Search the Community

Showing results for tags 'remotely access fx series plc data'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 201 results

  1. Can anyone advise if there are data structure #s associated with each of the data types in Logix?  Example if it is a Bool, I believe Logix advises it is a 32 bit number.  But is there an "under the hood" data type reference number for each Logix data type?  I.E.  if it is a Bool, that is a RA data type #1, if it is a DINT, it is a RA data type #2, etc.  
  2. Hey all, I've reviewed a number of threads regarding converting one data type to another and I have something I'm working on that I'm stumped on and haven't found an answer for yet. Without getting into the details, I need to get a DINT bit value from an entered decimal value. A user will enter in a whole number in an entry box and then it needs to get converted to the number of whatever bits that the DINT number holds. For instance: # Entered Variable Bit Value -----0------------------0 -----1------------------1 -----2------------------3 -----3------------------7 -----4-----------------15 etc... I'm looking for a fairly clean way to do this, with perhaps just two or three instruction blocks to handle it, if possible. I can provide a screenshot of the HMI and the logic (4 rungs) if necessary. Any suggestions or advice from the group would be greatly appreciated!
  3. I am adding a remote device to an existing cc-link network. The master station is an A1SJ61BT11 and the CPU is A2USHCPU-S1. The CC-Link network currently has 20 remote I/O stations and I am adding a remote device. The A1SJ61BT11 has parameters written to its internal memory. In order to add my new remote device, I think I need to only change two parameters: First, I need to change parameter address H1 from 20 to 21 since my device will be the 21st. Second, I need to change station information parameter address H34 from 277 to 4373 to enter it as remote device. I looked at the example in IB(NA)-66721-J(0310)MEE, section 6.3. In the example, they are setting up the parameters for the first time. However, I am only changing two of the parameters. I followed the example except I only entered rungs to change the parameters for H1 and H34. My question: If I run the parameter setting program to only enter parameters for H1 and H34, will it affect the other parameters the original programmer entered? Could they go back to default? Any advice? Thanks in advance
  4. I'm trying to use CX-Server to pull data from my Omron CJ2H PLC directly into Excel. I'm able to pull a single element into excel, but when I try to pull more than one element, I get a huge strand of numbers. Is there a way that I can set up a single point in DDE Manager that'll hold all the elements that I need, then in excel have a formula that will pull out specific memory elements. Specifically I'm trying to pull data from D7200-D7399, and put each element into a separate cell it in a chart that ranges from B3-K22 This is what the formula looks like when I copy a point into excel =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1' I didnt know if I could put something at the end of each string to call out specific elements, but I keep getting "#BadPoint" =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7200' =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7201' ... =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7399' Any help would be great
  5. In my last plant, we used 100% Rockwell Allen Bradley PLC's. I was very familiar with replacing a SLC series with a 5000 series, a no brainer. Now I work in a foundry with 100% Mitsubishi A-series PLC's with a weird gateway coaxial loop communications that is way beyond it's service life. There is little no no support, and I have been tasked with updating it to something Ethernet based, and reliable. I would like to stick with Mitsubishi, for no other reason than to convert the code from the A series to the new series using my existing GX developer software. This is a running factory, no time to demo the old controls and spend weeks re-inventing the wheel with new Rockwell/Seimans/ect PLC's; plus I already have the software Despite a rather long learning curve, I've been getting comfortable using it. My question is: If you had to choose today what series to convert an entire plant, which would you go with, and why? Please keep in mind this is a foundry, its hot, dirty and nothing really needs to be high speed, or math intensive. I would like something easy to install, easy to expand, easy to use Mitsubishi HMI's and something the electricians can wire and repair (prefer screw terminals not spring terminals).
  6. Hi, I am trying to connect a CP1L-E to a NB7W-TW01B via a 5 port Ethernet switch. I have communication from the laptop to the PLC and from the Laptop to the HMI. but it seems like the HMI and PLC aren't communicating with each other. The HMI will not control the PLC. I've tried everything I know to do with the communication settings and it still will not work. If anyone has any suggestions they would be much appreciated! thanks
  7. G5 Series Servo Overload

    Hello, I am using R88D-KN08H-ML2 servo drive with R88M-K75030T-S motor. PLC is CJ2M-CPU35, with NCF71 position control unit. There are total of 6 axis and the one in question with above combination is giving me trouble, rest 5 work OK. I get Overload trip error even at 200% of torque. The motor doesn't move at all. After disconnecting motor power cable, it is possible to move the assembly by hand so nothing sems to be jammed or binding. Tried Auto-Tune, ended with successful completion (at least no errors etc). But scenario didn't change. Motor doesn't have brake, as per model number as well as physically no brake cable on motor. Since all other axes are moving, with similar setting, not sure what is going on here! Any parameters I can change? Any other way to check?
  8. Hello: I am new to Connected Component Workbench and Ladder Logic. I am using a ladder with 2 direct contacts on the first rung in series - the first is a N/O switch and the second is a N/C switch how do I make the second direct contact represent a N/C switch. So that someone else looking at my program would know right off the second switch is a N/C switch. Thanks My program functions as it should but the ladder diagram looks like two N/O switches in series.
  9. Dear experts, I used this forum for help analyzing our PLC setup in the warehouse in 2013 and feedback from the experts here was very helpful. I would like to offer an engagement as freelancer on our project since we need to cut-out a system which runs out of maintenance in Dec 2016. Please see attachment for details and very happy to receive any questions. I hope this is not against the forum rules as I couldn't find a suitable forum "job offers". Kind regards, Gunter Senior PLC Engineer Japan.pdf
  10. Hi friends, I am a little new to WinCC. I am using a WinCC RT Advanced license within TIA portal v13.1 I need a little help in my current project as described below. I am attempting to create a faceplate of a solenoid valve,, The "Valve" is a user-defined data-type with the following 4 elements 1. Cmd - or command. - Bool 2. Cls_Fb - or Closed -Feedback -Bool. 3. Aut - or Automatic Mode -Bool 4. FTC - Fails to close -Bool. I tried the following procedure as described in TIA portal help.. Method -1 1. I created a User-defined data type called Valve comprising of the above 4 bool elements. 2. In the graphics I made a image of solenod valve with one rectangle (solenoid) and one polygon for valve body. 3. Under the Faceplate Properties (See figure attached) I inserted a property ang gave it the data-type Valve as above. However, when I drag a property from the 'Contained objects list' to the interface side, it is not getting substituted. such as the Rectangle_1 's background color I try to associate with the interface property Valve.Cmd. It does not get assigned when dragged. Since this does not work I tried another approach, Method -2 I attempted to declare a variable tag of UDT type 'valve' in the faceplate's tab Tags. I found that it is not possible to declare a local variable of User-defined types here. Please guide me how to proceed. Thanks for looking in and best wishes for your success. Regards, Raj S. Iyer
  11. Hi friends, Can anybody tell me when to use a local-Static variable and when to use a Local Temp variable whilst creating a Function-Block in S7 -1500 using TIA portal. Thanks for looking in. Best wishes.
  12. Hi all and nice to meet you here! I hope that someone with experience helps me and I hope in future to offer also my help to someone. I am having problem with a Mitsubishi plc with A2N (S1) cpu installed on a machinery. The machinery stayed 20 days switched off and with battery empty as I realised when switched on and the problems come out. I changed the battery but the problem didnt resolved. The plc gave error with stable error led and flashing run led on the cpu. Also an error led stable on a (double role) module of printer and ram. I have to say that I have never used GX developer environment before and it is my first contact with Mitsubishi plcs. Reading some manuals (found on the internet) and by using GX developer I read from plc the faults. Register D9008 was set at 12 error meaning MISSING END INS. I Followed the described flow charts from a2n manual for reseting faults but the situation was the same always as described above. I tried to read the program from plc and succeded to read it. It is a lader with about 6000 lines. Anyway I have no previous experience of the GX development environment but I tried to put the missing END in the program as sugested also by the flow chart in the manual. At this point I have to say that it was automatically added from gx developer as I can remeber from an appeared message. I verified also many times the program on gx developer with the plc and the only difference was that missing END at the last line of ladder program. Anyway I tried to write back to plc the program with correct end but it was not possible. I tried several times. The error mesages took with Gx developer was the following : "THE SAME T/C COIL EXISTS IN PROGRAM (MAIN) AND/OR PROGRAM (MAIN-SFC). THE VALUES ARE SET TO BE THE SAME AS IN THE FIRST FOUND T/C COILFROM THE TOP OF PROGRAM" "THERE IS A DEVICE IN THE PROGRAM (MAIN) THAT IS OUTSIDE OF THE RANGE. CHECK THE PROGRAM AND CORRECT THE DEVICE THAT IS OUTSIDE THE RANGE." Anyway I decided to delete the plc memory. After that the run was stop blinking and the error led went off. Only the error on the printer-ram module was on (This module was changed with a know functioning one witout any variation on behaviour). I thought that problem has gone now that the cpu is empty. I tried again to write the program to the plc but again i take the above mentioned messages. Now I have an empty plc and a program on the Gx developer that cannot be written to plc!!!!!!!!!!!!!!!!!!!!!!!!! I am desperate!!! I do not know how to proceed. I am not knowing the mitsubishi development environment. Other than Gx developer I tried to install the GX simulation but it not works to my computer. At this point I dont know even if the ladder program is somehow corrupted after the described above messages. I can sent the code (GX developer project) and any other information to someone expert, if necessary, to have an opinion. Please help!!! Let me know how to proceed!! I have to write back the code to plc !!!!! Thank you all in advance!! Now i realised that there is SFC that is my problem. Could someone help please? Big part of ladder is in yellow color. How can i proceed?
  13. Hey All, I am trying to do some data storing on a PanelView+ and the built in data logging doesn't quite fit my needs. I was looking into the possibility of creating my own ActiveX control for doing this. Is it possible to create custom ActiveX controls for Factory Talk? If so, are there any tutorials for doing so you recommend? Also, are there any sites that have custom ActiveX controls to download? I realize this may not be the easiest thing to do, but if I could create my own I could use it for various machines and would make things a lot simpler in the long run. Thanks
  14. Hello, I am having troubles configuring my Data Station Plus to be able to read my Vacon VFD registers over a Profibus network. The network is configured from an Omron PLC. I have communication but i do not know how to map the tags on Crimson to be able to read what the drives are doing. I am most likely thinking my offset on the tags that i have set are the main problem. Any input/ suggestion would be great thanks Specs on System: -Omron PLC CJ2M w/profibus PRM21 -Omron HMI NS-12 -3 Vacon NX VFD's -Data Station Plus w/profibus module
  15. Hello all, I am trying to get around a lot of manual inputting by exporting a routine and opening it using excel, but looking at the file that excel shows I have a couple fundamental questions 1. when excel opens it and "creates a schema', can I save this in a format that will allow me to import it back into the program? 2. Since I am mapping data using add on instructions, the table excel has created becomes quote complex, with no clear point of reference to where my Input tags are going to go. We are doing this because someone thought it would be a good idea to put a SCADA based control platform over the top of an AB control system, so we have to exchange thousands of points of data back and forth with their system. I created the mapping AOI blocks to be able to manage the file structure a little better in the routines, but that still leaves me with copy and paste thousands of tags into the AOIs. Has anyone developed a good way to create logic, or modify logic using excel? While I can hold my own with utilizing the RS5000 platform, my excel experience is limited. The processor is a 1756-L75 Thanks
  16. Hi, I am looking at options for integrating MATLAB/Simulink with Q-series PLC (Q04UDE) for hardware-in-the-loop simulations. I would like to have a Simulink model send speed/torque setpoints to the PLC and have measured values feedback from the PLC to the model. I know this can be done via OPC but I think the update rate may too slow for our purposes (I would ideally like to have <100ms update rate). Also, I saw Simulink have a toolbox for converting their models to PLC code, but they don't seem to support Mitsubishi PLCs. Anyone have any ideas on how this can be done? Thanks, Darren
  17. Dear Experts; I have already install a 10 slot chassis in a system. Now for the further process i need to add 5 slot expansion chassis for further I/O modules. I have now 5 slot expansion chassis part number IC693CHS398. But when i configure the hardware by using LM90 software i have not seen the option of expansion chassis. Image are attached. Please guide me how i install or cofigure the expansion chassis ? Regards
  18. Dear Sir, I want to read data (Digital Input say X0 (Local PLC) and after some additional logic i want write to Y0 (Remote FX3GE PLC on same network) from one Mitsubishi FX3GE and Write to another FX3GE on the same network. Master PLC IP Address 192.168.0.40 Slave PLC IP Address 192.168.0.50 Atif
  19. I am getting this error. How to resolve this?
  20. String encoder

    I need to replace existing encoder with quadrature output which is failing. We need to have minimum measuring distance of 60 inches. The encoder installed by manufacturer is Temposonics R-series RHS0650UMSO1Q1AC10 The resolution can be lower than the current encoder, probably 500 counts/inch or higher would be OK. Do you have any product that can be used? I was thinking about string encoder but I am open to suggestions.
  21. http://accautomation.ca/now-you-can-have-robust-data-logging-for-free-part-1/ YouTube overview: https://www.youtube.com/watch?v=6Xa2HYVOxE0 Robust PLC Data LoggerWith traditional loggers, software will read the memory of the PLC and store in a local computer. If the network stops or the PLC communication fails then the logging will stop.Creating a robust PLC data logger allows the communication to be stopped for a period of time without losing any of the data for collection. This is accomplished by storing the data locally on the PLC until communication is restored. All of the data is then read without loss. The amount of time that the connection can be lost will be dependent on the memory size of the PLC and the frequency of the data collected.This series will walk you through the steps to create and implement a robust PLC data logger using the following equipment and hardware. Automation Direct – Do-More – H2-DM1E PLC (Ethernet Modbus TCP)Do-more Designer 1.3 (Simulator instead of PLC mentioned above)Windows based computer running IISVisual Basic 6Regards, Garry http://www.accautomation.ca
  22. Count SM410 pulses

    Hello! I need to count the number of pulses SM410. Use instructions Counter_M has no effect. How to count the number of pulses(100 mc)? My soft:GX Works2. My plc is L-series(L02SCPU). In FX series It works well.
  23. Hi I have a scenario where I need to setup communication between a Mitsubishi L-series PLC to Schneider Modicon M580. I need to use the onboard ethernet port of the L-series PLC. The protocol I need to use, is Ethernet IP. (socket communication). Can someone please assist?
  24. Hi dear all , i need some helping .. I used CJ2M cpu31, then i want to send data (example D100 = 2000) to PC ...essentially i want send value 2000 to my PC.. wherein the PC and PLC conect via internet IP .. What should tool/software may i used ? Thanks before ..
  25. I have the following situation; I have a distribution network connecting about 400 RTUs, using 101 protocol to connect to their PDH MUX, which data slot is transported using SDH STM-1/4, to the Primary Substations. Then the primary substations connect to the LDC building using STM-16. At the Control Centre Building where the Front End is located, there is a STM-16 node with some PDH ports, but definetly not 400, so how can I extract this 101 asyncronous data channels to connect them to the SCADA Front End? Note that conversion to 104 is not allowed by the client. Thanks in advance!