Search the Community

Showing results for tags 'read program file'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 122 results

  1. Hello, On our DCS we have a button that will open an RDP connection to our PLC server and open the .mer file connecting the DCS to the PanelView HMI. This is supposed to be used for troubleshooting purposes only, but that is not the case. Is there a way to prevent operators from operating the HMI through the RDP while still allowing them to have read only access?   Thanks, Michael
  2. Hi, I have inserted new RTD module into in my SLC500 as replacement to defected RTD module however the module LED is enabled but the channel LED's are blinking. I have checked the following: In the advanced I/O configuration the module configuration is shown as expected In the data file word format it is not corresponding to the channel preferences What should I do and how to fix the word bits?        
  3. How to scan Ethernet/IP network?

    Scenario: You show up on site and the only knowns are Omron PLC and EtherNet/IP network. You have a laptop loaded with CX-One, an ethernet cable, and the ethernet port that is connected to a known EtherNet/IP Omron network (you can not see the PLC). I have previously worked with Siemens systems and used Primary Setup Tool and Proneta with wonderful results. Do similar tools exist for an Omron environment?  Question: How to (relatively quickly) scan an EtherNet/IP network for connected devices without knowing their ip addresses?  
  4. plc mtsubishi r series and rj71c24-r4

    hello, im working with r04 mitsubishi plc with rj71c24-r4 in modbus rtu mode, i need to read and write PM1200 scheneider values, but i have problems, is my first time with this model and very different than fx5u model, i working in GX works3 someone who can guide me, I would appreciate it too much
  5. I have an analog output card 1734-OE2V and there is in the fault/actions page parameters for program mode. What is program mode and when it is activated? Fault mode is clear but... Program should be written the value, but when this happens?
  6. Pumps controlled with counter

    I need som help and suggestion how i can control 2 pumps that shall go 10 times each?i have 2 level sensors that is giving it the start and stop,and pump1 shall start 10 times,then pump2 shall start 10 times.Can i use CNT and how is the best smooth way to do it?   thx
  7. Hello Im trying to read from my PLC but i cannot see the program file.  However, if i try to compare it using other file program, i could see the program file. Is their any restriction in my software?
  8. Sysmac Studio

    Hello ,  Is my frist project on Omron and also on Sysmac Studio .  I have one PLC NX1P2 - 9024DT1 I write a sample program on ST with internal variable ( struct ) but i receive an information that i dont have permition to write on Var  Ps.  I can uploaded file with image   
  9. Hello all, I need to read device memory mostly I need to read R registers from PLC L26. I read device data, but inside of table, I can't find R or ZR registers. Can you help me?  What I did wrong?   BR KS  
  10. FX-2NC-32MT PLC program Download

    Hi, There are two machine in the factory controlled by Fx 2nc PLC. One machine control part is not working. It could be for battery failure. But the other one is working properly. In this case can I change the battery?  After that,  is it possible, I upload the program from the good machine PLC and download it to the other machine PLC? Regards Sohel Ahmed
  11. Hello, I have some files for a piece of equipment but do not have the RSlogix software to view the code. It is for a SLC 5/02 plc. Would anyone be willing to convert the files to pdf for me, it would be greatly appreciated. Thanks in advance! 2730-AR14.RSS 2730-AR10_BAK494.RSS 2730-AR10.RSS 2730-AR9.RSS 2730-AR7.RSS 2730-AR15.RSS
  12. Hi,     I'm trying to communicate Omron CP1E unit with PC via serial port using hostlink protocol.  I need to read the Timer/Counter SV value and write the timer/counter SV values to the PLC.  I'm able to use other C mode commands (like RC (timer/counter PV read), WC (timer/counter PV write) etc.) but when I give the command for Timer/Counter SV Read 1 which is R#, I get the response as IC (Undefined Command).   How do I write or read the timer SV Values?  Example command and response : @00R#TIMH001028*  (TIMH is the high speed timer, 0010 is the timer number and 28 is the FCS) Response: @00IC4A* Is is that CP1E doesn't support these commands? If so what is the equivalent command that I should send inorder to perform this? Please help.  
  13. Hello, We have a FX3G connected to a FX3U-ENET-ADP inside a main cabinet. We are then using that master PLC to collect data from 2 other fx3g plcs in a node:node serial network. I was assigned a small project of pricing out some wireless adapters so we can upload/download to the two slave plcs. My question is, is it possible to upload/download programs to/from the slave plcs through the ENET adapter and serial network in the main plc? It would save us some money if possible. thanks.
  14. Hello all, is anybody out there who may read out a program that is stored on a telemecanique cartridge (more or less of 1993)? Program is still running on a TSX 47 40, but have an identical second cartridge. I would send it to him/her even if international post and do not necessarily require the cartridge back. Would be great to have the program as a text file / pdf / hardcopy. Any help appreciated!! Best regards Stefan
  15. I am looking for how others have set up vertical axis motions using the Kinetix 5700 servo system. I have a 2 axis pick/place unit with a horizontal axis (X @ 2500mm) and vertical axis (Z @ 1200mm) that works as designed during normal operation. X axis has no holding brake and Z axis has a factory installed 24vdc to unlock brake. There is a GuardLogix L81ES control system that handles the safety and control. On pressing E-stop/opening Gates the vertical axis will stop the motion, apply the brake and hold with no problems. (2198-D032-ERS3 Drive, 2198-P031 Bus Power, MPL-B430P-MJ72AA X Axis, MPL-B330P-MJ74AA Z axis) The issue that I ran into was an accidental download of the program without activating the e-stop and the vertical axis dropped unexpectedly when entering program mode on the processor. I am aware that this instance was my fault as the programmer, however I am also concerned that this might occur again in the future if the controller ever enters fault mode or someone else completes a download. I have done some investigation with the "ProgrammedStopMode" parameter on this single motion axis and attempted all 5 options and the vertical axis still has a free fall drop for a second before the brake grabs hold - so evidently this is not working for me. (Page 24 of Vertical Load/Holding Brake manual - https://literature.rockwellautomatio...t003_-en-p.pdf) I am curious if there needs to be something done elsewhere as the X and Z axis are set up as coordinated axis? I also am unaware if I need to preform some action/parameter with the bus power supply for this? The current state of the machine as it sits now is preforming a MSF in manual mode after 5 seconds of inactivity or 30 seconds in auto mode. This axis is usually in demand every ~22 seconds. This will shut down the axis after preforming a brake test on the vertical load and seems to function OK, however it is still in the back of my mind the issues mentioned previously if we ever enter a controller fault while indexing. Thanks for your insight
  16. Folks, we have a set of Mitsubishi Q12PRHCPU (redundant) running effortless since many years. CPU-A as standby and CPU-B as Control. Recently we noticed BATT low alarm on CPU-B. So we arranged for a spare battery Q6BAT and started the procedure as per manual(attached procedure and flow chart). We did memory copy from Control to standby (as prescribed precaution) and did the Reset of Standby PLC CPU-A. Memory copy from B to A completed successfully 100%. But the BACKUP LED did not turn Green from Red & Error LED kept flickering on standby CPU-A. CPU-B remain in Control but backup LED turned RED. From system monitoring we found that there is a Error 6000 (FILE DIFF.) observed in One of the .QPG (program 00-MDBUS.QPG). We tried to reset it but were not successful. We are surprised that why does the program differs when it was copied from CPU-B to CPU-A using the memory copy. Still we did the VERIFY and found no difference between the programs in CPU-A & CPU-B.  Can anyone explain the cause of this issue and the solution. Please note that the CPU-B is still in control and plant is running. Backup LED on both CPU are red which means (redundancy loss) and error LED on standby CPU-A is flickering RED. There is no error in the CPU-A (Control) -we checked this using the GX Developer. Also attached here are the image of the error and error help. Thanks in advance. Battery Replacement procedure.pdf Battery Replacement procedure-Flow Chart.pdf Error.pdf MELSEC QCPU ERROR CODE 6000 FILE DIFF.pdf
  17. What Is a PLC Communication Error?

    PLC doesn't respond to communication requests or responds negatively to such requests. A PLC communication error can occur between the programmable computer and the devices it controls or when the technician attempts to program the device. If anybody have idea then share i am fresher now i learn it from CETPA INFOTECH. I think this is the best place to ask.
  18. HI everyone ,  i will be very glad if anyone helps me to clear the doubt . I am using MX component version of 4 to connect with my CCLINK J61BT11N   Board. Is there a way to read group of registers from the CC-LINK . for example, if i want to read from D0 to D5  or write D0 to D5.  is there any function  in MX component which helps to read the group of registers? I use MItshubi PLC .
  19. hello every body.  I want to upload program from  HMIGXU3500 . I have  Vijeo Designer Basic v1.0   software Is it possible to upload program from this HMI.? I want to have back up file 
  20. Sorry if this is covered elsewhere, but my search hasn't revealed anything yet.  I have a number of PanelView graphics created with FactoryTalk View ME and some use a lot of Parameter Files, which link to popup faceplates. So a large number tags are represented with parameter files, which, when clicked on screen, then pop-up an appropriate faceplate, based on tag type or category etc.  I am still digging into the very elaborate FT View ME manual, but at 500 pages, that's quite a deep study.  But I don't see the linkage between the tag's parameter file and how it specifies which faceplate to pop up, and I've not yet found a good article other than keep digging into that FT manual. There does not appear to be a linkage entry in the parameter file itself, where I would have expected it.  Nor do I see any "hot spot" click type event code in the display itself, which would also make sense.  Is it in the PLC code itself?  I would not have expected that, since they seem to be keeping the FT environment self-contained. But there must be some sort of table or linkage somewhere that I'm over looking. Thanks in advance for anyone's thoughts & guidance on this.  Other parts of FT HMI screen development does seem intuitive, just not this dynamic linking.
  21. Hi all, I'm enhancing an Ethernet IP driver but only just learning the ropes in terms of Allen-Bradley PLCs. I'm presently focussing on that part of the driver which specifically supports SLC/500 & MicroLogix 1400, for which I have one controller of each type for testing purposes. I can already cater for a range of standard file types: integer, float, binary, input, output, string, counter, timer, control, status, and this is working well. However, by working with RSLogix500, I can see that there are other data file types which can be hosted in these controller types (dependent on model) and, indeed for test purposes, I have actually created instances of them as follows: ASCII (at A21, 20 elements) for both SLC & ML1400 Long (at L22, 10 elements) for ML1400 Message (at MG23, 8 elements) for ML1400 PID (at PD24, 4 elements) for ML1400 Programmable Limit Switch (at PLS25, 3 elements) for ML1400 Routing Info (at RI26, 3 elements) for ML1400 Extended Routing Info (at RIX27, 3 elements) for ML1400 Now, the driver obviously uses standard DF1 PCCC data types (see below) to read/write individual elements/sub-elements of the file types that I can already support -- and I can see that there's a file type listed below for ASCII. •80 to 83 hex: reserved •84 hex: status •85 hex: bit •86 hex: timer •87 hex: counter •88 hex: control •89 hex: integer •8A hex: floating point •8B hex: output logical by slot •8C hex: input logical by slot •8D hex: string •8E hex: ASCII •8F hex: BCD However, my question is this: since there are no hex file types corresponding to non-elementary data types such as L, MG, PID, PLS, RI and RIX, what file type do I specify in my DF1 PCCC packets to read/write the elements/sub-elements of these six data types ? Thanks in advance.
  22. In my research on NJ processors and 1S servo programming, I came across an HMI graphic that I would like to use.  There was a file download that I think had something to do with it..."Machine.IAG"..but I don't know what an IAG file is and if it even has anything to do with an NA5 display.  Is it a Graphics file I can load into my HMI program to use?   Thanks,
  23. mitsubishi PLC R series

    I have R16 PLC (firmware45) and SD card(2GB). Can any one help me to create CSV file in SD card.I need to Logg the data of D0-100 when the M0 trigger bit goes high. can any please help to creat  ladder for this. it will be really helpful.
  24. Read/Write data to PLC

    Goodmorning a question... I builded a simple monitor of plc. I need to read the data of the Mitsubishi FX3GE PLC. In example I should read: D14  FLOAT 32bit D16  FLOAT 32bit alarms from M100 to M119 and a bit of state M450 How can I do this? The PLC is connected via ethernet and the port il 5002.  I'm working with PHP and normally use modbus, opc-ua, etc. But here? Thanks in advance Carlo
  25. Program lost after battery replace

    We think so we lost the program after a battery replace, because the program isn´t loaded on GOT. Is it possible restore it by the PLC?