junkyardgary

MrPLC Member
  • Content count

    18
  • Joined

  • Last visited

Community Reputation

0 Neutral

About junkyardgary

  • Rank
    Sparky

Profile Information

  • Country United States

Recent Profile Visitors

1326 profile views
  1.  Hey guys, I'm on site with some old AB hardware. I have a DH+ loop with several panelviews 300's, 1000's. Customer wants me to modify one of the PV 1000 HMI's and I cannot open the panel that the screen sits in. It's an explosion proof room, and the system will shut down if I depressurize the enclosure. I do have a saved copy of the PV program to work on off-line.   I do have access to the other PV's and the main PLC, a 5/03 with DH+. There are no AIC modules in the loop. I have the proper serial and round port A-B cables. Can I upload/download to one of the PV's through the SLC processor? I see there are some pass through instruction dealing with serial connection between the PLC and the Panelview. But this is using DH+ between the PLC and Panelview, so the instructions don't work as written.  Rockwell document 2711-um014-en-p.pdf, page 202 has some pass through instructions.   
  2. Proficy POSCON issue (Emerson PLC) PAC software

     Turns out there is a bug with the PAC using "one shot" type instructions fed by real world inputs. I used an intermediary M1500 bit from the I00100 input, then used the M1500 to feed the one shot, everything worked fine. Apparently the "I" inputs do not solidly transition from off to on in the scan, like an internal bit. I can show you logic where the input appears on and off on the same page. Sometimes they work fine, sometimes they refuse to switch. Other than single scan instructions, the inputs seem to work as expected. Tribal knowledge, I guess.  Perhaps if I used a positive transitioning output POSCOIL, instead of a POSCON it may have worked fine, but I'm not going to rewrite it for giggles, need to move on. Perhaps its a certain PLC, or who knows why some work, some don't.  Not a fan of the Proficy/PAC software in any event. I can see why so few companies use it. 
  3.  I have been troubleshooting another engineers logic. There is a couple lines that have real world inputs, IE: I00100 and I00101. Each has it own rung, these inputs are POSCON and feed a reset coil each. One line works fine, one does not. I have verify the inputs are transitioning from off to on, but one reset works, and the other does not.  The processor is a CPE-100. Is there a problem using real world inputs with the POSCON instruction? The results are very reliable, the same issue happens every cycle, never any variation. I'm just trying to make sense out of it before changing a "standard" logic program, without explanation.   I am a hired gun engineer here for a few months. Don't want to make unnecessary waves.   
  4.  I have been troubleshooting another engineers logic. There is a couple lines that have real world inputs, IE: I00100 and I00101. Each has it own rung, these inputs are POSCON and feed a reset coil each. One line works fine, one does not. I have verify the inputs are transitioning from off to on, but one reset works, and the other does not.  The processor is a CPE-100. Is there a problem using real world inputs with the POSCON instruction? The results are very reliable, the same issue happens every cycle, never any variation. I'm just trying to make sense out of it before changing a "standard" logic program, without explanation.   I am a hired gun engineer here for a few months. Don't want to make unnecessary waves.   
  5.  We have been tasked with saving money on equipment within our 4 plants here in the USA. I would like to investigate using low cost HMI's, I've had great success using C-more in the past. Has anyone had any of the several low cost HMI's attached to Emerson PAC (AKA GE Prophecy) PLC's? has there been any connectivity issues? I'd like to try one to replace the Emerson HMI's which are hard to source, and expensive. I believe any time setting up a low cost option would offset the cost of the Emerson, and open up our choices of HMI's and not be boxed in to one brand. We also use Profinet along with Ethernet connection, I believe the Emerson HMI only uses Ethernet (for us) but if there is a Profinet version that is easy to set up, that would make it an easy sale for me.   This HMI would also have to work with the older 90-30 series PLC's, but i'm pretty sure the communications have not changed much from the to the stand alone RSTi-EP and RX3i PLC's. Any advice would be appreciated.  Have a great week. 
  6.  I've been debating whether to stay at my current employer who uses Emerson PAC software, vs going back to a similar company that uses Rockwell (compact/control logix) mainly because A-B is used by most companies around here. I work as a technical temp, usually 12 month contract jobs. Learning the Emerson PAC (aka Prophecy) seems to be a waste of time, since I am not aware of any companies that use it, other than my current employer. My placement company is pushing back, but I know I am correct. I do not have hard numbers, but I've been around the industry for 20+ yers, and have only seen 1 company use Emerson.   Does any one agree or disagree, or have some circumstantial evidence of the actual market share of A-B vs Emerson. I am mainly working in the Auto industry, in Michigan. Just looking at this site, there are 3200 postings for GE and Emerson combined, vs 58,000 postings for A-B. 
  7. Easy way to import a PAC program?

    I found the "RESTORE" option that seemed to do the trick. Thanks for anyone reading this. JYG.  
  8. Easy way to import a PAC program?

     My colleague sent me a few  PAC programs via email, my PAC/ME V10 software has the "FILE/OPEN PROJECT" greyed out. How do I pull this into my PAC/ME? I do not know where Emerson keeps it programs internally, this is a network/server set up -we do not store programs on the laptop much. Am I missing some easy way to open programs from a desktop/USB source?
  9.  I've never seen a production facility use Proficy to communicate to a Rockwell PLC, when the rockwell works perfectly fine though direct ethernet network in the building. The only advantage is the Proficy keeps a copy of the ACD file inside a project environment with the HMI, misc other programs in a nice package form. But if it doesn't work, then its a mute point to demand other people to use it.   I gave them their fixed program on a thumb drive, then emailed another copy, with the change logs, and left it for them to sort out. They are also removing Rockwell 500 PLC's and installing Emerson PLCs to run large machines in the plant. This doesn't make any sense either, but it's their money. I can understand swapping out the Panelview HMI's for another HMI brand, but not the PLC that works perfectly fine. Perhaps they plan to drop the Rockwell software and Tech-connect expense in the near future and need to rid themselves of the A-B hardware. Not sure. 
  10.  I'm having issues saving the program on an older machine running a 1769-L30ER controller. I can open and close the file offline, using PAC machine edition software -no problem. I cannot upload, or go online, citing some RS linx pathway issues. Be aware this is run through an Emerson PAC program that is supposed to open/communicate/upload/download through a Profinet interface using the PAC software (AKA Proficy). I have doubts the communication in Rockwell (which is pretty specific about how it works), is set up correctly to see the Profinet via PAC software RSlinx  pathways.   I can directly open studio 5000, change my I/P address, up/download via ethernet cable, works perfect. The company wants me to "check in" the project through their PAC software, which opens, closes and saves the .ACD file in their database inside the PAC system. It doesn't seem to work. I did notice the RSlogix was written in 30.01.11 and this laptop is using 30.02.xx software. I assumed that should not be an issue. correct?   I'm trying to eliminate any errors on my part, before telling the company their software just isn't working for this application. I'm here to edit the machine and leave, not to repair the 3rd party software they own, that does not appear to be communicating correctly.  
  11. Difficulty using the SEARCH function PAC software PLC application

    That seems to help greatly. I wonder why they use that old search tool? seems counter-productive.  Thank you for the answer, sir. 
  12. Emerson (GE) memory map data types

    Exactly what I was looking for. I'm seeing coils that are M's, some G's but see no real difference in their use. My background included Modicon and Mitsubishi, which are similar to the Emerson, but some of the data types use different prefixes. I was aware of the tag name in the newer PLC's (thank God), so I was able to troubleshoot my first machine. Now I'm doing some service work on older Emerson stuff, and stumbling around in the dark trying to figure out why and how it works. Your last paragraph sums it up quite nicely.  Thanks for your time, sir.   
  13. Emerson (GE) memory map data types

     I've always had this Allen-Bradley memory map taped on my wall in my office. It used to be handy to use, until I remembered al of the prefix letters for each data type. Now I am using Emerson (GE) the old proficy software now called PAC ME machine edition. Now I'm finding it's about impossible to find the data type list amongst the thousands of help files, videos, ect... it seems like a simple thing to find, but I'm not having any luck. They use I and Q for regular inputs & Outputs, but there are R files, M files, S files, N files, G files, ect.... this is old-school PLC software that doesn't use tag names.   Is there a steadfast rule for each type, or can they be used for any type of data? Dazed and confused...  
  14.  I've been using this Emerson PAC software for several weeks now. I cannot seem to get the search function to work well, when working on PLC. I can open a search box (from the search icon) and type in text that's right on the screen, and it returns "not found". It's frustrating. I've tried using wild card *, quote marks, % signs. Nothing works.   How does one properly use the search function? My coworkers are just as stumped as I am. Unfortunately nobody has real training on this software, we are kind of thrown into the fray to figure it out on our own. It would greatly improve my troubleshooting time if I could find things, either by variable number, or description text.   The on-line help for this software is about non existent. One "tutorial" is 8 hours long, another is over 11 hours long. 
  15. I wish it was that easy. Opening the power to the drive, or the motor lead trips it out, and requires a homing/reset to continue. I suggested the builder either put in an STO type drive, or build a physical brake/hold device to lock it in place during a safety circuit event (light curtain or E-stop). I can be over-ridden buy  management, but at least I voiced my opinion, and suggested reasonable fixes. When the inevitable accident happens, I'm usually able to pull out my emails, audits and avoid any disciplinary issues.