Search the Community

Showing results for tags 'nb designer control recorder error'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 367 results

  1. FC1 Two hand anti tie down

    Version 1.0.0

    131 downloads

    Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value.
  2. FC1 Two hand anti tie down View File Logic takes two inputs (I0.0, I0.1), debounces each (T0, T1), looks for actuation during a timed period (T2), and provides validation (M20.0). This logic is not designed, nor intended, to replace the use of any OSHA required two-hand safety control relay. It is provided for the sole purpose of it's educational value. Submitter pop29684 Submitted 03/22/16 Category PLC Sample Code
  3. GE PACSystems Ehthernet Interface Error

    Hi ALL, In the Rx3i controller fault table-the following fault keeps coming-up "0.4-LAN System-software fault: resuming" Error Code: 402 Group: 16 Action: 2 Diagnostic Task Num: 6 28001d001400000004011d000000000c0a88066 Does anyone have the definition of this error code and how I can interpret the error? Thanks Chris Ok Tedi PNG
  4. I need to learn about position control for 2 axis with a QD75MH2 module. I know how the basics about programming with the Q Series PLC but I've never done any positioning control. I'm having a really hard time understanding the program I have to modify and I don't know where to start. Is there any course you might recommend? Even if I have to pay for it. Thanks.
  5. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  6. C200HW-MC402.pdf View File C200HW-MC402-E Motion Control Unit Operation Manual Produced June 2001 Submitter IO_Rack Submitted 03/09/16 Category Manuals
  7. C200HW-MC402.pdf

    Version 1.0.0

    23 downloads

    C200HW-MC402-E Motion Control Unit Operation Manual Produced June 2001
  8. Hey guys, first post!  Friends at Practical Machinist sent me over here b/c we were stumped.   I have a Mitsubishi 500M control CNC machine.  There is a section of the ladders that i don't understand, and Mitsubishi couldn't help, and the OEM is defunct.  I do not have a hardcopy of the ladder circuits. I have an output , [Y13], that i can't get to turn on because of an internal relay | M453 |       see pic 1 When i searched for relay M453, it seems as if it's in some sort of array function.  see pic 2 None of the relays from M448 thru M512 ever turn on.  I understand that all these are controlled thru this circuit, but i have no clue what is going on with the R registers, and how the heck these internal relays can be turned on. Can you guys help explain?   Thanks!
  9. Error code: 4140

    Hallo. Recently ive got an error i haven't seen before. Error 4140 im using GX IEC developer  CPU is Q06UDEH I cannot figure out why the error happens.  When show the location to the step where the error occurs it makes no sense. The specific area has only got simple bool operations. When trying to recompile the entire project. The error "moved" to another location in the program. At this step there was a lot of float operations. When monitoring one of the variable value was NAN. I could not find anything about NAN in the manuals. But google stated it could mean not a number, which makes sense when reading the error description. I know it impossible to help me with my specific problem, when i cant really tell where or why the problem happens. But im pretty sure it has to do with me using float operations wrong. Ive tried to do a simple test program just to see if i could provoke the error, but no luck. How can i make a number go out of range, make it unnormal, nonnumeric or even infinite? Maybe someone could give me a simple example how to provoke this error, which might help me on my search in my own program. Thanks. Below is a screen-dump from the manual on this error.
  10. Sequencer Input

    I have a program using the SQO instruction. However, I am looking to control my program with a sequencer input. I have never used the sequencer input before and I have 16 sensors to move cylinders using the sqo.
  11. Let me try to explain this correctly..  I have a machine built and coded in Japan, so while I know 90% of the code and functions there are certain parts of the code I have never touched.    Today i started getting an error that is commented as E-Net, so I am assuming its an ETH I/O issue.. but the device is something I have never seen. U1C\G20480  Can someone explain to me what this device is or how it is used? 
  12. Hello. We have in the company machine from China. Omron HMI panel NB7W TWOOB. When you upload a project program NB-desinger 1.36 Windows writes the program stopped responding. And then when decompiling .pkg file comserver.dat font_1 font_2 font_3 font_4 font_5 gui.dat ?????????.pkg ?????????.rcp servo.dat Error fonts. Error macro files. How do I install fonts And what problems Upload project I need your professional advice. Thank you
  13. Dear all, Last week I had an A1 PLC in error. I was wondering if there is a D-register that contents the error which caused the PLC to go down. Especially the D-register that keeps the information of previous errors because we had to power down the PLC to reset the problem. The problem did not happend again but i like to know how to deal with it when it does. I Know there are some D9000 registers to show internal errors like battery fail however I don't know if there is also a register that shows the last and second last error after power down. I hope someone has the answers to this. I'm looking forward to hear from you. Best regards, Theo V.
  14. Dear friends. I faced one problem of recipe working. Could somebody help me? I try to create recipe and use it in my program. Fisrt of all I decided to learn how it working and for this I used documentation NB-Designer Operation Manual. I created my test program, but it doesn't work as I need. Bellow I want to describe, what I need: I want to have 5 program with 4 parameters and download these program with parameters inside to the PLC. In attachment you can see my program. test.zip
  15. Bit strange - I use CompoNet all the time and just had my first issue. I found Remote I/O error code 9 in the CPU but cannot find what the code means. Went through the manuals and all errors appear to be in hex. Can anyone help at all please?
  16. I forgot how to do this. If I put in let's say 1234569632<cr><lf> how do I store the carriage return line feed along with the number in my ST file??? 1234569632(chr$13)(chr$10) something like this, but can't remember. Thanks
  17. Hello! So I have this issue with me by this week. I have an NJ with unit version 1.00. I had not did any download/upload on this unit. Due to the need of showing using Password capability on Function Blocks, I need to upgrade the unit firmware version, so I changed it to 1.10. After that I tried to program a simple two Sections program. I left the CPU for a week, then when I get back to it, I upload the program from the CPU. And the upload was SUCCESSFUL! No errors are shown. However all of the Rungs inside each Sections contains nothing. Even though the two Sections that I made before are still present. The program itself is still working though. If I open the previously saved project, going online and do variable controlling, I'm still able to do so. Has anybody experienced this before? Any suggestions / solutions? Thank you...
  18. I have an interesting problem. On my NQ HMI, I am changing one bit of the alarm word to true. The first time I do this, one alarm becomes active, and appears in my alarm list on my HMI. Then when I change the bit back to zero, the alarm becomes inactive. Then when I make the bit true again, the alarm does NOT become active again. Nor does a new alarm appear at the top of the list. What do I need to do to make a fresh alarm appear in the list? Any input would be greatly appreciated. Thanks in advance.
  19. Good day, I´m helping with small project and currently i am stuck because of this problem. And I hope you can help me out. I´m using PowerFlex 525 connected with AB CompactLogix 1769-33ER PLC via EtherNet/IP. Connection is working, I can read and write values from/to 525. To configure both devices i´m using RSLogix 5000. 1) First problem occurs after I loaded configuration to 525 and it´s, that 525 keeps overwriting values of Accel and Decel Time 1. It happens when i directly change parameters in Module Properties (online) or after I upload configuration to device. It happens even if i set parameters directly to 525 with its HMI panel. - I kinda get around this problem when i use Accel/Decel Time 2 for Step logic, but if i send direct reference value motor still jump to it and that is not good, especially when changing direction of rotation. 2) Second problem is that I cant get Speed Sources and Start References right. Usually Is working only option 1 and others are not, or they are doing something else that they should. For better imagination this is what i want to do: I have 3-state switch (left = 1 ON(DigIn TrmBlk 02), 2 OFF; center = 1 OFF, 2 OFF; right = 1 OFF, 2 ON(DigIn TrmBlk 03)), In center position I want to control 525 with EtherNet (already working when: Start 1 AND Speed 1 = EtherNet/IP). In left position I want to control motor directly with Drive Pot and In left position a want to start Step Logic (which i have already set) - Funny thing, If I set Start 1 = Ethernet, Speed 1 = Step, Start 2,3 = DigIn, Speed 2,3 = Drive Pot then in all three position motor goes in Step logic.. Or when i get left and right position working then Ethernet is blocked.. and this kind of things.. I Attach print-screen of my current settings, if you need something more just, tell me. Thank you for your time, and I hope someone will be able to help me.
  20. Where can I safely download NQ designer? Thanks in advance.
  21. Hi guys, I have a problem with GX IEC Developer 7.04, i hope some of you can help me. When i try to connect with the PLC type - Melsec FX1s- 30MR-DC, there is an error: I check all COM port settings, and everything is ok. Com_port parameters: FX Parameters: Transfer setup: PLC Type in the program is the same like physical one (FX1s). I try to change all of this stuffs but there is no result. The cable I use for comunnication is this type: Thank you very much in advance. Have a nice day! eng R. Bukov
  22. Hi all and nice to meet you here! I hope that someone with experience helps me and I hope in future to offer also my help to someone. I am having problem with a Mitsubishi plc with A2N (S1) cpu installed on a machinery. The machinery stayed 20 days switched off and with battery empty as I realised when switched on and the problems come out. I changed the battery but the problem didnt resolved. The plc gave error with stable error led and flashing run led on the cpu. Also an error led stable on a (double role) module of printer and ram. I have to say that I have never used GX developer environment before and it is my first contact with Mitsubishi plcs. Reading some manuals (found on the internet) and by using GX developer I read from plc the faults. Register D9008 was set at 12 error meaning MISSING END INS. I Followed the described flow charts from a2n manual for reseting faults but the situation was the same always as described above. I tried to read the program from plc and succeded to read it. It is a lader with about 6000 lines. Anyway I have no previous experience of the GX development environment but I tried to put the missing END in the program as sugested also by the flow chart in the manual. At this point I have to say that it was automatically added from gx developer as I can remeber from an appeared message. I verified also many times the program on gx developer with the plc and the only difference was that missing END at the last line of ladder program. Anyway I tried to write back to plc the program with correct end but it was not possible. I tried several times. The error mesages took with Gx developer was the following : "THE SAME T/C COIL EXISTS IN PROGRAM (MAIN) AND/OR PROGRAM (MAIN-SFC). THE VALUES ARE SET TO BE THE SAME AS IN THE FIRST FOUND T/C COILFROM THE TOP OF PROGRAM" "THERE IS A DEVICE IN THE PROGRAM (MAIN) THAT IS OUTSIDE OF THE RANGE. CHECK THE PROGRAM AND CORRECT THE DEVICE THAT IS OUTSIDE THE RANGE." Anyway I decided to delete the plc memory. After that the run was stop blinking and the error led went off. Only the error on the printer-ram module was on (This module was changed with a know functioning one witout any variation on behaviour). I thought that problem has gone now that the cpu is empty. I tried again to write the program to the plc but again i take the above mentioned messages. Now I have an empty plc and a program on the Gx developer that cannot be written to plc!!!!!!!!!!!!!!!!!!!!!!!!! I am desperate!!! I do not know how to proceed. I am not knowing the mitsubishi development environment. Other than Gx developer I tried to install the GX simulation but it not works to my computer. At this point I dont know even if the ladder program is somehow corrupted after the described above messages. I can sent the code (GX developer project) and any other information to someone expert, if necessary, to have an opinion. Please help!!! Let me know how to proceed!! I have to write back the code to plc !!!!! Thank you all in advance!! Now i realised that there is SFC that is my problem. Could someone help please? Big part of ladder is in yellow color. How can i proceed?
  23. Automation professionals, I would like to read the display values of a red lion DP700 in a control logix PLC. I was able to successfully integrate both devices through EtherNet / IP and I am geting the corresponding values in a DINT register in the PLC. But the problem is that the value in the PLC register is not in the same format as in the DP700 display. The display reads the length of a product in inches like 288.484 etc. Where as the value in the register is a 10 digit number like 1133526516. For sure, there is a definite correlation between these two values but I am not able to figure out the exact relationship as a function of a formula. I have given below 25 data pairs for your analysis. I tried to find out the scaling factor (slope and offset). The scaling that I found fit the first 10 records but did not fit the remaining 15 records Can you help me to find out the relationship between the ? # DP700 PLC register 1 288484 1133526516 2 288627 1133531202 3 288631 1133531333 4 288739 1133534872 5 288741 1133534937 6 288742 1133534970 7 288746 1133535101 8 288757 1133535461 9 288776 1133536084 10 288796 1133536739 11 241060 1131482972 12 241043 1131481858 13 241027 1131480809 14 241032 1131481137 15 241055 1131482644 16 241038 1131481530 17 241078 1131484152 18 241025 1131480678 19 241030 1131481006 20 241037 1131481465 21 241040 1131481661 22 241023 1131480547 23 241053 1131482513 24 241041 1131481727 25 241077 1131484086
  24. Sinamics G-120 Drive on Profinet

    Dear Friends, In my present project, I have a S7-1500 PLC & 3 Nos, Sinamics VFDs(PM-240s) with Profinet ports.(CU-240E -2PN) The drives and PLCs are on the same Profinet network. I wish to know the essentials of controlling the command and speed reference of these drives directly from the PLC on profinet. Reading the help in TIA portal got me nowhere its all about Telegrams and things that I haven't figured out yet Thanks for looking in; I shall greatly value all help and advice.
  25. B&R plc, motion control, CNC

    Hi all. I have a B&R PP420 panel, some I/O on the X2X and 4 Acopos servodrives /servomotors. Successfully created and tested 4 axes, they work OK, control via NCtest or X2X IN, or PP420 display. But creating CNC system is the problem... On NCtest, I have errors, and no move. Error 7742: ACP10_MC FB error or aborted Info: Axis Index [0] Info: ACP10_MC FB error number [29226] Info: Command aborted [0] Info: ACP10_MC FB number [1] = MC_BR_MoveCyclicPosition (cyc. pos.) On SDM, axis error: 32274 Network coupling: The broadcast channel was not configured Can someone help? Thanks.svinaga@yahoo.com Foto errors.pdf