altan

MrPLC Member
  • Content count

    7
  • Joined

  • Last visited

Community Reputation

0 Neutral

About altan

  • Rank
    Newbie

Profile Information

  • Country Bulgaria

Recent Profile Visitors

1961 profile views
  1. Hello Bigha, Here was changed system and my .pdf file is removed from other post. I send you some example that i have. As i see you  have error in "Controller type". It Shoud be iQ not FX. I think Communication Port No Should be 5001. Upload my program it must work P.S As i remember for HMI GS2107-WTBD have additional GS Installer in Installation disc. So install GS Installer. (find it) Best regards: Altan Sadak   P0382014n2.GTX P0382014n9PID44n16.gx3
  2. Problem is solved. You can delete this post :)
  3. Dear colleagues and siemens experts, I''m new in siemens. As all I make my program for PLC, but I need help with PID autotunig (pretuning) I use : 1.CPU 1214C DC/DC/DC (6ES7214-1AG40-0XB0) 2. 6ES7214-1AG40-0XB02. 16IN/16 OUT DC/DC/DC (6ES7-223-1BL32-0XB0) 3. 2x 6ES7231-5PD32-0XB0 ( 4 channel RTD analog module - PT100) We use 7(seven) Pt100 points with 7(seven) heaters ... so I need 7 additional outputs..... [you can see example of wiring in attached pic 6es7231-5pd32-0xb0-modules.jpg] Maximum heating point is around 220 degrees. I make my configuration for PID_Compact : 1. Basic settings 1.1 Controller type : Temperature : °C Set mode to : Pretuning ( sometimes I make it Automatic mode) 1.2 Input_Per(analog) -----> Output_PWM 2.Process value setting: 2.1 Process value limits: Process value high limit : 220.0 °C 2.2 Process value limits: Default 3. Advance setting 3.1Process value monitor : Default 3.2 PWM limits Minimum ON time : 0.5 sec Minimum OFF time : 0.5 sec 3.3 Output value : Default 3.4 PID parameters : Default I start Commissioning with these steps : 1. Measurement : Sampling time 0.5 Start 2. Start PID_Compact 3.Tuning mode : Start When I try first time my setpoint was 90 degrees , second time I try with 120 degrees. After 4-5 hours it stop more in Progress bar it stop when I reach a little more then 50%, and I stop PID. For heaters it is not normal to process to be 4-5 hours, there have some wrong. Example with 120 degrees : During process I make : When Input_PER reach 120[1200] degrees I stop physical access to heaters. When Input_PER reach 100[1000] degrees I start physical access to heaters So 4-5 hours is soo long time for this type process. Time to reach 120 degrees from 100 degrees is around 2-3 min. Time to fall from 120 degrees to 100 degrees is around 4-5 min. Total time for one whole cycle around : 8min. Sometimes when I set setpoint to 140, 150 degrees it writes me that output set value is to high after I give Start Pretuning ? Even sometimes when try for 120 degrees .... As all I want to start PID pretuning (autotuning) with setpoint 140 - 150 degrees. Which are minimum requirement to start PID autotuning with PID_Compact ? Could you send me some very simple example and steps that I must make or only steps ? I attached files in dropbox with images and program example, because I can't attached nothing here. This form don't give me access to attached something. So link is here : Even program is there. Thanks in advance Best regards : Altan
  4. Dear all, Do you have some ready examples for Mitsubishi fx5u where you use PID ? I use two analog input from 0-10V and two PLC output and I want to head 2 heaters. So how can I use PID autotuning? As I see in examples in manual, there also have other parameters, which I must set, except PID function. Thanks in advance . :)
  5. To enable select GS2107-wtbd HMI , you shoul install addtion GS-Installer which is in somewhere in folders for main Install. solved
  6. Hello everybody, I have network from : PC - 192.168.3.11 PLC - 192.168.3.250 I change this option in FX5U PLC in GX Works3 for Network Ethernet port --> Application Setting -> Security -Disable Direct connect with MELSOFT : Enable/disable -DO not respond CPU module search : Respond / not respond and I upload program to PLC. After upload program to PLC and restart it was impossible to connect again. I Have ping between PLC and PC, but could't write program. Always writes me Error <ES:0180840b> So to disable Security Option you should to do : 1. Open Works3 2. New Project (Choose your PLC - FX5U) 3. Online menu 4. Specify Destination Communication 5. Click twice in PLC module 6. Set Connect via hub (In my case i connect PC and PLC directly !) 7. Choose IP Address ( in my project : 192.168.3.250 , PC must be in same network 192.168.3.X) 8. Give OK 9. Connect Test. With steps I disable security options and it was enable to connect to PLC and Write data on it. I Hope that will help to other with same problem. Special thanks to : Piotr Tynor(Mitsubishi, Poland ) , Adam Syrek (Mitsubish, Poland ) , I. Ayvazova (Bulgaria) , K. Raykov (Bulgaria)
  7. Hello everybody, I want make communication PLC FX5U series and HMI GS2107-WTBD. IP for PLC is 192.168.3.250 IP for HMI is 192.168.3.18 I can make upload programs via Ethernet. My Laptop , PLC and HMI are connected toghether via switch. But I could connect data between PLC and HMI. So what must name of device and how to set BIT for example, which must communicate PLC<---->HMI. (bit.jpg) In GT Designer communication also write that i couldn't connect HMI via PLC in red , you can see attached picture. (GS.jpg) smiles : Altan ------------------------ Solved. My error was that PLC and HMI must have different Station Number Special thanks to Piotr Tynor(Mitsubishi, Poland ) , Adam Syrek (Mitsubish, Poland ) , I. Ayvazova (Bulgaria) , K. Raykov (Bulgaria) /you can see atched .pdf file/ MTS0026 - FX5U and GOT2000 (1).pdf