Search the Community

Showing results for tags 'cj2m ns12 net(-) network number'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 157 results

  1. Hi again I browse through half a dozen mitsubishi manuals but turn up nothing for mitsubishi plc cross-communication. In this project there are about six L-06 plc:s. All are on the same ethernet network already, communicating nicely with the SCADA system. Per today information is (temporarily) exchanged via the SCADA system. Here is another hole in my knowledge. Namely how to correctly setup communication between these plc:s. I plan to continuosly exchange some 50 bytes of information. I would be grateful for some pointers and/or perhaps a reference to a manual. Cheers to all of you //
  2. Hi. Can anyone help me on how to connect to OMRON cj2m with fins or ethernet/ip protocol from windows ? Is there any vb code or javascript ? I saw an omron fins javascript  topic from patrick  but i was not able to connect with the plc.  How many steps are needed to connect ? Thank you.    
  3. CJ2M Modbus communication

    Hello everyone, in my project I have to connect CJ2M-CPU34 with CJ1W-SCU31-V1 module to external device (see technical specifications in attachment). The CJ2M should read and write a few values from the external device. Unfortunately, I dont have a chance to try this communication before, just during system start. I never make any project on Modbus. Anyone can send me a program to communicate with this device, according to documentation in attachment?   38RBS_Modbus_1.pdf Modbus_2.pdf
  4. Hello guys, I have the following distribution in a profibus network: S7-315-2 DP(--> Salida del conector)1- Free DP connector2- RS485 repeater3- Periferia ET200S4- Periferia ET200S5- Periferia ET200S6- Periferia ET200S7- Periferia ET200S8- Variador MM440 (Cabinet C)9- Periferia ET200LENDS7-315-2 DP(<-- Entrada del conector)1- Variador MM440 (Cabinet A)2- Variador MM440 (Cabinet A)3- Variador MM440 (Cabinet A)4- Variador MM440 (Cabinet A)5- Variador MM440 (Cabinet A)6- Variador MM440 (Cabinet A)7- Variador MM440 (Cabinet A)8- Variador MM440 (Cabinet A)9- Variador MM440 (Cabinet A)10- Variador MM440 (Cabinet A)11- Variador MM440 (Cabinet A)12- Variador MM440 (Cabinet A)13- Variador MM440 (Cabinet A)14- Variador MM440 (Cabinet A)15- Variador MM440 (Cabinet A)16- Variador MM440 (Cabinet A)17- Variador MM440 (Cabinet A)18- Variador MM440 (Cabinet A)19- Variador MM440 (Armario A)20- Variador MM440 (Cabinet A)21- Variador MM440 (Cabinet A)22- Variador MM440 (Cabinet A)23- Variador MM440 (Cabinet A)24- Variador MM440 (Cabinet A)25- Variador MM440 (Cabinet A)26- Variador MM440 (Cabinet A)27- Variador MM440 (Cabinet A)28- Variador MM440 (Cabinet A)29- Variador MM440 (Cabinet A)30- Variador MM440 (Cabinet A)31- Variador MM440 (Cabinet A)32- Variador MM440 (Cabinet A)33- Variador MM440 (Cabinet A)34- Variador MM440 (Cabinet A)35- Periferia ET200S36- Variador MM440 (Cabinet B)37- Variador MM440 (Cabinet B)38- Servoamplificador E94AYCPM (Cabinet B)END What would be the best way to configure the network? As you can see I have more than 32 nodes in 1 segment and the RS485 repeater is not being used properly. Hope you can help me, Regards!
  5. I'm searching for supported EtherNet/IP CIP objects documentation for CJ2M. With Wireshark, I see unknown service 0x54. Thank you!  
  6. CJ1M CPU11 how to set IP adress?

    Hello, I have to work now with a cj1m cpu11. I would like to connect it to a ns10 display. My first obvious problem is when i made the project in cx programmer, that unlike in cj2m i wasnt able to select the cpu unit in the IO table and set the ip adress. How do i need to set the ip address? im reading an omron guide, but it is confusing, and so long, i only want to set the ip address :/. Also how can i set the fins network to 2? On the cx-designer i set the network address:2 and the node adress:40. I know that the 40 means the end of ip address. Thats why i want to set the plc. How about the network address 2?  Help is much appreciated. Thanks!
  7. Omron CJ2M encoder reading

    Good day  I have a CJ2M cpu with ID211 module I have 2 E6B2-CWZ6C encoders connected to inputs 6,7,8,9 the plc data trace shows that pulses are being read, but I`m trying to configure PRV 881 instruction but it doesn`t work   please find attached the images   Best Regards   Eduardo   encoder error.pdf
  8. CJ2M i/O bus error

    Hi, my company got project using omron CJ2M but we got trouble when the output is over ch10  here the PLC hardware setup  :  1. PLC CJ2M 2. PSU PA202 2. Module Input ID211 (5 Pcs)3. Module Output OD211 (2 Pcs)4. Module Output OC211 (3 Pcs) and because addtional input and output we Change modules : 1. ID211(1pcs) -> ID231 (1pcs) 2. OD211(1pcs) -> ID231 (1pcs) after the setting and upload program , warning appear for the image its on attachment. so if i want this system to run do i need to buy expansion rack or there is another solution ? Best Regard
  9. Hello, My quest is to make a memory card, which I can just put into my PLC on the field and load all program and options etc to my plc. Now i found the official omron guide about it but its not good at all... For example is does not explain that how i need to transfer the H and D memory part to the plc, and that not all network settings are being copied if im not careful.   But my question is: is it possible to make this backup memory card without having the actual plc? Because the process is done in memory card window, which is only available if you are online. So basicly i have to get all the plc rack parts to make this work? I tried with the simulator but ofc it is not working.   Someone mentioned me that it is possible he heard from someone but no one actually knows how to. And there is nothing in the omron manual as i see.
  10. So here's the problem I'm facing. I've recently started working for a company that has two facilities. They have lots of old equipment/PLCs, plus some new stuff. We undertook a project to upgrade the network infrastructure, and replace all the old programming terminals (Some had Windows 2000!) with a new standardized programming terminal, all sharing a common image. We've installed these new computers, and they were working great. Recently, we switched all the licensing to a Hyper-V based server, using FactoryTalk Activation Manager. Right off the hop, there was issues with one of the sites (let's call it site B). Site A is working fine. When you open FactoryTalk Activation manager, it populates the activations from the server in about 1s. The wait times for opening software are pretty normal (For RSLogix 5000, "normal" isn't exactly rapid, but like I said, that's normal). For Site B, the activations take forever to refresh in Activation Manager when opened on a programming terminal. The software takes even longer to open (we're talking about 2-3 minutes). Network wise, Site B is further along than Site A. We've implemented a Stratix layer 3 switch at the top of the network and use area specific VLANs to reduce multicast noise across the network (much of the multicast noise comes from vendor equipment, not PLCs, so I can't control it). This works fine. I can remote in and use TeamViewer/VNC with acceptable performance across the network, so it's not being bogged down to unacceptable levels. However, connection to the activation server is unacceptable. I'm not sure of the culprit (yet). We are continuing network improvements, removing some older 10/100 links and installing Gigabit equipment between the Hyper-V server and the above mentioned Stratix, hopefully that might help. However, that same 10/100 link is the one I use to remote in and use Teamviewer currently, so I can't see how much improvement it will give us for activations (which really should take almost no network traffic). To get activations, I'm just adding the IP address of the Activation Server into FTActivation Manager on the programming terminals. Any ideas, people? Thanks
  11. Addressing I/O

    Hello Guys and Girls, I am new to Omron and I am just setting up a new project. I have populated my rack in the (I/O Unit And Table Setup) but how do I address the physical inputs and outputs?  I started to populate the symbols area but when the inputs I had typed in 3.0 - 3.15 (16 inputs) It wouldnt let me populate the other 16 inputs (3.16 - 3.31) of the 32 input card?  What am I doing wrong? any help will be much appreciated. Many thanks in advance. MrEngineer
  12. I have an application I am currently working on where I have a single AB ControlLogix PLC that needs to read data from 12+ Omron CJ2M PLCs.  The Omron PLCs don't need to read any data from the AB.   I have tried several things including the generic .eds file from Omron and the instructions in the document I found on this site:  Omron CJ2 to Rockwell ControlLogix Ethernet/IP Datalink.  The generic .eds file gave me a D6 error on the Omron side and after talking to support it does not seem like the correct path.   When I tried following the instructions for the datalink I ran into several issues.  The first issue was that after configuring my network in the Omron software upon trying to load it I got a unit mismatch message for the 1756-EN2T, the .eds file I have is for a 1765-EN2T but the card shows as a 1756-EN2T/D, so I am concerned that could cause an issue...that being said I can't find any .eds file specifically for the /D revision.  The next thing I noticed was that there doesn't seem to be be a way to link the produced data from the Omron to the AB, the Omron configuration software with the AB .eds files loaded only gave me the option to send data to the Omron which we do not need to do.  I created a generic Ethernet module in my RSLogix program for the Omron PLC and then created a consumed tag and linked that to the module but I do not see where I set up the link on the Omron side for that, so how does it know what addresses to read?? Any help would be greatly appreciated!!!! Thank you!
  13. Version 1.0.0

    11 downloads

    Opto22 PAC SNAP UP1 ADS read network settings using Linux or other OS using a serial port terminal app
  14. View File Opto22 SNAP UP1 ADS read network settings using Linux Opto22 PAC SNAP UP1 ADS read network settings using Linux or other OS using a serial port terminal app Submitter Absolutelyautomation Submitted 04/01/16 Category Other PLC Demo Software
  15. 502 port error

    Hi  i am trying to connect to omron plc (cj2m ) using modbus tcp/ip , by using the port 502 i  get an error saying that the port can't be reached is there any method to fix that or change the port number ?   thank you 
  16. port 502 error

    Hi  i am trying to connect to omron plc (cj2m ) from my pc  using modbus tcp/ip in c# , by using the port 502 i  get an error saying that the port can't be reached is there any method to fix that or change the port number ?   thank you 
  17. I need some help and advice communicating between an Omron PLC and a Keyence KV-5500. My system typically uses an Omron CJ2M-CPU34 which comes equipped with the built in Ethernet IP port.  My customer is insisting that we change the CPU in our system to a CJ2H-CPU66-EIP in order to communicate with the Keyence KV-5500.  They have not been able to detail why their communications require the CJ2H, they just say they will be using Ethernet TAG communication and for this they need us to change the CPU. Has anyone successfully established communicated between the Omron PLCs and the Keyence?  If so how did you do it and which CPU did you use?  Is there an .eds file available for the Keyence CPU? Please help!!! They will be visiting from halfway around the globe to test communications in January so I want to be prepared!
  18. Hi all, Quick question about adding ENET modules to a plc. If I have a local network of a HMI, PLC and 1 device all on IP 192.168.255.x and I have another device across the plant with an address of 171.27.19.x, can I add that one device to the PLC and it will recognize it? Is there a way to add a device with a totally different IP address to a PLC that is already set up?
  19. Hello, recently I tried to hook up a new CJ2M-CPU31 (built-in EIP Port) with a NS10-TV01-V2, which has an Ethernet/IP connection also. I made the simple setting as usual : 1. PLC, IP Address 192.168.250.1, Sub 255.255.255.0, FINS Node 1, no change to FINS/UDP parameter (Auto Dynamic Generation) 2. HMI, IP Address 192.168.250.2, Sub 255.255.255.0, FINS Node 2, Register the Host as EIP, SYSMAC-CJ2 mode with the PLC IP, Disables the Serial Port For some reason, there is no communication between NS and CJ2M (timeout error always occurs). I tried to re-register the Host as FINS, set the Node to 1, and also with no avail. I did try to connect the NS to a CP1L-EM with FINS Comm. and it works fine. Anything I did miss? Thanks in advance
  20. CJ2M serial communication

    Hi! I'm trying to connect Omron plc CJ2M cpu11 (photo below) with Weintek touch panel. I've made proper cable, and I'm trying to establish communication between these two devices. I've wrote a script in Weintek's program, that sends and receives via serial port, rs232. Also, I've used example for serial communication in CX-Programmer, that you can see in attached files. I'm trying only to toggle one W adress using hmi. That sounds simple, but still, I'm not able to make plc and hmi to talk with each other. What I'm doing wrong?
  21. Have looked on this forum and found NO hint of a solution. I hope someone can provide me with a starting point. I have a Allen Bradley Micro830 & Connected Component Workbench that I use to SMS text message out the value of an Analog sensor. The value is a real number data type so it holds a number like this 123.32659+e. All I want to do is to "Truncate" so that the value ends up being like this 123.32 this would then be what sms receiver would see as the value. Thanks
  22. CJ2M CPU32 SERIAL COMMUNICATION ISSUE

    Hi, I am having an issue with Omron CJ2m Cpu32 serial communication. I'm not receiving the data from pc to plc. sometimes during the production. When I recycle the power its working fine. Is there any Flag to reset the Serial port and clear the buffer on Cj2m VPU32. I contacted tech support and they told me to use A526.00n to clear the port. But I think A528.00 is not for CJ2m cpu32. I'm new to Omron programming and serial communication any reply or response would be helpful. thanks in advance.
  23. Hi. My goal is to communicate from a Wago 750-881 Controller to CJ2M With ETN21 on Modbus UDP. I can only find Modbus TCP function Blocks but would prefer UDP. Does it excist ? Cheers. WagoGrim
  24. Hello everyone, I need to modify furnace ladder diagram to take control of the upper PID limit. The temperature on the furnace is controlled using PID. There is master PLC CJ1GCPU45SP which communicates several slaves CJ1MCPU13. It looks that all the PID parameters are send from the master to slaves over DeviceNet using seven DRM21 modules installed on extension rack. I can see where the values for the PID are entered on the HMI and moved to new location in the master but I don't understand why they are not placed in memory locations used by DeviceNet by default as per DRM-21 manual ( which if I understand correctly are D30000 to D31599). Is it because the DRM21 are mounted on extension rack? I will list all the upper limit locations in master, it is a long list but hopefully will help in resolving this issue: HMI entry location Moved to location in the ladder D16401 __________________ D32023 D16403 __________________ D32047 D16405 __________________ D32071 D16407 __________________ D32095 D16409 __________________ D32323 D16411 __________________ D32347 D16413 __________________ D32371 D16415 __________________ D32395 D16417 __________________ D32623 D16419 __________________ D32647 D16421 __________________ D32671 D16423 __________________ D32695 D16425 __________________ D29923 D16427 __________________ D29947 D16428 __________________ D31723 D16429 __________________ D31756 D16430 __________________ D31757 D16431 __________________ D31758 After they are moved to the D3xxxx location they are not used anymore anywhere in the master PLC so I am assuming they are transmitted over to be used in slaves. Is my reasoning correct? How can I calculate address space used by each DRM-21 card to make sure I am understanding what is transferred where? Thank you.