Search the Community

Showing results for tags 'can i download program to fx5u by sd card'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 203 results

  1. Hello everyone, I am controlling a mitsubishi servo amplifier type MR-J4-20A-RJ with a Mitsubishi FX5U PLC. I am using DDRVI instruction to output the pulses to the amp with pulse/sign connection. Servo seems to work as requested, and cumulative pulses in MR configurator make sense. The problem: I can follow the output pulses and get a "position" from special register SD5502. If i understand it correct, the register sums the pulses output. If drive the servo to other direction, the register keeps adding up the value, not subtracting it. As i am new to mitsubishi, what would be the right way to get the position data? Is it possible to use the special registers for it, or should i just connect the servo to output the cumulative encoder pulses to PLC?   Thank you all for your time!
  2. Brian B

    I need help with a program I wrote for school that didn't work quite right.  I have to make a chasing light program that will freeze the lights when a PB is engaged and reverse when PB is engaged on light 1.  The assignment has already been turned in but our instructor ( if you want to call him that) has told us a similar sequence will be on the final.  Can anyone help me out??
  3. Dear Experts!!!   Could you please provide me the sample of "QD75MS Module & MR-J3-B program with functional block"    As you can see the page no. 3  in the attached document  "KI-Doc_QD77MSXX_MR-J3-XXBS.Zip" sample is there but i am not able to find it anywhere.   Or if you have any otherone please share it.   Please help!!! KIdoc_QD77servo_English_20130131.pdf
  4. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  5. Program not comparing

    Dear Sir, I need to update the PLC program offline with online, so I tried to compare the program blocks but I got the error that The comparison of the two blocks in STL showed that codes are identical. But still when I want to go online it is giving error that codes are different. Can anybody help us in this? New Microsoft Excel Worksheet (2).xlsx
  6. Is SOE card compatible with both quantum & premium plcs.? 
  7. CQM1H-CPU51 Download Program

    hello...... i use of C200HS-CN220-EU Program Download Cable for downloading program to plc. i can work online but when transfer to plc error is check dip switch.... i read manual and dip switch table but cant set dip switch..... please help me to setting dip-switchs for C200HS-CN220-EU Program Download Cable...
  8. How to resolve my plc is stop working after download program from H1U-XP with autoshop v2. It show download plc program process but i don't have any program in ladder chart. Pls help...
  9. Hello everybody, I want make communication PLC FX5U series and HMI GS2107-WTBD. IP for PLC is 192.168.3.250 IP for HMI is 192.168.3.18 I can make upload programs via Ethernet. My Laptop , PLC and HMI are connected toghether via switch. But I could connect data between PLC and HMI. So what must name of device and how to set BIT for example, which must communicate PLC<---->HMI. (bit.jpg) In GT Designer communication also write that i couldn't connect HMI via PLC in red , you can see attached picture. (GS.jpg) smiles : Altan ------------------------ Solved. My error was that PLC and HMI must have different Station Number Special thanks to Piotr Tynor(Mitsubishi, Poland ) , Adam Syrek (Mitsubish, Poland ) , I. Ayvazova (Bulgaria) , K. Raykov (Bulgaria) /you can see atched .pdf file/ MTS0026 - FX5U and GOT2000 (1).pdf
  10. FX5U

    Halo, i have question and asking for help. my factory use mitsubishi plc type fx5u. can anyone help me how to setting everything that make motor servo can run. PLC : FX5U Ampli Servo : MR-J4-70A Thank you for helping me.
  11. Verify program

    Hello, I have a question concerning the verified program. I do not know if the program is verified or not. I can not upload pic. I have 8 programs Verify result MATCH and one green line Data (Verify destination):NOT TO USE Verify result: Dest. Only. The green line is confusing me. I ask for an explanation. Please. Greetings to all
  12. I have a problem when trying to download a program from a FX1S-30MT PLC. I am using a SC-09 USB cable. The software i am using is GX Developer 8. When trying to download the MAIN program the screen in the attachment appears. I tested the download from another PLC of same model and have no problems, therefore the cable is ok, and the laptop is ok. When downloading of the parameters and comments does not give error, just when trying to download MAIN. Also I tested connection with Test Connection button and says communication is ok. Anyone who can help? I have a doubt, how can i see the communication parameters on the PLC side? Thanks a lot
  13. Hardware & software HMI - Beijer iX T12B / iX Developer 2.10PLC - Mitsubishi FX5U / GX Works3Error HMI shows "Controller 1: Comm err station 0". i.e., The HMI isn't getting a response from the PLC. IP addresses are all correct and ping (and can be programmed) OK. The HMI software PLC comms configuration has a "port" setting - see below. I can't find anything comparable on the the Mitsubishi software. Does anyone know what insight I'm missing here? iX Developer is configured as shown below: Note the port setting above. I can't find any documentation on what the PLC is expecting or what's special about 1025. The PLC is setup as below with GX Works3: Anyone got any ideas how to get the two talking? Many thanks.
  14. How do I check the program execution order in GX Works3? The help file says but there is no context menu option when I right-click any of the items in the Navigation / Project View. Any clues?
  15. Hello! I am working with RSLogix5000 software and writing the program. Very often I need to download the program to the CPU and of course it writes all program at the same time. This downloading makes problem to me, because I loose parametrizised data from the CPU, downloading will always overwrite default values of the tags. Some parameters are written from the panel and I want to keep these parameters allthougt I am downloading new program. How should I handle this? Some tags can be overwriten, some not.
  16. Help about converting program

    Hello, First of all, Hello to all members. Im From Portugal. I trying to help my dad. I Have a Omron CJ1M-CPU11 with a program running that works fine... Now i need to transfer this program to a CJ1M-CPU13. I started to download from CJ1M-CPU11 to a file... them im running the Cx-programer on the CJ1M-CPU13, connection its ok, but when i try to transfer i get this error : The connect PLC type : CJ1M-CPU11 The Project PLC type : CJ1M-CPU13 Its possible to convert ? Please Help. Please view in attached file. Thanks
  17. Hello: I'm not sure how to go about creating the structure of this program, would like some ideas/help. I have a program that checks/reads 8 analog inputs and compares each input against 4 different settings, if the value is outside any of these settings the program runs a subroutine to send out an email for (Alarm/Event) notification for that particular input. The way the program is structured now is that it reads analog input 0 first and checks against the settings if the reading is not in range it will call a subroutine to send out email for that sensor(analog AI:0.0) then it will return and read for Analog input #1 and check reading and if it needs to it will call another subroutine to send out email for that sensor(analog AI:0.1) and so forth. What I need to add, is a way to count how many times a sensor(input) has sent the alarm email because I want to limit this to 5 notifications after that, stop sending emails. Now this has to be done for each sensor(input).(Note: I would also like to have a timer involved so that it will only send emails about every 15 minutes for 5 counts.) I need this because the plc will send out emails until the error for the sensor has been corrected, this could take a few hours and if I don't have some sort of control, that would result in 1000's of emails being sent and world probably get shut down for spamming. Would like some ideas on how I should go about this. I am using a micrologix 1100 and rslogix 500 software. Thanks
  18. Do I need to write the "Program Loop" into the ladder or will the complete program start over once it has hit the "END RUNG"??? Micrologix 1100, programming with the RSLogix500. Thanks
  19. We have a couple Mitsubishi FX2c-96MT 's running a Laser engraver and one of them appears to have a faulty card or connections on the card. we picked up a couple spares one is a FX2C-96MT and the other is FX2c-96MT-ess. Is there really a difference between these? I see on the old PLC the middle card says ess on it already? we need to "harvest" the current plc program before swapping into the new unit. we picked up one of the cheapie pc connection kits which doesn't look like it is right and don't want to connect it and burn something out. IT has a rs232 on one end than a male 25-pin connector with a second cord that goes from female 25-pin to the mini-DIN connector. Neither of the FX2c-96MT plc's have a mini-din connection as i read online everywhere. there is a 25-pin connector on the top next to the FX2c-96MT label. is this the programming port? I would have assumed the programming port would either be the one covered up by the battery cover or the little one on the end with a 3/8 x 1" cover. I am assuming thae, with no instructions for much of anything. Thanks for all and any help in this matter t we should be able to use an older laptop running winXP for this? i downloaded GX developer and will install it on the xp laptop as soon as we are able to be sure of a cable that will be safe and not damage anything. If this cable we purchased will not work, could someone send a link for instructions to fabricate one? I see several in a gogle search, but they are all different and we want to make sure we do this safely as the program on the PLC is apparently NOT backed up anywhere, and the people who set it up years ago are long gon Paul
  20. Hi all, Currently running a Quantum 140-CPU-652-60 FW3.12 out to a remote rack over a Modbus Drop in to a 140-EHC-105-00 High Speed Counter, words are mapped OK to the program, configured at a type 7 setup (1sec frequency) etc. The card used to work when we were running the system as a ConceptXL 2.6 setup with a 140-CPU-534-14. We have just upgraded to UnityProXLv8 and it stopped. The mapping is configured by word to bit / bit to word across the %IW and %MW (previously 948 3x and 4x registers, but converted nicely, everything is aligning). Anyone stumbled across this issue before? Any help would be appreciated. Thanks, Rob
  21. Hey, this may be an obvious question, but here goes: I have a CompactLogix L36ERM running RL5000 controlling one of our lead die cast machines. When I make a change to the program offline and need to download I always go and shut the machine down for safety reasons before downloading. One of our techs stopped the machine but left the control power and hydraulic pump on while downloading (something we are not supposed to do) when he finished downloading he switched it back to run mode and the machine closed on it's own and started right back up. This is a safety concern to me. We have a "close enable" tag that is true when all necessary conditions are met, and gets latched on when the machine is running in full auto. Before he downloaded the machine was at idle, meaning that the only way to close the machine would be to press the two dead-man switches to start the process. But, when he downloaded it started up automatically. Now I know the reason why is when the program was last saved, the "close enable" tag had a value of 1, it was latched on, so it bypassed the dead-man switches. A quick fix would be to save the program with that tag un-latched so that it can't start up on it's own after downloading. But, in case somebody saves the program while the machine is running and with that tag latched on, I need a better solution. Is there any tag or bit that goes true when a program is downloaded or when the mode of the PLC is switched from run to download to run? I want to manipulate that tag so that when I download it un-latches the "close enable" tag. I'm sure there is a way to do it, I'm just not even really sure what to search for in the online help. Any help is greatly appreciated. Thanks Howard
  22. I am trying to determine or find any figures that could assist in obtaining the lifespan of a single output of a 1756-OB16E output card. I have a signal sending 400 pulses a minute to an output. I am starting think about when this card or output may need to be replaced before failure. I was given a MTBF range by Rockwell for the card itself but they could not expand on the likelyhood of the output failing exponentially due to the rapid signalling. I could also not find anything in the manual itself that could provide me with an idea of longevity, I could be missing it? Also with this project I experienced something odd with the originally scoped hardware, a solid state 24VDC relay (700-HLS1.) By measuring the resistance I was able to see that the relay should have been opening and closing but the signal was not being received. So, I swapped the solid state relay for a mechanical relay and it worked fine. I was curious if the leakage could have an effect on this. The problem with the mechanical relay is that the life is dramatically reduced to about a month for this installation, life for the relay is shown at about 10,000,000 actuations. I was hoping to have this working with a little longer life expectancy. If anyone has any experience / tips / or suggestions it would be much appreciated! PG
  23. I am writing a new program for a MicroLogix 1500 LRP Series C. When I verify the project I get the following errors: Program error ERROR: Attempted to set more IO data than has been allocated Program error ERROR: Incorrect Output Force File Size The IO Configuration should be correct because I had the software "Read IO Config". I don't see any unverified rungs. My software is RSLogix 500 Version 9.00.00 (CPR 9) Does anyone have a solution?
  24. Hello Everyone, I am new to ladder logic, and trying to understand flow of below attached ladder logic- How does the program flow ? Does PT4601_I in rung 3 waits for rung 2 to complete inorder to consider updated value of PT4601_I or it consider PT4601_I default value and runs simultaneously with rung 2 ? Thank you in advacne
  25. Dear all, I need some help with programming time in concept 2.6 in FBD. I use momentum PLC 171 CCC 980 30-IEC I would like to program 24Hours Clock with day, week and year. Can someone help me with this please. Regards Sam