz. For example, our case: Using 1000 PPR and the motor speed (coupling output) is 3600 RPM (in practice it is around 1750 RPM) the frequency is calculated as follows: F = (PPR X RPM) / 60. : F = (1000x3600) / 60 = 60 KHz, ie 60 KHz is much less than 1 MHz, I think this kind of problem does not occur. Application Info: . Studio 5000 V31 . PLC Model: Rockwell 1769 - L19ER-BB1B CompactLogix 5370 . Encoder Card: 1734-VHSC24 / C . Incremental Encoder: Sick, DFS60 up to 10,000 PPR and HTL Electrical Interface. Using a 200 mm circumference / perimeter wheel. . Motor Nameplate Data: 1670 RPM, 0.37 kW / 0.5 HP, 60 Hz . Inverter: Weg CFW500, Output Frequency 62 Hz. Card Settings we use RPI: 2 ms Type: Counter, but we already use it as Encoder X1 Store Count Mode: Disabled Filter: No Filter, but we use 50 KHz and 5 Khz filters in our tests. Counter Attenuator: 1 Wiring Diagram VHSC24 We turn on encoder A at input 0 and encoder Aret at input 1 In logic (Structured Text) Using the PMUL instruction to convert encoder (Pulse) data to mm scale. (Ladder) The window comparisons part (GRT and Les) and other part of the process. We emphasize that we performed the tests also only with the reading and comparison part of the data, excluding the other parts, precisely to verify the issue of Scan, but the problem persisted. If anyone here in the forum has some information that can help us, I would appreciate it.
  8. hi, We want to integrate Allen Bradley L16-ER with Zebra Printer GT800 and Zebra Scanner Li4278 with RS232 extension Card. We have hardware : 1.ABPLC L16-ER 2.1734-232ASC 3.Zebra Printer GT800 4.Zebra Scanner Li4278 5.Communication Cables  We are not able to receive and transmit data from and to Printer and Scanner
  9. Virtaul Axis - Simulation

    Is it possible to simulate a servo axis in Sysmac Studio? Can you create a virtual axis and then set velocity & position for this virtual axis? If this is possible, is there an example program that anyone can share with me? Thank you. Happy new Year! 
  10. Getting this error while adding MC_TorqueControl. I want to control torque from HMI value. Using R88D-1SN08H-ECT drive and R88M-1M75030T-S2 Ac servo motor with NX1P2 PLC. Newbie Here. Please support. Error    1    The Axis parameter of the MC_TorqueControl instruction does not support single-axis position control axes.    Program1 Section0    Row 6  
  11. stepper motor position control

    Hello, I need to have a cx-programmer code which I can control my linear actuator position by setting 3 positions with timer, I am using a CP1L pro'skit
  12. This may be more of a Zebra question than a PLC question but I will post it here. I am using Zebra's Network Connect to enable communication between a CompactLogix L13ER and a ZT410. My issue is that the QR Code omits the 5 elements of the array in Field 1 of the CompactLogix. I expect the first two elements in the array to be ignored per the manual but the first 5 has me puzzled. All the characters in the text shows up fine. I have attached what I am seeing. If you have a QR Code reader, you can scan the QR Code.
  13. Remote Access to CompactLogix PLC

    Can the PlC be accessed remotely. If I hook the CompactLogix L32E up to the internet WAN, would it be possible for an engineer to access and make changes to the program remotely?? Or does it have to be done onsite through the LAN.
  14. Hello,   I have  a project where I need to run 2 Omron Servos 1S at same time with 1:1 ratio. I created virtual servo axis and attached my 2 physical axis to virtual one ( screenshot from Sysmac studio attached). For some reason when 1 of the axis has a fault, my whole virtual axis goes down. For recovery I need to to do GearOut and GearIn again. In one of the moments I'm losing count in my motion that cause issue later. I believe that I'm doing something wrong.  Can somebody help me to understand how I can keep my synchronized axis all the time? Thank you in advance!  
  15. Dear All, 2094-BM01-SA0192 was installed on a machine, now we are installing 2094-BM01-SB1111 Problem is that when we Power ON, it start showing 0,1,2 and remains on 2 while in old SA0192, it goes to 1,2,3 and 4 then comes to normal display. can anyone suggest the solution? waiting
  16. Sample blocks for S7 1200 plc's

    Hi experts, please share the sample blocks for the EDITABLE TIMER block it should be editable from HMI(Siemens). And also motor run hour block. Actually i am having all blocks in tia v12 version and sadly i dont have the old software to convert it again. So please share the blocks that it shoud be work in TIA V14 for s7 1200 plc's. Please note that the blocks should use add instructions to calculate the time because i don't have much memory.
  17. MR-J4-60GF-RJ Programming

    I am new to Mitsubishi (only done Allen Bradley) and Im tasked with programming a MR-J4-60GF-RJ servo drive with a HG-SR motor. I am using GX Works 3 and have a R02CPU and I am wanting to use CC Link IE Field Basic communication with this. Do I have to use the point table to move this motor from "Point A-B" or can I send absolute positions, speed, etc to a given position. Any advice/programming examples would be great. 
  18. Autotuning Kinetix 350

    Hell PLC World! I have been trying for several weeks in my spare time at work to tune an Allen Bradley Servo Motor.  Below is the list of hardware I am currently using: - CompactLogix Motion Controller (1780-L33ERM) - Kinetix 350 Driver (2097-V34PR5-LM) - MPL Series Rotary Servo Motor (MPL-B310P-MJ74AA) I have been using RSLogix5000 for testing and I plan to use it to develop a simple conveyor type program later.  I have tried a list of things which will be below, but to no avail, I cannot simply jog the motor for any period of time without triggering a position, velocity or bus voltage error.  I have tried changing the motor, driver and feedback cable to no avail.  Here is the process I have used: 1) Add the hardware to RSLogix5000 (PLC, Driver and Motor) 2) Configure the motor 3) Run the hookup test.  This works flawlessly.  The motor will slowly turn independently on the feedback test for as many revolutions as I input.  This is what makes me think I am doing something wrong in the tuning process. 4) Run autotune process with the velocity, acceleration and jerk set well below the limits of the hardware.   5) Attempt manually control motion 6) Recieve error I have tried changing the input from trapezoidal to S-Curve, changed velocity and position limits, manually tuned velocity gains in a myriad of configurations.  I have swapped legs on the 3 phase input (which made matters worse). I suppose it is possible that multiple pieces of hardware are faulty because this equipment was previously used, but I still cannot wrap my head around why the hookup test would work so flawlessly, yet I cannot just get the servo to rotate at an equivalently low speed. If anyone recognizes my mistake, I would be eternally grateful.  I am an intern studying control systems in graduate school and as popular as AB is, I would sure like to get some experience with it.  Thanks in advance!  
  19. Hello, I have a project where I need to synchronize 2 servos. I use GearIn command to sync this servos. I created 1 virtual axis and attached my 2 physical servos to virtual one. Based on application logic I need to stop sync servos when count from sensor reached max value. To stop the servos I'm using ImmidiateStop command. For some reason stop point for this servos variate based on servos speed.    How I can improve my stop point?      Thanks!
  20. Alice Sales Manager Changsha Zhinian Automation Equipment Co;ltd   Te/whatsapp:+8613341312293 Fax: 0086 0731-82292217   Email: info-zna@zhinianauto.com   Main products: PLC: Mitsubishi, Omron, Panasonic Inverter: Mitsubishi,Fuji, Omron,. HMI: Mitsubishi, Omron,, Proface,FUJI, AC Servo: Mitsubishi, Omron,FUJI Sensor: KEYENCE,OMRON   Air cylinder: SMC Below is our best price product list: MITSUBISHI: 1.MR-J2S/ MR-J3/ MR-ES AC servo pack ( amplifier, motor, cables ,connectors) 2.FR-A700, F700, E700, and D700 inverters 3.GOT1000 and GT1500 Human machine interfaces 4.A, Q and FX series PLC(FX1N/FX2N/FX3U/FX3G/FX1S) plc OMRON: 1.C200H/ CQM1/ CS1W/ CJ1W/ CP1H/ CP1L/ CPM1A/ CPM2A/ CPM2AH plc 2.SYSDRIVE 3G3JZ/3G3MX2/3G3JE/3G3RX Series inverter 3.NS5-V2/ NS8-V2/ NS10-V2/ NS12-V2/ NS15-V2 Human Machine Interface 4.E3JK/ E3JM/ E3Z photoelectric switch 5.TL-Q5/TL-W3/TL-N Proximity switch 6.E6B2/E6C2/E6CP rotary encoder 7.G3NA-205B/G3NA-210B/ G3NB-240B Solid State Relays 8.H3CA/H3CR-A/H3DE/H3DS/H3JA/H3Y-2 Solid-State Timer   Contact me if you are interested, thank you !  
  21. CompactLogix E/IP to Kuka KRC 4

    Hello everyone,   I need to communicate a CompactLogix to a Kuka KRC 4 by Ethernet/IP but I do not know to generate the EDS file..... any clue please ?
  22. Stepper Motor Control

    can anybody Know how to control stepper motor using PLC
  23. Mitsubishi FX2N, Servo Output problem

    Hello guys, I am facing a problem that our Servo is generating output for only reverse direction, when we give forward command from HMI the output Y0 is active but when we give reverse command same outut Y0 is high, other output which is Y4 is not high, what could be te possible reasion.
  24. Mitsubishi FX2N, Servo Output problem

    Hello guys, I am facing a problem that our Servo is generating output for only reverse direction, when we give forward command from HMI the output Y0 is active but when we give reverse command same outut Y0 is high, other output which is Y4 is not high, what could be te possible reasion.
  25. Hi all. I have a Kinetix 350 and an AB TLY servo motor. I'm using the drive's STO function. AC power is supplied into the drive, passing through an "M1" contactor. It makes sense to m e to keep that contactor open, preventing AC power to the drive, until the drive is fully awake.  Is that what you guys do? Someone suggested to me in another forum ( http://www.plctalk.net/qanda/showthread.php?t=121021&highlight=drive+awake ) that there is no reason not to supply power to the drive right away because the STO function is inhibiting power to the motor anyway.