Search the Community

Showing results for tags 'fins node ethernet/ip'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 255 results

  1. Problem: I am getting a control sync fault on 2 recently installed kinetix 5500 but only when my programing PC is connected to the machine network.  Install and setup all went great over a 5 day period.  Then all of a sudden I started to get this fault. Sometimes 100 times in an hour.  As soon as I go offline, and unplug my PC the problem goes away.  I have also tried another PC connected to the Machine network and still get the same result.  Sometimes machine can run for hours with my PC connected with no problem.  I do not have to be online with controller for fault to occur. Setup: I have the 2 K5500's ethernet ports daisy chained together, and then connected via shielded CAT 6 cable directly to port 2 of the Compact Logix Controller Coarse Update is set to 3.5ms and utilization's are at 33% and below.(I have tried the default 2ms with same results) Ethernet modules are configured with FW rev 7.013. Machine network is isolated.(not connected to plant network or internet) Equipment: Compact logix L33ERM Running version 30.01. There are a total of four servos in this system all running over ethernet.  2 Kinetix 350's(not affected), and 2 kinetix 5500's. I have tried: separate ethernet cables for each drive ran through a switch different ethernet cables resetting coarse update speed connecting a different PC for programming   I am just not sure where else to go with this.  Thanks in advance for any help.  
  2. Hi. what i've gathered, i need an EDS-file for the siemens s7-1200-system to be able to specify an ethernet connection in sysmac from the omron plc side to connect to the siemens ethernet/ip server. Anyone know where or how to get an EDS file for the siemens plc so i can import it into EIPprofiles in sysmac?
  3. GOT2000 <-> Omron CJ PLC

    I have an application where I'm using GOT2000 to read data from the weighing unit using RS232 and I send this value to Omron CJ2M through Ethernet/IP. Some variables from that PLC are connected to the elements of the HMI. The problem is when writing the weight value to the PLC through script or Data Transfer is disabled, the RS232 reading works fine, it's fast, etc. However, when I enable the script which writes data to the PLC, the RS232 slows down by a lot, like it refreshes every 2-3 seconds. If i set the script to execute like every 1-2 seconds, it is working better (still slower compared to when the script is disabled) but I cannot leave it like this, because the weight is used to control some valves, pumps, etc. Enabling script doesn't slow down normal communication with PLC, because I tried to test it by displaying the value of seconds from PLC on the HMI and it refreshes every second. Does anyone have idea why such tiny script causes so many problems with RS232?
  4. I'm trying to exchange some data between two controllers. I've used a manual which describes Tag Datalink communication. Everything works fine on the Bradley side, which means I can read values from Omron without problems. However, on the CJ it isn't working. In the Network Configurator I get error every 10 sec (Tag data ling error, code 03D5) and cannot read any data from AB. When I open Connection Structure Tree I see that the input tagset from AB has 'Broken path (0000000000000)' and Unknown Device right next to IP address. I've tried using EDS from the Rockwell as well as uploading it from AB PLC directly - I don't know if it might be EDS issue. The only thing I noticed that inside CJ2M-EIP21 EDS it says that Ethernet/IP is Class 1 connection, however in the 1769-L35E EDS Ethernet/IP is Class 2 connection. Have anyone ever had such a problem?
  5. Hi all,  I am trying to modify the date and time of several PLCs from other PLC. Them are all CJ2M, and they are all in the same ethernet network (192.168.100.xx) and in the same FINS network (#1). I am doing it using the FINS command 07 02 ("CLOCK WRITE") with the CMND2 instruction. It is not working entirely: the clock time is being modified at the specified node; however, I do not get the FINS response (expected 07 02 00 00). If I modify the number of retries of the CMND2, the command is repeated all the specified retries though the clock was already written on the first try.  The D+0 and D+1 (response channels) are always #0; nevertheless, the I+1 ("Communication Completion Code" channel) allways receives #205. Acording to the manuals, this code is for "Response Timeout". I have tested it with 10 retries and with 10.0 seconds of monitoring response time, but it is working in the same way: the clock is modified fast enough, but I am not getting the FINS Response and the I+0.00 bit is ON after 100 seconds...  I have been also doing tests with the OMRON's Etherway Software, sending the same FINS command, and here I am getting the response properly. (???) I would say the FINS network was set-up correctly. All the PLC were set in network #1 with Cx-Integrator. In fact, they are currently sharing several channels using the SEND command on this network #1. I don't know what I am not doing right... Any idea?  The ladder is attached as .cxp and as .png. Thanks a lot.  Best regards.  CLOCK_WRITE.cxp
  6. Has anyone have any experience getting a Wieland Safety plc (SP-COP1-ENI) communicate with an Omron Plc (NX102) via Ethernet/IP? EDS file installed, connection is set as per the documentation yet  I cannot get it connected.  
  7. Error **03 Special Parameter Error

    Hello I have a problem whit PLC mitsubishi FX3U thernet communication, we have a module  FX3u-ENET-ADP. and we have the error "**03 Special Parameter Error".  
  8. OMRON CJ1W-ETN21 Node Number

    Hello. I'm having CJ1M unit with ETN21 card on remote site. I can't drive to the site and look at the rotary switches to determine what is the units NODE NUMBER. I can connect to the PLC remotely using CX-Programmer. Is it possible to read the setting of NODE NUMBER remotely? Is this NODE NUMBER settings saved somewhere in CIO or DM area? Thanks. BR, Andrej.
  9. NB to CP1L-EM

    Has anyone connected a NB HMI to a CP1L-EM via ETHERNET NB = Node 2 IP 192.168.1.152 PLC = Node 1 IP 192.168.151 Using my Network Switch/HUB NB works fine when setup to com 1 on the PLC (Wrote the PRG using serial) NB says no response from PLC Is there a secret setting in the PLC i need ? ? Rob  
  10. Hello All, I would like to control Powerflex 525 drive with Omron NJ301-1200 PLC via Ethernet/IP (Set speed, start, stop). I've gotten until the part where I downloaded the necessary .eds files of the drive and imported into my Sysmac studio. However, I'm stuck after this point while assigning target variables and Originator variables and eventually setting speed and controlling the vfd. I've attached images for your reference.
  11. NX1P2 Fins

    Hi:       Has anyone use Fins Command with NX1P2 (or any NX/NJ). I try with Multiway with "[!]: Command format error (1004)" Below is the command from multiway 800003000100000100060101820001000003 Data memory are define in global variable table as  A as %D1, B as %D2 and C as %D3. The relevant setting are done on Fins Setting and Memory Setting in the PLC.   Anyone ?    
  12. NX1P2 Fins

    Hi:       Has anyone use Fins Command with NX1P2 (or any NX/NJ). I try with Multiway with "[!]: Command format error (1004)" Below is the command from multiway 800003000100000100060101820001000003 Data memory are define in global variable table as  A as %D1, B as %D2 and C as %D3. The relevant setting are done on Fins Setting and Memory Setting in the PLC.   Anyone ?    
  13. I'm trying to understand the basics of using a serial to ethernet converter such as this Comtrol DM-EIP-2101, with Studio5000 code. Basically I have a weighing machine that only outputs data via RS-232 and I need to send that data to a PC that will process it through a Studio5000 program and have the data displayed on an HMI using FTview SE. Is it as simple as just connecting the serial and ethernet to the converter and it does all the work? Obviously checking ip addresses and firmware will need to be verified. The main thing I am unsure of is the process of passing the individual data packets from the machine to the Logix code on the PC,  things like what the weight of the item was, was it over weight or under, etc....  Would there be an AOI or tags built into the software for a machine like this Checkweigher? I've worked with much smaller items like Cognex Dataman cameras and I know you can just use their AOI that allows you to simply call a tag if you want to display information like if a scanned barcode was correct or whatever. If anyone has done something similar I'd appreciate any guidance. It can be difficult getting the information from the manufactures so I'm looking for answers anywhere I can. EDIT: I guess I should also clarify that only using one or the other (serial or E/IP) is not an option. It will be a serial connection from the Weighing machine to the converter and then Ethernet to the PC.
  14. I'm trying to set up an Ethernet/IP communication with a CIP block between a Micro850 and a SMC EX600-sen3 pneumatic Module. I can read the inputs of the module with the configuration below, but I CANT write to SET or RESET the digital outputs. There are NO errors showing communications issues in the CIP Generic Block I am using... I read that for some reason, it seems that there are problems with writing thru Ethernet/IP protocol between Micro family and other devices not from Rockwell... Does anyone know if there is a way to make it work? Configuration that is working to READ: CIP Service Code:     14 CIP Class ID:         4 CIP Instance ID:     100 CIP Attribute:         3 CIP Member ID:         0 Configuration that is NOT working to WRITE: CIP Service Code:     16 CIP Class ID:         4 CIP Instance ID:     150 CIP Attribute:         3 CIP Member ID:         0
  15. Hmi modbus TCP/IP device communication

    Hi all; I have Delta DOP110 IS hmi and i have a modbus tcp device. I want to communicate hmi and device with modbus tcp/ip but i didnt understand device's register address. For example, input bytes 0,1 analogue control word, What is the register address? 40.000 or 40.001 can you help me ?  
  16. Hi, I have a CP1L and CP1E Omron PLC, and I try to make communication between my PLCs and my system (raspberry pi with Linux OS) using Node-red and specifically using the OMRON-FINS node ( https://flows.nodered.org/node/node-red-contrib-omron-fins) and more detail ( https://github.com/ptrks/node-omron-fins ). So I’m looking for a module to create an Ethernet port for my PLCs. ( both PLCs have RS232 port) . Can you please guide me to find a compatible RS232 to Ethernet module for my PLCs?  Thank you
  17. I have a bit of an issue with communication between GOT1000 HMI (I think the exact model is GOT1675V) and Q03UDE PLC over Ethernet. The GOT is set to 192.168.1.4 and PLC is set to 192.168.1.2 but I get the error "Communication Error. Refer to System Alarm in Utility Menu". Now how do I access the utility menu? I have tried to tap and hold on the upper corners of the HMI but nothing happens. I also can not switch between screens when I press buttons even though they are directly linked via screen #. Almost like the HMI froze up. Wonder if anyone had similar issue and what the solution might be. Thanks for your help.
  18. I recently wrote a simple java driver to communicate with Omron devices (CJ1 and CJ2) via the FINS protocol over UDP. I've installed this software at a number of my client's sites and it works well most of the time. However, I've encountered a number of instances where a CJ1 device will consistently return what looks like a valid response but every memory register I request will return zero. I've deployed the software to 5 sites with identical configurations. The sites have one CJ2 device and one CJ1 device.  The CJ2 devices work exactly as expected. Three of the CJ1 devices work exactly as expected but the other two have this issue where every value is zero all of the time.  This issue is not intermittent at those sites - I have never had it return anything other than a zero for any memory register for a CJ1 device at those two sites. Example: TX: [80, 00, 02, 00, 0a, 00, 00, c9, 00, ff, 01, 01, 98, 00, 00, 00, 00, 64] RX: [c0, 00, 02, 00, c9, 00, 00, 0a, 00, ff, 01, 01, 21, 08, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00, 00]  
  19. Hi! I would like to ask your help. I want to know more about the communcation systems what allen bradley use. Most important for me, is Ethernet IP communication, Controlnet communication, Sercos (servo) communication, maybe devicenet communication.  I know I can find some manulas on the web, but I thought I ask it here too, maybe you guys have some more documents which is contain more information. Every information is highly appreciated. Thank you very much guys.  
  20. Hi I am looking for a way to read and write data from PLC omron words, bits via FINS or EtherNet/IP protocol using python programming lang. Does anyone have any results in this? I really want to see your work, because all my attempts have failed. Thanks.
  21. Hello guys I am a beginner in FINS TCP communication and I am trying to do a FINS TCP communication between an omron PLC CP1L-E in client mode to communicate with my PC that is in server mode, I am using the SocketTest v3.0.0 program that is in listening mode and still was unable to receive any information from the CLP, can you help me? The program and some images of the simulation are attached Thanks for reading SERVER PC IP ADDRESS 192.168.15.160 CLIENT PLC IP ADDRESS 192.168.15.10 tcp socket_vms.cxp
  22. I am new to automation systems and devices and I just want to know how to connect two HMI's (each one would control different things) to one PLC using Sysmac Studio and NB-Designer via Ethernet. The model of the PLC is NX1029020 and the HMI's are one NB10W-TW01B and an NB7W-TW01B. I searched for info about this topic online but I couldn't find anything that worked for me, I saw an article from OMRON where they connect two NB's to the CP series, but in my case, NB designer doesn't allow me to insert more than one HMI in the same project, I also found something similar on a youtube video that gave me an idea about how to connect multiple HMIs exporting the pks file and importing it to another HMI project but I still can´t figure out how to add both to my PLC. I would thank you a lot if you could help me with this because I know it's not a rare implementation, just I haven´t found the right way to do it. I also leave the links to the Omron article and the youtube video I found. https://www.myomron.com/index.php?action=kb&article=1554 https://www.youtube.com/watch?v=rXx5lut7G9I
  23. Hey all, I am having some issues with a Keyence IV2 camera which has Ethernet/IP functionality.  To summarize briefly, it has been configured and reading the data into my PLC (NJ501) into a structure data type.  The issue I'm having is that I cannot control this on a bit level for triggering the camera, etc.  I was reading that a Union type is the way to go, but unfortunately, I stopped getting data into the PLC when setting it up that way.  According to the configuration guide for Rockwell and setting it up in the Network Configurator, I needed to go with the SINT type.  When registering the device, the 8-bit option was necessary since the Input/Output sizes needed to match.  This was predetermined by the EDS file for the IV2. I am stumped as to how to get the data to read into the Union Type, and any suggestions would be greatly appreciated. Thanks, -K  
  24. Hello, I have to make communication using Ethernet between omron CP1H and siemens s7-1500 plc. I was thinking about Modbus TCP or Ethernet IP using theese adapters: Modbus TCP - CP1W-MODTCP61 Ethernet IP: CP1W-EIP61 But I am quite new in Omron, and I am looking for some exapmple codes, FB. Do you anyone have experience with that?   Thanks for all responses.
  25. Good day everyone, First post here so hopefully I'm not violating community guidelines in anyway. I've got a system that has some 50 odd Micrologix 1100 and 1400 in use and I'm currently working on setting up an auto timesync for all of them using just 1 of the PLCs that will be my master time PLC. So far I've put together the logic for all the message instructions with the corresponding IP of the slave devices. I'm running. Into an issue with not being able to terminate/break the message connection on a PLC that I have already synced. Is this even possible to do on the ML1100. Once I get to 16-17 messages DN it starts to ER and will not complete any further messages. What I have is a message instruction ladder with a timed trigger to activate a MSG and write the RTC data then time down and connect and write to the next and so on. When it triggers the message instruction of one PLC it also fires an OTE to trigger the BK of the previous message instruction. However it doesn't seem to be actually cutting the message connection and holds it persistent until a power cycle/download event.