Search the Community

Showing results for tags 'omron keyence ethernet ip union'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 660 results

  1. Hi,   I'm developing an application in C# and need to communicate with a plc omron NX1P2. How can i do it? With cx-compolet? Or is there another way?  
  2. Omron NB HMI Recipe Setup

    Hello Everyone. we have Omron NB7Q-TW01B. Only one HMI is programmed to run two identical machines.   Scenario: There are two different screens on HMI to set the parameters of machine-1 and machine-2. (let's say there are 10 numerical input parameters for controlling machine-1 and 10 numerical input parameters for controlling machine-2.)   Requirement: We have to design a common recipe function for both the machines. (let's say we create recipe named A,B,C,D,E,F,G,H.. of 10 parameters)   Now we need the selection to load any recipe to either machine-1 or machine-2.   Let me know if you have any idea of how to do so ?
  3. Hello All, I would like to control Powerflex 525 drive with Omron NJ301-1200 PLC via Ethernet/IP (Set speed, start, stop). I've gotten until the part where I downloaded the necessary .eds files of the drive and imported into my Sysmac studio. However, I'm stuck after this point while assigning target variables and Originator variables and eventually setting speed and controlling the vfd. I've attached images for your reference.
  4. Hi community, i need help .... I want to connect my HMI GOT 1455 to a PLC OMRON CP2MC by RS-232, but i cant do it. I'm using the following connection: HMI GOT1455   -    PLC CPM2C (Interfaz CS1W-CN118)              2 (RX)          -            2 (TX)              3 (TX)          -            3 (RX)              5 (SG)         -            9 (SG)                                 -            4 (RTS)                                 -            5 (CTS) * PIN 4 (RTS) IS CONNECTED WITH PIN 5 (CTS) In the HMI I configurated driver OMRON SYSMAC, CHANNEL 2 RS-232, TRANSMISSION SPEED 19.200, DATA BIT 7, STOP BIT 2, PARITY EVEN. But with all of that I can't connect both devices. In the PLC i can see the led COMM blinking, so it should have communication, but the HMI show me "Communication error. Refer to System Alarm in Utility Menu"
  5. halo, i'm newbie in HMI and PLC. i have a problem connect HMI omron NB7W-TW00B TO PLC OMRON CP1E. i done setting same baudrate,data bit,parity check, and stop bit in HMI and PLC and i use nb designer for create a HMI display. and this is attachment: a cx programmer, bit switch and bit lamp in nb designer. and the output in hmi is [2]PLC No Response:00-00-1 can you help me? thanks
  6. Hello all, I am looking into creating a system where I have an NX102 in a main panel, and numerous satellite panels (up to 20) with EtherCat Slaves which would then have daisy-chained EtherCat slaves. Essentially, the main panel would need a GX-JC06 to allow branching out, but this only has 6 ports.  1 of them would be used to connect to the master (NX102), but would I be able to connect one GX-JC06 to another?  I highly doubt the GX-JC06 behaves like a typical router, but I can't find any documentation about creating more than 5 branches. Thanks, K
  7. CP1E won't connect or run program

    Hi there! Today a CP1E-E10DR-D suddenly stopped working. RUN led was off and I couldn't connect to it via USB getting this error: "Selected port does not exist. Select proper port number from Change PLC dialog and press OK button", and automatic online function didn't work as well(it's not a cable/driver problem since I successfully connected to a CJ2 CPU using same cable and PC). Since I also tried to connect with the CPU outside the control cabinet with no success, I asume there is something wrong at hardware level.  My question is, have you ever faced something like this? My plan is to try to revive it somehow (maybe trying to locate any defective component in the PCBs or something). So I was just wondering if you have any advice in order to achieve it.  Thanks in advance!
  8. I'm trying to understand the basics of using a serial to ethernet converter such as this Comtrol DM-EIP-2101, with Studio5000 code. Basically I have a weighing machine that only outputs data via RS-232 and I need to send that data to a PC that will process it through a Studio5000 program and have the data displayed on an HMI using FTview SE. Is it as simple as just connecting the serial and ethernet to the converter and it does all the work? Obviously checking ip addresses and firmware will need to be verified. The main thing I am unsure of is the process of passing the individual data packets from the machine to the Logix code on the PC,  things like what the weight of the item was, was it over weight or under, etc....  Would there be an AOI or tags built into the software for a machine like this Checkweigher? I've worked with much smaller items like Cognex Dataman cameras and I know you can just use their AOI that allows you to simply call a tag if you want to display information like if a scanned barcode was correct or whatever. If anyone has done something similar I'd appreciate any guidance. It can be difficult getting the information from the manufactures so I'm looking for answers anywhere I can. EDIT: I guess I should also clarify that only using one or the other (serial or E/IP) is not an option. It will be a serial connection from the Weighing machine to the converter and then Ethernet to the PC.
  9. HMI Replacement Options

    Hello! We are looking to find a replacement for our Omron NS Screens in what seems like about 20 systems...there are so many third party/other vendor options available, I am honestly overwhelmed, so I thought maybe some of you had great experience with other vendors screens that I could look into using in our equipment.  The screen will have to communicate with an Omron CJ PLC, serial or Ethernet is fine, Ethernet is preferred.  Would also prefer screens that actually have Omron drivers.   Thank you!!
  10. Hi to everyone!   Our company is planning to build >10 same machines. Some features will be developed later down the road. And here I'm facing a problem where I need to start tracking PLC and HMI program build revisions. Has Omron any internal tools to generate program build revision? Regards, Scotty
  11. Hi all, I'm new here and need an opinion from you guys on how to set the Gateway for PLC CP2E in CX Programmer ? From my discussion with supplier (OMRON), they mentioned it was unable to set any gateway for CP2E model but I found on some sources that for previous model for CP1L is able to set the gateway. Supposed to be the Gateway function can be supported by latest model, am I right ? Need an explanation on this, Thank You
  12. I'm trying to set up an Ethernet/IP communication with a CIP block between a Micro850 and a SMC EX600-sen3 pneumatic Module. I can read the inputs of the module with the configuration below, but I CANT write to SET or RESET the digital outputs. There are NO errors showing communications issues in the CIP Generic Block I am using... I read that for some reason, it seems that there are problems with writing thru Ethernet/IP protocol between Micro family and other devices not from Rockwell... Does anyone know if there is a way to make it work? Configuration that is working to READ: CIP Service Code:     14 CIP Class ID:         4 CIP Instance ID:     100 CIP Attribute:         3 CIP Member ID:         0 Configuration that is NOT working to WRITE: CIP Service Code:     16 CIP Class ID:         4 CIP Instance ID:     150 CIP Attribute:         3 CIP Member ID:         0
  13. I would like to get some feedback or alternate suggestions in terms of monitoring a database connection. The attachment here shows the current programming for the DB_Connect function block which requires the Execute input to constantly be ON.  From what I can tell, if the connection is dropped - let's just say the Ethernet cable is unplugged - this input will still be on, and according to the function block, still connected. The Get1minClk is in place to continuously try establish this connection once powered on, but I cannot find any way to periodically check this connection without dropping it and reestablishing it.  My understanding is the _DBC_Status.Run only checks that the PLC service is running properly, but is there a way to monitor a heartbeat of the connection TO the database?  The only way I've found thus far is to drop the connection and reconnect.  But this would be detrimental to the system as it would possibly be reconnecting to the database while trying to write to out to it and hold up the show.  As it stands in the second image, the Ethernet cable is unplugged, but the connection shows no errors. Thanks and happy Friday! -K  
  14. Hello,  I am using Omron’s safety G7SA to relay 24 volt line. But the strange thing happening is that, one relay’s output is only 5 voltage, even the relay is on. I exchanged relays, it remains the same. Maybe the base socket is problematic?  Or is this just G7SA failure? 5v (exactly 4.96v) is strange. Please give me some advice.   Many thanks in advance.   Ting    
  15. Hmi modbus TCP/IP device communication

    Hi all; I have Delta DOP110 IS hmi and i have a modbus tcp device. I want to communicate hmi and device with modbus tcp/ip but i didnt understand device's register address. For example, input bytes 0,1 analogue control word, What is the register address? 40.000 or 40.001 can you help me ?  
  16. Hello, I am rather unexperienced with PLC's but have some experience. I Currently have 2 Lexium ILS1 motors which we want connected over RS485.  I have read a couple of manuals. I have found which format they want to receive their data and what the pinout of their pre assmbled cable is (which hasn't been delivered yet).  I am currently unsure about a couple of things. The wiring the formatting of my data i'm sending, and the program.   The pictured below show my motor (which runs when i connect it to the PC and run it using the software provided so it is in working order) and the PLC with option port (which i used to transmit data to another PLC, so again i can't blame the hardware for being at fault here). However when i connect the cable and try to communicated I Don't see the LED light up. I followed Lexiums guide on which pins to use. But i figured for good form i might include these pictures to be certain hardware is correct.      Finally here is my program. I followed Omrons quick start instructions. But: my send ready flags never become high and the way data has to be formatted for these lexiums seems very labour intensive. But this is how i understood it needed to be done. Am i doing something (or a lot) wrong here?      I hope someone can help me out here! If any further information is needed i'll do my best to provide it.   Kind regards.
  17. Hello every one in this video, you will learn about Omron PLC PID Control (CX-Programmer) you could see it for free by using the below referral link for 5 days. https://www.udemy.com/course/omron-plc-training-course-fa/?couponCode=0384FB604CD8E26CDD09 I hope it will be useful for you.   Regards Mehdi
  18. Omron PLC PID Control (CX-Programmer)

    Hello every one in this video, you will learn about Omron PLC PID Control (CX-Programmer) you could download as free by using the below referral link: Omron PLC PID Control (CX-Programmer) | Udemy I marked free download for 1000 people. I hope it will be useful for you.   Regards Mehdi  
  19. Hi, I have a CP1L and CP1E Omron PLC, and I try to make communication between my PLCs and my system (raspberry pi with Linux OS) using Node-red and specifically using the OMRON-FINS node ( https://flows.nodered.org/node/node-red-contrib-omron-fins) and more detail ( https://github.com/ptrks/node-omron-fins ). So I’m looking for a module to create an Ethernet port for my PLCs. ( both PLCs have RS232 port) . Can you please guide me to find a compatible RS232 to Ethernet module for my PLCs?  Thank you
  20. Hello, I am working on a project currently that uses a windows application on a PC to communicate with an NX1P2 controller to read and write variables data. I found a course on Udemy which has a Visual Studio project with OMRON DLLs that are used for these communications. I confirmed with OMRON that they do have official DLLs for this, but the technical support guy has told me he is trying to find them himself.   I have attached a screenshot of the DLL references.  I am really looking for the DLL libraries, aswell as the documentation on their functionality to I can use them to communicate. Any help would be greatly appreciated!  
  21. Hello! I am working on a quote for a new project that will use EtherCAT but also requires DeviceNet for some legacy components.  Has anyone successfully used the Beckhoff EtherCAT coupler (EK1100) with the DeviceNet Master Terminal (EL6752) and an Omron PLC as the EtherCAT master? My concern is that the coupler will only communicate with the Beckhoff EtherCAT master, but since it is so much more expensive to get the new Omron parts to communicate DeviceNET i am hoping this could be an option.  The equipment is extremely simple and price is a major consideration.   Thank you!!!
  22. CP2E Modbus RTU Slave

    Hi, I would like to know CP2E have any modbus rtu slave function block. CP2E with add on CP1W-CIF12
  23. Hello everyone I'm new to omron plc . I have a system which consists  1. Omron Plc CP2E 2. Two stepper motors and their drivers.  3. 4 Inputs-  one stepper start push button, second stepper go back push button, third stepper 1 home sensor, fourth stepper 2 home sensor 4. 4 Outputs- stepper 1 step(-) Q 100.00, stepper 1 dir(-) Q100. 02, stepper 2 step(-) Q100. 01, stepper 2 dir(-) Q100. 03 Seuence is like that:- Initially both stepper motors are at their home sensor.  When start push button is pressed both stepper move 110 mm distance and then stop.  Now when go back push button is pressed both stepper motors should go back to their home sensors and should stop at reaching their hone sensors.  This is the sequence. Can someone please send me the program by writing in cx - programmer or upload the photos of ladder program and settings also. Please
  24. Bonjour, svp comment résoudre le problème désactivation master
  25. Bonjour svp, qlq me l'aide ,j’ai un problème au niveau automate CJ1M CPU12 via  Erreur de numéro dupliqué