Search the Community

Showing results for tags '1769-it6 causes processor to fault when put in run mode'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 74 results

  1. Hello Guys, i have an issue with my powerFlex40; it's getting the F081 sometimes after a start. I have 4 pf40 and they are almost configured the same way and this working like this for years. the 4 pf are wired in the same way that when an emergency stop is pushed they are all powered off(400V); after acknowledging the e-stop they all start normally but that one brings sometimes(not always) the F081: Comm Loss. I can even not reproduce the issue because it is not happening every time.  Any Ideas what it could be? the network cable of the pf goes to a switch (all the 4 pf are connected on that switch) and from the switch to a 1794-AENT Ethernet adapter.
  2. Hello everyone, I have a problem with packing machine. There are some issues with one of the axis, when axis actual position is near to 1800000 some error appear and operator has to turn off machine on main contactor. This axis is working in Linear mode. I think that rotary mode would be better for this axis. And here is my question. Which instructions, and what options i should change/check when i change count mode in axis's options. Can any1 point me some manuals to read or give me some advice ? Thank you in advance.  
  3. PLC occasionally going out of Run mode?

    Has anyone had an issue with Siemens plc's occasionally going out of run mode? I was doing some research and found that it could be due to a bad analog input. Is there a way to tell which input or output is causing this fault? I know I can create a hardware diagnostics error organization block but that only correct from what I've read.     Edit: I've added a screen shot of the diagnostics report. The fault that may be the problem is: Temporary CPU error: Serious firmware exception  CPU changes to DEFECTIVE mode (system reaction)  This plc / system was installed 2 year ago and we've had this problem occasionally since. I'm guessing the wrong firmware was used during the install. Will try upgrading firmware this weekend.   
  4. Hey, I have a 1763 L16BBB...when I plug the 1762IF20F2 analog card in, I get a 0189h error code. Any help would be appreciated. Currently looking at doing a bootp on the plc to get online...no ip
  5. Hi All, I have an AB servo TLY-A110T and 2097-V31PR0-LM Kinetix 350 drive. I thought that it was fully configured and ready for tuning, but when I issue a MSO it immediately starts to spin the shaft (no load yet). This lasts about a second until a Physical Axis Fault, Excessive Velocity Error occurs. I've double and triple checked the feedback and power wiring, and everything looks right. Is there anything else I can check? What can I do to trouble shoot this if I can't even give an MSO? Any insight is greatly appreciated.
  6. BECKHOFF CX-9020

    Hello PLC experts, I am master student currently writing thesis. For this, I have a initial task of making some changes to PLC program (Just started getting to know about PLCs- complete beginner). I have a BECKHOFF cx 9020 PLC connected to my notebook using ethernet. I am using TWINCAT 3.1 (VS) as IDE. Firstly, I cannot find my PLC IP address connected to my notebook . I added the route in the Twincat and it shows the PLC is connected. When, I am trying to run a program (activate boot project), I am unable to login to the PLC. It gives an error "login failed for application port 851". What I undertood from BECKHOFF scripts,  there is something wrong with the ADS ams net ID which I am trying to figure it out. I appreciate all the help. Thank you.
  7. faulted processor

    Hi I'm a bit new to Siemens, we;re an Allen Bradley plant...until now. we just got a brand new used press and it has a seimens controller on it. The press doesn't seem to have any manual functions so I as asked to move the cylinder, but I can't until I clear this fault. it won't do anything.  I'm told I'm working with an older processor, s7 300?I don't really know seimens that well.  I saved the diagnostics buffer as a text file and pasted it below. in case that helps solve my problem. I'm thinking it's just having trouble communicating with remote IO, but I'm not sure. I might be trying to communicate to a robot that used to be there that no longer is.  Diagnostic buffer of module CPU 314C-2 DP Order No./ Description            Component                         Version                        6ES7 314-6CH04-0AB0               Hardware                          5                              - - -                             Firmware                          V 3.3.11                       Boot Loader                       Firmware expansion                A 37.12.12                     Rack:                             0 Slot:                             2 Serial number: S Q-EDU050142014 Event 1 of 10:  Event ID 16# 2522 Area length error when reading Global DB, word access, Access address:    262 Requested OB: Programming error OB (OB121) Priority class:  1 Internal error, Incoming event 10:36:07.052 AM  04/17/2019 (Coding: 16# 2522  0179  0024  0106  0000  0000) Event 2 of 10:  Event ID 16# 2522 Area length error when reading Global DB, word access, Access address:    260 Requested OB: Programming error OB (OB121) Priority class:  1 Internal error, Incoming event 10:36:07.052 AM  04/17/2019 (Coding: 16# 2522  0179  0024  0104  0000  0000) Event 3 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     40 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.052 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0028  0000  0000) Event 4 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     36 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.052 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0024  0000  0000) Event 5 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     38 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.051 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0026  0000  0000) Event 6 of 10:  Event ID 16# 2522 Area length error when reading Global DB, word access, Access address:    262 Requested OB: Programming error OB (OB121) Priority class:  1 Internal error, Incoming event 10:36:07.051 AM  04/17/2019 (Coding: 16# 2522  0179  0024  0106  0000  0000) Event 7 of 10:  Event ID 16# 2522 Area length error when reading Global DB, word access, Access address:    260 Requested OB: Programming error OB (OB121) Priority class:  1 Internal error, Incoming event 10:36:07.050 AM  04/17/2019 (Coding: 16# 2522  0179  0024  0104  0000  0000) Event 8 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     40 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.050 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0028  0000  0000) Event 9 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     36 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.050 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0024  0000  0000) Event 10 of 10:  Event ID 16# 2943 I/O access error, writing P area, word access, Access address:     38 Requested OB: I/O access error OB (OB122) Priority class:  1 External error, Incoming event 10:36:07.050 AM  04/17/2019 (Coding: 16# 2943  017A  0020  0026  0000  0000)
  8. Hi there, is somebody experience whereby the output of the 1769-OF4Ci is not responding on the value entered?.  Setting: 4-20mA Res: 0- 32767 - PID set whatever value I key in the output current remained.  please help. Ganie
  9. Hi, Can someone provide information about function and interpretation of each flashing or steady LEDs on MLC 1200. For example where to look for when Fault LED flashes during normal operation and so on. Thanks in anticipation that someone will help. Regards
  10. Hello forum! I'm using AB Compactlogix 1769 L35E CPU energized by 1769-PA2 power supply which is also supplying to 1769-SDN DeviceNet scanner, both via backplane. Trying to build a simply DN network connecting the scanner to a Balluff BNI DNT-104-000-Z004, which is a 16 PNP digital input block, since is only input module I rely that no extra power supply will be required. The problem is that when connecting both scanner and input block via my DN thick cable (Balluff BCC07YY), the input module does not energize. In fact I got no voltage reading when measuring voltage between scanner V+ and V- terminals. I measured voltage at 1769-PA2 power supply DC output (which is not in use) and its providing 24VDC, also scanner is powered on so I do not think the problem could be power supply nor backplane. Scanner display shows 92 number, scanner manual says that 92 error is "no devicenet power" and has the following description: No network power detected on DeviceNet port. Provide network power. Make sure the module drop cable is providing the proper power to the DeviceNet port. Which I do not get, is not the power supply from 1769-PA2 via backplane enough?  Is not the scanner supposed to provide voltage to the network? I've no grounding connection connected to PE yet (just between devices GND terminals)... is that a problem for testing this small network? It will be done soon but now I'm waiting for cable material. Actually I'm online using Studio5000 and have 1769-SDN DeviceNet scanner device declared at the project, there is no warning nor major fault displayed from the software. Thanks for reading.
  11. Trying to figure out a fix to a processor issue, I have 2 1785-L40E processors a series E and F. Both when inserted into the rack and powered up go straight to a solid red BATT and PROC light as well as a Solid amber Force light, they both wont even attempt to start a boot up sequence. When connected through DH+ and ENET there is no visibility to either of these processors. These are refurbished processors.
  12.  Hi all. I have a question about how to set up the motor in rotary mode. My application will be a basic rotary table driven by a servo motor without gearbox between. So, in my servo drive axis settings, I select the motor as a rotary mode. then I defined the maximum position setting value for 360 degrees, and minimum to 0. So far so good. But the problem comes when I want to make an absolute move using the mc_moveAbsolute to move 360 degrees. Whit this settings the error "target position settings out of range " will come up. So, what is the solution to rotate 360 degrees without generating this error? if I set up the maximum value to 361 degrees and then if I rotate 360 the error will not occur and the motor will rotate 360 degrees as I aspected, but it's this correct ? or there is another way to do it? Thanks  
  13. C-mode hostlink library for NJ/NX1P or CP1L

    Anyone knows if there is a C-mode hostlink library for NJ/NX ? Also, a C-mode hostlink library for CP1L could be helpful, to translate such a library to work with NX1P is probaly less work whan writing a new library.  Maybe Omron France has developed such a library? - they seem very active..   Background: Looking into writing a programmatic c-mode hostlink master for NX1P12, this is for connecting the handheld NSH5 HMI to the NX1P12 via RS232C using a CIF01. I have the hardware set up, and an machine built, expected some compatibility efforts by Omron.... but the NSH5 seems to talk C-mode hostlink, and the CIF01 only seems to support the FINS version hostlink.   On the NJ you can of course add an SCU module, thus not need a library.  But working with NX1 ( due to limited space available ), you are dependet on available CIF-modules which do not support C-mode hostlink.  
  14. Can anyone help me with the information related to Fx-5 and Fx5-4LC module. Like which processor is used for internal operation ?? What is the selection criteria for that ??
  15. Here is a link to a thread on a recent post showing how to communicate serially to an Omron PLC using VB.Net. This uses the Omron Host Link serial protocols. (C-Mode Commands) It will read 10 DM registers and display them on the form.   http://accautomation.ca/implementing-the-omron-host-link-protocol-vb-net/ Here is the source program that can be downloaded. Other links: VB6 Program: http://accautomation.ca/how-to-implement-the-omron-plc-host-link-protocol/ VBA Program: http://accautomation.ca/how-to-implement-the-omron-host-link-protocol-part-2-vba/ Regards, Garry www.accautomation.ca
  16. Hi, I have some trouble with a CJ2M-CPU33. My client did a backup to memory card earlier today, and after this we did some changes through remote link. Now the client wanted to restore the previous backup to the PLC and has done so, but the system would not function correctly. After going online on the PLC it seems like the PLC is stuck in "Stop/Programming Mode". When trying to change to "Monitor" or "Run" mode a dialog comes up containing the following message: "Failed to change the operating mode. The operating mode may be still changing in the PLC."  - All the dip switches are set to off after restoring backup - The PLC has been rebooted  - I have downloaded the application again through CX-programmer  - Verified that the PLC is set to start up in "Monitor mode" But nothing helps. The same message comes up when trying to change the operating mode.  Hoping anyone can help to resolve this issue as it is very critical for us and the client. In advance, thanks for any tips or help received. Best regards Stian
  17. Symax model 400 processor.

    Hello.      Does anybody know if theres a newer interchangable version of the symax model 400 processor?     Anybody know wat equipment is needed to program a model 400??
  18. I need to run 4 exactly same devices with 4 different controllers. The logic for them would be exactly the same but the IPs and controller names would be different. Is there a way to do it using 1 project file? Basically whenever download is done the logic would be downloaded but the controller name/IP would be left unchanged. They will be connected to the same network so the IPs must be different. I am using 1769-L32E for these and all racks are set up exactly the same. Any ideas?
  19. Hello everyone, my name ia alif from indonesia i have redundancy module 1756-RM2 controllogix5000 Allen bradley. On the module, fault codes appear as EG12. What is it means ?   I have already search in the user manu but there is no explanation about this fault codes.     Thank you
  20. Has anyone used a 'Spectrum 1769sc-IF4IH' hart card?  I am currently using studio 5000 vr 24.
  21. Hello,  As the title indicates, we have a micrologix 1400 that has been installed for a long time.  Recently it faulted out on 71h and was in Remote Mode.  Do these PLCs revert to Remote Mode when in a fault condition?  We placed it back in Run Mode and everything worked fine, but how did it get to Remote Mode in the first place? Thanks,  J 
  22. Binary Mode vs BCD Mode

    Hi all, I have created a program using the binary counter and timer instructions and everything works fine (yay!), but I am not entirely sure if there is a major difference between using Binary mode or BCD Mode on the PLC. Does it just come down to personal preference or is there an advantage to using a particular mode over the other? Also, does the operating mode affect anything besides counter/timer? The option in CX-Programmer seems to indicate it doesn't. Cheers, Jay
  23. I'm trying to ramp up from zero to enable a NJ calculated random curve to never produce a negative position point:                                                     Calling the move "Offset", and using a MC_MoveAbsolute fb, the idea is to trigger the curve generating ST to start when the move reached 50mm.  (Wanted the variable "Ready" to go TRUE at the end of the ramp to 50mm)  .. Then, MC_SyncMoveAbsolute fb would continue from there, sending streaming position data to the LinMot Linear motor. As seen above. But, there's a problem.  Initially, I used the MCMoveAbsolute.Done to start the ST curve move sequence, which also ramps amplitude from zero, over a period of 3 seconds: Offset + [(a number that goes from 0 to 1.0 in 3 seconds) * (the mathematically generated position curve)]   The result is a "clunk" at the transition of the end of the ramp and the start of the curve. Not sure when "Done" happens... started to think perhaps it's when the fb is finished making the command to move, and not when the move has actually finished. So I tried an IF_THAN:                    That was kinda silly, because the ramp final position never reached 50mm ... "Ready" never set to TRUE ...  close, but no cigar. So the next step was use a Round instruction that actually monitors the position of the slider: and a EQ instruction that compares the two, and issues a "Ready" command to start curve the curve program:                  This produced the Minor Fault:  Axis 0x543B0000 Motion Control Instruction Re-Exicution Disabled Now I'm thinking this can't work because "Ready" will only be TRUE when the the curve hits 50mm (which is quite often, after it starts running ... 50mm being the new zero) However, It did start the curve sequence.. but nothing moved because of the fault... Soooo.. The question is: How can I do a smooth transition from the end of an Offset move to the start of the curve?  Or.. better still...How is an "Offset" normally done to any curve generating routine? Thanks much, Regards, Michael PS:   Here's a look at what's happening when I tried using State Tracker... and something to compare actual position at the end of the Offset move, and the start of the random sea curve: https://www.youtube.com/embed/BdpvC1yyKxU?rel=0&controls=0&showinfo=0      RSStart is the variable that powers the Random Sea ST program, and the SyncMoveAbsolute fb that drives the motor.  Cycle time is 1ms.  Probably would be quieter if I could 500us .. but the NJ is only a 101-1000               FYI... Delta Motion's RMC75E Motion Controller can make the Random Sea using LinMot's B1100-VF drive .. as quiet as a mouse.  But then, I think that controller has a cycle time of 1us!   Wondering if there's a problem with Direction or BufferMode:    _emc_Direction#_mcNoDirection or _eMC_Buffer_Mode#_mcAborting ????  Thanks for any ideas on the "Clunk" ... I may have to live with the "singing" ... sniff!  .... or use a Delta Motion Motion Controller ..      
  24. I got a CJ1M CPU11 that I can connect to but I can just go to run mode but when I try to switch to program mode I'm tell that I can modify the mode
  25. I have just started programming PLC's and the first thing I have came up against is a 4-20ma signal to a analog card for a Turbidity meter. The problem I am having is the reading is very erratic. Is there any way to get it from jumping around so much?