Search the Community

Showing results for tags 'DP700 Control logix EtherNet/'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 370 results

  1. We have been successful using the EIP4CCPU module in communicating Ethernet IP between Compact Logix And Mits Q PLC's. Always with the Allen Bradley as the master. However, we are presently trying to control a 520 PowerFlex VFD from the Q series as master.  Has anyone attempted this?
  2. Any tool to simulate Ethernet/IP for omron PLcs? I need to know the complete packate structure for Omron Ethernet/IP over Omron PLCs. I have read that we can use FINS command inside Ethernet/Ip packet . But how to get full pacakte structure.   Please help , it is urgent.
  3. Hi, I've been working with RSLogix 500, today i found that i was unable to connect to Micrologix PLC because in the RSLinx the Driver Ethernet IP that was configured to communicate whit PLC appears with a Red Cross. Yesterday everything was working. I've installed an antivirus software, i supposed the reason was the antivirus, but i've tried on configs and even uninstalling it, and RSLinx seems that can't reconigze the ethernet adapter (guess that means red cross) RSLinx 3.51 CPR 9 SR 5.1 RSLogix 500 Pro 9.0 Windows 7 Ultimate 32 bits Could you, provide to me some guidelines to solve this, or if somebody has had this problem, could share the solution? thanks in advance
  4. HOW TO CONNECT AB 1769-L33ER ETHERNET /IP TO MOD BUS RTU
  5. mitsubhishi serial drivers

    Hello write now i am working with Q6UDEH PLC  project in which (nextgen 2000) 6021 card is used for conversion of serial to Ethernet data & vice versa , is it possible  by only installing the Mitsubishi serial drivers ?? or can anybody tell me how these Mitsubishi serial drivers works ??  
  6. mitsubhishi serial drivers

    Hello write now i am working with Q6UDEH PLC  project in which (nextgen 2000) 6021 card is used for conversion of serial to Ethernet data & vice versa , is it possible  by only installing the Mitsubishi serial drivers ?? or can anybody tell me how these Mitsubishi serial drivers works ??  
  7. Hello everyone, I need the help to do setting of datalink between CJ2 and LOGIX-5324ER. The Allen bradley PLC was programmed by contractor and I have no software of it, so I am doing the network setting in CX-one network configurator. I tried to do the instruction in the Quick Start Guides on Downloads section here under Omron, but I couldn't find the option to register tags in network configurator. Is there anything wrong here? or is it possibly because of that they not support to do a datalink in these version of PLCs? They appeared like these in the pictures.
  8. MES US over Ethernet

    I have a Mitsubishi MES US network module ( QJ71MES96US ) connected to an Ethernet remote PLC (through an Enet switch). I'm not sure if this matters, but the remote rack has a Q PLC and an Ethernet master module kit (Q03UDECPU-EIP-K is the kit that has a Q03UDECPU and EIP4CCPU next to it). I am wondering if and how we connect the MES to a Q PLC over Ethernet to pull data. A coworker has configured the MES US module to talk to a PLC in a local rack, but never to a remote rack. If anyone can assist, or even reference a manual that would be appreciated, thank you.
  9.   In a certain area of our facility we have several machine that manufacture a handful of products. These machines were built at random intervals starting in the late 80's and consequently have a range of different PLCs that are used to control them (SLC 500 to ControlLogix L61).   The other areas of our facility use a server that has a historian installed (Canary) and the client (Axiom) is installed on our computer so we can view data trends in real time.    I would like to network our PLCs mentioned in the first paragraph to this historian to gather production and maintenance data.   I know that I need to network these devices through an OPC server (which we have).   Several of these devices have been connected through DH+ and/or Ethernet networks in the past but are no longer connected.   We recently connected some of the DH+ Devices to the Ethernet network (just to see if we could) with a Prosoft AN-X2-AB-DHRIO.   My questions are:   Are there any best practices for networking devices with different protocols, i.e. DH+, Ethernet, etc.? Is the way we have it set up now (with the Prosoft DH+ to Ethernet bridge) a robust (scalable, etc.) solution? Is there a better way to do this? Is it worth getting EtherNet/IP cards for the PLCs that don't have them?   If anyone has any experience with a similar scenario, insights/advice would be much appreciated
  10. Hi PLC programmers, I got a problem regarding my installation of Logix Designer/Logix5K. Here's the situation... a) Initially installed Studio 5000 without problem. b) I needed to open a program from Logix v20.1, installed RSLogix5k v20.1. After installing v20.1, RSLogix was corrupted and won't open program. c) Reinstalled entire Logix Software. d) Was able to open and convert program from Logix5k v20.1 to Logix Designer v24 but this annoying error occured on v24 (See attached "EN2T")... "Failed to Create Module Profile". All of a sudden, the module (1756-EN2T) I created with working v24 is no longer usable. Now, even when I create a new project, add a module with "Select Module Type", the list of available modules has been trimmed down to what it normally has (see attached "AB_Modtype"). Kept on re-installing entire Logix 3 times, clearing the registry with CCleaner and even deleted installation folder for Rockwell software but the problem is never gone. I even downloaded AOP for EN2T and installed it but to no avail. Now I'm lost and dumbfounded that uninstalling and reinstalling isn't working. By the way the OS I'm using is "Windows 7 Enterprise". I appreciate all the help I could get. Thank you very much. Sincerely, Andrei K.
  11. Hello I have a SLC5/05 and a Microscan MV40 smart camera which receives commands to a TCP port. Is there a way the LSC 5/05 can send a command to the camera using the MSG instruction or any other instruction? I would appreciate any advice 
  12. My client is a pharmaceutical company and they want to interface their Blood Gas Analyzer (which is a RAPIDPoint 500) to a Controllogix PLC via EtherNet. I have attached a Spec that I found, which gives the initial information you would need to do this. It says that the BGA can transmit data in ASCII. However, it doesn't list what bits I need to send to the device in order for it to send the PLC the data. I've tried contacting Siemen's (who makes the BGA) and they were useless. I also tried searching the RA knowledgebase.  Does anyone have any insight on how to communicate with a device in this way? Thank you Tyler RP500_LIS_5_20_13_-_Rev_C_.pdf
  13. Omron CJ2M - Wago remote I/O

    Hi there, I’m not sure how familiar most of you are with Wago remote I/O, but I hope you may have some solution for the following connection problem I’m having. I’m working on a project to modernise an old folder collecting machine for which I’m using an Omron CJ2M Cpu33 together with 8 Wago 750-352 remote I/O units over ethernet/ip. These Wago units all contain two 8DI digital input cards and two 8DO digital output cards alongside a 750-610 bus power supply card. Adding them to my network in CX network manager is no problem and all seems to work fine. That is, as long as I don’t physically add the bus power supply card, which I need to, well.. power the Wago bus. Soon as I add this card (which was in place while making all the necessary settings to the Wago and Omron units) it just won’t connect. Remove it and it connects like it should. As far as I know the power supply card has no I/O addresses or other communication functions whatsoever, so I can’t get my head around it. Even stranger is that when instead of it I add an analog input card, with bus power connections build in, it connects without a problem. The .eds file only contains info about the main Wago unit, after installing it I should be able to add any kind of I/O card and address them in the Omron software. Also, the supply card is added and visible as a fifth card in the Wago I/O settings and the I/O status led is green during this error. Therefore I would say the problem is at the Omron side. Any sugestions?   Thanks in advance Andy - The Netherlands  
  14. WeinTek to AB PLC Issues

    I am connecting a WeinTek eMT3105P to a CompactLogix L2 series PLC via the WeinTek Rockwell PLC (CompactLogix) - Free Tags driver and I cannot for the life of me get the thing to connect. I have all my tags imported and have played around with all the settings in the manuals I can find. Any help/advice would be greatly appreciated. I know my IP addresses are correct and if I connect my cable directly from the HMI to the PLC I still get the "PLC no response" message 
  15. CAM Control Data

    Hi everyone, I'm trying to use the cam control data by using an MR-J4-A-RJ and MR Configurator 2. When I switch the input "CAMC" to ON, I see that the output "CAMS" is switched to ON which means that the cam mode is activated. When I switch CI0 to ON to choose the Cam Data No.1 and switch ST1 to ON...nothing is happening like if there is no Cam Data. Please, have you any issue or idea ?? Thank you in advance Omar
  16. Hello.   I'm trying to communicate between two PLC's  using FINS function block _CPU011:ReceiveData.   PLC1: IP 192.168.1.50 (MASTER)   PLC2:IP 192.168.1.51 (SLAVE)   If I don't use »IP Address Table« everything works using NODE number &51.       The problem is that on the real project these two PLC's will be on different subnet.   For example:   PLC1: IP 192.168.1.50   PLC2: IP 192.168.2.50   So I will have to use »IP Address Table« to achieve communication between these two PLC's.   I tried to sett IP Address Table on MASTER: Node 1=192.168.2.50   But If I try to communicate I see that packet is sended to network but I've got error #1005.   Do I have to sett the SLAVE IP Address Table?   Hoe to do this?   What are the right settings for MASTER and SLAVE IP Address Table?     I'm attaching pictures of CARD settings.  I don't want to use CX-Integrator because I would like to make project to UPLOAD and forget.       Thanks.  
  17. Hi,  I am writing some routines to decode the data from my Input: data array to User-defined Array Parameters. Is that possible to have a generic routine to decode data coming from more than one module? I have two Module ENode and ENode_1. I have defined User-Defined parameters for the module. Can I make a generic routine to decode the data coming from these two modules and put them in the defined arrays?  the two arrays ENodeData[0] and ENodeData[1] have the Generic User-Defined parameters.
  18. We recently obtained a new Vendor ID (VID) Number from ODVA, 1477 for the purposes of developing an EtherNet/IP scanner device.  When we try to use that number with the Allen-Bradley PLC & Studio 5000 Logix Designer, our data type REAL's are showing up in Studio 5000 as SINT's.  We have seen this mangling of data types before when using the Omron VID, 47 with the same Allen-Bradley PLC/EIP Scanner.  The data types are being misinterpreted, or mangled from REAL to SINT, e.g. the *.eds file defines 32 REALs for Input and 32 REALs for Output, but within Studio 5000 we see 128 SINTs each for Input and Output. It is as though the Allen-Bradley/Studio 5000 database does not have our Vendor ID.  When I change the *.eds file, Vendor ID Number from #1477 to #1 then we see the *.eds file being properly read and interpreted, e.g. 32 REALs for Input and Output show up as 32 REALs each.  Does anyone know what file we need to modify in Studio 5000 ???  We want to add our Vendor ID #1477 to that file. Hardware: EIP Scanner: Allen-Bradley Compact Logix L18ERM EIP Adapter: Delta Tau Power PMAC Motion Controller (EIP OpeNer Stack) Thanks in advance! See screenshots below. within Studio 5000, see screenshots
  19. Hi, Is that possible to define INT data type in EDS file so the Tags for the module in RS Logix Designer would receive INT data type in Input Tags not SINT? As marked in the image, the Logix Designer is receiving data as SINT but I want to have INT data type. Thanks Muhammad Azeem
  20. Hello to all, I am new here, and I have a project with FX3U plc and CR 2DA 700 robot controller. Does anyone have some experience in establishing communication over FX 3U enet module and robot controller, I need to send and receive 5- 10 M registers and D integers. Thanks
  21. Hello everybody, I have network from : PC - 192.168.3.11 PLC - 192.168.3.250 I change this option in FX5U PLC in GX Works3 for Network Ethernet port --> Application Setting -> Security -Disable Direct connect with MELSOFT : Enable/disable -DO not respond CPU module search : Respond / not respond and I upload program to PLC. After upload program to PLC and restart it was impossible to connect again. I Have ping between PLC and PC, but could't write program. Always writes me Error <ES:0180840b> So to disable Security Option you should to do : 1. Open Works3 2. New Project (Choose your PLC - FX5U) 3. Online menu 4. Specify Destination Communication 5. Click twice in PLC module 6. Set Connect via hub (In my case i connect PC and PLC directly !) 7. Choose IP Address ( in my project : 192.168.3.250 , PC must be in same network 192.168.3.X) 8. Give OK 9. Connect Test. With steps I disable security options and it was enable to connect to PLC and Write data on it. I Hope that will help to other with same problem. Special thanks to : Piotr Tynor(Mitsubishi, Poland ) , Adam Syrek (Mitsubish, Poland ) , I. Ayvazova (Bulgaria) , K. Raykov (Bulgaria)
  22. Hello, I was hoping for some help in trying to read/write to a handful of bits in a CJ1M-CPU13 controller from a Compact GuardLogix. The CJ1M rack has a CJ1W-ETN21 card that is already communicating to a handful of Yaskawa drives. Is it possible for me to communicate with this controller from a CLX unit over ethernet? I don't believe an ETN21 card uses EIP but is there a way around this? Right now, I'm struggling to even find the IP address of the ETN21 card as the CX-Programmer file provided to me by the customer does not have the card in the IO configuration and I've never worked with Omron PLCs before. I found a CJ2M to CLX guide but it assumes communication over Ethernet IP and the ethernet port is native to the controller. Any help at all would be appreciated. Thanks!
  23. Grupa ProfAs Sp. z o. o. jest firmą doradczą, świadczącą usługi w szeroko rozumianej dziedzinie Human Resources. Specjalizujemy się w rekrutacjach na stanowiska specjalistyczne, średniego i wyższego szczebla. Wierzymy, że nasz Zespół złożony z profesjonalistów jest w stanie zapewnić perspektywiczne spojrzenie i najwyższą jakość wykonywanych usług. Aktualnie dla naszego Klienta - firmy z branży automatyki przemysłowej - poszukujemy osoby na stanowisko: Programista sterowników PLC Kraków / Piła / Poznań ZAKRES OBOWIĄZKÓW: Programowanie sterowników PLC Siemens Wykonywanie aplikacji dla systemów SCADA i HMI Dobór konfiguracji sprzętowych PLC Testowanie i uruchamianie maszyn u Klientów końcowych (delegacje krajowe i zagraniczne) Wykonywanie programistycznych prac serwisowych u obecnych Klientów Sporządzanie instrukcji obsługi maszyn   WYMAGANIA: Bardzo dobra znajomość sterowników PLC Siemens Umiejętność parametryzacji serwonapędów, falowników, etc. Znajomość paneli HMI oraz systemów SCADA Znajomość sprzętowa oraz programowa komunikacyjnych sieci przemysłowych ProfiBus, Profinet, Ethernet, DeviceNet, Modbus, etc. Znajomość zagadnień i komponentów automatyki (przetwornice, serwonapędy, obwody bezpieczeństwa, aparatura modułowa, itp) Mile widziana znajomość programowania innych sterowników: Allen-Bradley, Omron Prawo jazdy kat. B Komunikatywna znajomość języka angielskiego lub niemieckiego OFERUJEMY: Współpracę w oparciu o umowę o pracę Udział w profesjonalnych szkoleniach Korzystne warunki wynagrodzenia Rozwój w firmie z doświadczeniem na rynku międzynarodowym nr w rejestrze 14990 Osoby zainteresowane prosimy o przesyłanie CV na adres k.dominik@profas.com.pl lub kontakt telefoniczny pod nr tel. 881 700 778.
  24. Hello everyone! Im hoping someone could shed some light on a issue im having. Im having issues with a 1794 ow8 output module. This module is used to control 8 hydraulic cylinders that push biomass into a burner. The overall problem is that roughly once every couple months a output will short in the on state and force a coil on, activating the vavle full time and burning out the coil. Each seperate output is fused on the module with a 2a fuse and each modules incoming power is also fused at 2a. The output that is shorted did not blow its fuse. The 'ON' light is not activated but 120v still runs through it. Since each valve has 2 coils and one is forced 'on' the main fuse will blow once the second half of the valve is activated because the valve is fighting itself. It is not just this one module, this happens on other modules that serve the same funtion as well. This is a contractor installed system but they have been no help so im left trying to figure it out. Could my seperate inputs be fused too high at 2a for this type of card. These are parker valves 120v 60hz with a max 1500psi pushing wet hog/chips. Any suggestions would be really appreciated!
  25. I have a "paddle wheel" style flow meter that I am trying to wire to my Micrologix 1400. It is a three wire device and there is a tag on it that says it can run at 6-36VDC. So, naturally, I thought to wire this to one of the HSC inputs of the Micrologix directly. I hooked the ( + ) on the meter to 24V, ( - ) on the meter to common, signal to the oscilloscope, and ground on the scope went to common. I see a small 60Hz sine wave @ like 5mv when the wheel is not turning. When the wheel is turning I get a small square wave but in the same mV range. It is not a nice smooth square wave either its all jumbled up with the 60Hz sine wave.  I hooked this thing up to a transmitter and scoped the signal and ( - ) in parallel with the wheel - I get a nice smooth square wave signal when the wheel turns. It is only at 4.5V though. My questions are? Why does't the paddle wheel give me what I am expecting directly? Also, what is the voltage range on the pulse that a micrologix will see? I am assuming that it will not count a wave with a 4.8V amplitude.... Thanks for your help in advanced! neech