Search the Community

Showing results for tags 'schneider 140 upload'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 92 results

  1. Hello everyone, I hope you are all doing very great, I'm new to Schneider PLCs and I have a project that I need to work on, so I will need your help with the following issues: *) How can one determine which Schneider PLC series is used if you only have a fuzzy picture of the PLC ?  *) I need to setup a historic of alarms, I have 13 PLCs, no connexion between them... I was thinking about creating a connexion between those PLCs and a database, so I need your help to determine a list of ALL the materials i will need (from cables to servers to a computer if necessary...) and some documentation on how that can be done... Thank you so much for helping me, Best regards
  2. Hello guys,   I'm new on this forum but I'm not new at PLC programming world. So far I had only experience with Siemens PLC controllers.    Now I have a relatively simple application in which I have 12 DI, 4 DO, 4 AI and 4 AO. The client insists that I use Schneider PLCs. I must admit that I had no previous experience  with these PLCs. Therefore I kindly ask for your help in choosing the appropriate PLC configuration.  The PLC must have RJ45 for connection to LAN network. I want to create a small HMI application and thinking of using IGSS software. There will be one simple PID controller to control temperature in one vessel.  Temperature is 4-20 mA signal. Via HMI application, operator can change setpoint for the temperature closed loop. Also, I need that other computer on the network have possibility to open HMI picture but only in read only mode. For this purpose, Web server would be ideal. I was thinking of using M258, but it seems to big controller for this number of I/Os. What can you suggest me regarding the PLC configuration and HMI software? Thank you!
  3. Hello there. I have connected wireless module (master) to Vijeo Citect 7.4 using RS-485 to USB converter. My slave modules are supplied power from gird/generator and the master module is supplies from a UPS.    I'm reading Modbus registers of slaves modules data via wireless master. Every time we have a power failure from grid, I get #BAD from all slave addresses. The generator kicks off within 30 sec. That is the slaves are off for 30 sec. Even after the slaves are powered on, SCADA does not poll data from it until I restart the SCADA.    My current MODBUS parameters are:   Inittype = 3, TimeOut = 3000, WatchTime = 10, Retry = 2. Could you please assist me on which parameters to change in .ini so that SCADA reads Modbus registers of slave for more than 30 sec.   I tried increasing TimeOut to 30000 but it couldn't solve the problem. I would appreciate if some one could help me out.   Thanak you in advance.      
  4. Hi, Um new to plc and at the beggining i bought a Twido TWDLCAA24DRF old one without the cable.I want to know if any rs485 to usb cable is possible to programme this plc? please someone help me   is this cable is possible?
  5. Hello, i have a premium plc of modicon schneider electric i made the application 6 years ago and now i want to change my variables but my password does not work anymore or i forgot. does anyone know how to recover this or to crack my own password. th   suriname
  6. Hi, i'm new to this forum. I encounter some problem with the existing set up, where  Quantum Hot Stanby PLC (Master) can't read/write to 3rd party ESD PLC (Triconex). Quantum PLC need to read from ESD PLC where the configured IO for modbus is in bool(coil) instead of word (register). Any idea what i can do beside getting ESD PLC to change from boolean to word? thanks,
  7. Hello gents,   I have an issue were I try to upload the program in the processor.  I have a copy of the program from a few months back however there have been some changes made to the program since then therefore RS5000 prompts me if I want to upload or download.  The program was done in v 20.01 and thats what I have as well. When I select upload everything goes good as fa as connecting and uploading tags but as soon as it start uploading the routines it stops part way through and gives a message that Logix couldnot upload AddOn instruction.  Has anyone seen this andhow did you get around it?
  8. how upload files where can i view the files to uplaod
  9. Hello, We have Modicon Momentum PLC and there is about 80 millions of Collision Errors (and growing cca 1.4 error per second) logged in Ethernet Statistics. In the manual they write only "This field should allways be 0". It is working for us though. We only have one problem that two machines on ADO 740 50 with ENT 110-01 stop simultaneously and irregularrly without any appearent reason. It is happening now for about 6 months, but I have calcluated that this collision errors accumulated over cca 2 years. My question is, what "Collision Errors" mean and could that by any chance make two particular machines on one ADO 740 50 module go off simultaneously?
  10. 1749 SDN device net scanner in control logic. How to upload device net file from scanner through ethernet connection. Anyone can show me how? thanks.
  11. Hello! So I have this issue with me by this week. I have an NJ with unit version 1.00. I had not did any download/upload on this unit. Due to the need of showing using Password capability on Function Blocks, I need to upgrade the unit firmware version, so I changed it to 1.10. After that I tried to program a simple two Sections program. I left the CPU for a week, then when I get back to it, I upload the program from the CPU. And the upload was SUCCESSFUL! No errors are shown. However all of the Rungs inside each Sections contains nothing. Even though the two Sections that I made before are still present. The program itself is still working though. If I open the previously saved project, going online and do variable controlling, I'm still able to do so. Has anybody experienced this before? Any suggestions / solutions? Thank you...
  12. Hello everyone, I'm having some trouble to setup the GSM configuration so I can receive alarms on my cell phone I'm using Schneider CPU Modicon M340 in association with a communication RTU NOR0200H and a Schneider Modem SR02 MOD02 this is the first time that I work on this kind of project, would you please help me I'm kind of blocked and I need a solution asap thank you for your time
  13. Hi everyone, Last time I want to make upload and I can not do this. I have message: "Failed to upload project. Reverting the last saved copy of ... " Like on the picture Maybe somebody had this problem ? Thanks in advance
  14. Hi I have a scenario where I need to setup communication between a Mitsubishi L-series PLC to Schneider Modicon M580. I need to use the onboard ethernet port of the L-series PLC. The protocol I need to use, is Ethernet IP. (socket communication). Can someone please assist?
  15. I am trying to upload from Panel View Plus 600 to my laptop using Factory Talk View ME via Ethernet. The RSLinx Enterprise does see the Panel View but when I hit the upload button I get the following error message: "The source selected is not a valid device. Please select a valid source and try again." Does anyone know what is the issue? I am attaching screen shot to visualize what is happening.
  16. Dear All, I have a little problem in reading data from Power Meter to Vijeo Citect v6.0 I'm using Schneider PM810MG for Energy reading from Power Meter and for the SCADA I'm using Vijeo Citect v6.0. I can do some simple data reading like current, voltage and the others using variable tags from Vijeo Citect with Data type INT. But i dont know how to read the data for "Real Energy In" since the data range from 0 to 9,999,999,999,999,999. Waiting for all your help soon. Thx. Best Regards, Budiman Chandra
  17. can anyone please provide me how to communicate between keithley controller 2182A(nano voltmeter) and any modicon or schneider plc.aslo the programme & instruction & parameters..ASAP using RS-232 interface?