Search the Community

Showing results for tags 'start and or end code not working'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 52 results

  1. Help needed with MM430

    Hi everyone, Now I used Micromaster 430 controlled by a PLC. I set parameters as follows: P0010: 0  P0100: 0 P0700: 2 (using BOP-2) P0701: 1 (start) P0702:12 Terminal 3+4: Connected to Analog output of the PLC  Terminal 5: connected to 24V via a relay which is controlled by the PLC DIP switch1 on (analog input1 with 0-20mA) When I turn on the relay to power to terminal 5, the inverter runs about 5 seconds, then stop automatically while terminal 5 is still powered. There are no fault and no alarm. I checked the parameter P0947 and P2110 with value 0. Especially, when I set P0700 = 1 (using Start button in Panel), the inverter runs well without stop automatically. Please give me some solutions.  
  2. Hello everyone, I'm currently trying to communicate  via ethernet with a Parker drive IPA15-HC. I'm using a 5069-L306ER CompactLogix 5380, revision 30.011. There are add-on instructions that allow you to control the drive, but since they're really basic I'm trying to use message instructions to get more data out of it.  The knowledge base provides a zip named IPA_AOI_Rev4, that includes the add-on instructions and the program you should download to the drive to use them, this is the current file downloaded in the drive. Now, I've tried different msg configurations: CIP Data table read, CIP Data table write, CIP Generic copying the values in the examples and I always get the same:  Error Code: 16#0001 Extended Error Code: 16#0000_0125 That extended error code is nowhere to be found, not in the Logix designer online help and not in rockwell's knowledge base. Any idea?
  3. How configure RUN

    Hi all, Working in GXWorks2 with an FX2 CPU. When i powercycle the PLC, the plc stays in STOP. With the software i can put him into RUN, also found an setting to give RUN signal by an digital input.   How can i configure the PLC to always go into RUN after power up / power cycle?        
  4. Hi All, I am pretty new at electrical design for PLC control panels. We are a UL508A shop, so this is the code I refer to most. Something struck me as odd when I was trying to size wire for this control panel. UL508A 28.3.1 says this: The required size of the field wiring terminal shall not be less than 14 AWG (2.1 mm2) and shall be determined by: a) Calculating the required ampacity per 28.3.2 – 28.3.6; and b) Determining the minimum field wiring conductor size from Table 28.1 having a corresponding ampacity that is equal to or greater than the required ampacity from (a). How can the minimum wire size be #14 AWG? We use #16 AWG for wire to the PLC modules? Are we breaking code or is there something I am missing? Also, understanding code books can be difficult. Is there a website or place I can go to get a plain English translation? I feel like I will read a sentence over and over again to try to understand what they are saying, and feel like there's is a much easier way to say it than the way it is written. For example, "28.3.1 b" ……...what is it really saying?  
  5. Fx1n 40mt dss

    I have 2 fx1n-40mt-dss plc and both wont startup when i put power on them. Any suggestions?
  6. Hi everyone - my first post here.  I have a customer with a SLC5/01.  The controller is 1747-L511.  Battery seems good.  The fault LED is flashing.   I tried to connect to it using RSlogix500 and I got this message (photo1).  I selected 'Load From EEPROM' and got this notice. (photo2) Customer has the printed ladder but I can't tell which data types are what. everything is just numbers - no B's, no I's and no O's.  the timers and counters are just numbers too. Luckily the printed ladder has a cover sheet, which led me to the PLC2.(photo3) The rack has two 8 channel inputs and 2 8 channel outputs.  I would like to replace everything with a micrologix 1400 or something, if I could translate the code. Can anyone advise on this matter please?      
  7. good day! I would like to put some ascii code in a device: D3000..D3009 has to be filled with 0x5F54 0x4F5F 0x4150 0x6F73...  ("_TO_APos")  When I fill it using an ascii-input-field in the designer and press "enter" it works. But I would like to put this text automatically in D3000 and following register, when the user press a switch-object. I tried with an 10 actions  "keycode" but I don't see how to say that the key code shouls be saved in D3000. Can somebody tell me the best way to fill more word devices with only one object switch? Thanks in advance   MEBoerner  
  8. Are there any good guide books out there that parse down the NEC to the sections relevant to controls engineering and panel building?
  9. FX-3G MODBUS

    fx 3g modbus.gxw
  10. I've been building a contraption with linear rails and stepper motors. It has an X, Y, and Z axis. I'm using Velocio PLCs to control the motors which seems to be work well so far. I understand these are not very common and my question are related to general motion control, not Velocio programming specifically. Since I'm new to PLCs, programming, and stepper motion I thought I'd ask for some input instead of trying to reinvent the wheel. I'm to the point in the build where I'll be adding emergency stop/limit switches and am wondering how to go about writing the program; if there's an "industry standard" way to go about it. I figure the PLC will check to see if any switch is active. If one is, drive the motor away from it till it's inactive and store the location. If one is not, drive the motor until a switch activates then back off a until it's inactive and store the location. Drive the motor to the other limit of the axis (the number of steps should be known) to activate the switch, back off and store location. Rinse and repeat for the other axes. Is my approach about right?
  11. What is M code in mitsubishi qd75d4?

    i have a question about M codes. what is it? using QD75D4 motion control
  12. Help Programming a Beckhoff PLC

    I have a very simple problem that I need help with.  I have some programming experience but I am brand new to PLCs and structured text.  I am using TwinCat 3 to program a Beckhoff CX9020.  My goal is to read the temperature from my thermocouple and open or close a valve based on the temperature.  I have successfully connected the PLC to the TwinCat software and I am able to see the value of the thermocouple increase and decrease when I touch it with my fingers.  I need to link that value to a variable in my code so I can have the valve act on it.  I don't know how to properly address the inputs and outputs.  Thank you!
  13. Hello! Is it possible to run a program only 1 time when i turn on the plc? In siemens it was ob 100 or soemthing like that, that program only runs one cycle at startup of plc. I want to make sure some bits are off at startup to be in safe position Thank you for your help!.
  14. Gents, i'am getting error code 8 when i try to read from another plc . Both are siemens im151-8 plc's. I hope anyone can help.   Regards, Mucho
  15. RXDU issues

    I have a data logging process on a CJ1M CPU13 via RXDU command on port 2 of SCU41-V1 It has been working, but has stopped.  There are 2 identical machines.  Both Honeywell bar code readers work on 1 machine, while the "RD2" led stays lit on one machine, and wont complete the RXDU command.  On the working machine, it simply flashes quickly during data receive.  I have compared the program in both, and it is identical. Cabling from both machines have been tested - works on one, not on the other.  Even swapped out SCU41-V1 with same results, so I am pretty certain it is a setting in the main processor of the non-working unit.  I did a compare of SCU settings and they are identical. #0 is moved into C  #2213 is moved into C +1 on first cycle.  Unit number is 3 1594.06 never seems to complete, which is an open contact in series with A202.02 (N.O.) to trigger RXDU (255) A202.02 is value 1 1594.06 stays at 0 when I trigger 1594.06 via laptop, it sends garbage data once.     Any ideas?  
  16. Error code: 4140

    Hallo. Recently ive got an error i haven't seen before. Error 4140 im using GX IEC developer  CPU is Q06UDEH I cannot figure out why the error happens.  When show the location to the step where the error occurs it makes no sense. The specific area has only got simple bool operations. When trying to recompile the entire project. The error "moved" to another location in the program. At this step there was a lot of float operations. When monitoring one of the variable value was NAN. I could not find anything about NAN in the manuals. But google stated it could mean not a number, which makes sense when reading the error description. I know it impossible to help me with my specific problem, when i cant really tell where or why the problem happens. But im pretty sure it has to do with me using float operations wrong. Ive tried to do a simple test program just to see if i could provoke the error, but no luck. How can i make a number go out of range, make it unnormal, nonnumeric or even infinite? Maybe someone could give me a simple example how to provoke this error, which might help me on my search in my own program. Thanks. Below is a screen-dump from the manual on this error.
  17. Hi guys, I recently was asked to configure a computer to host an Factory Talk SE Client application. I was able to get everything working except the trends and the Alarm window, all I have is the cross hatch screen. at the bottom of the screen it is saying cause: Trend: CAB file missing on the server: http://hmi1/RsviewActiveXControlSetup/RSTXView2ocx.CAB. I have worked on this for a while and am stumped. All the other computers on the same domain network are working fine, so it leads me to believe my problem is with my installation on the new computer. Any suggestions or if you need more input please let me know. Thanks
  18. Bit strange - I use CompoNet all the time and just had my first issue. I found Remote I/O error code 9 in the CPU but cannot find what the code means. Went through the manuals and all errors appear to be in hex. Can anyone help at all please?
  19. Greetings, I'm ok with RSLOGX 500 but am an absolute beginer with RSLOGIX 5000 and was wondering if anyone had any simple sample code just to study. I would love something using analog input and or analog output. thanks in advance.
  20. Hello! I am programming with FT view studio version 8. In the program, when I make numeric display, I can not input values for this tag I am using in the display. Then I decided to make 'invisible button' for enabling the input for this tag which is shown in the numeric display. This is okey for me, only if there is other ways to do this please tell me. Now when I have created this numeric display with input enabling -'group', I have a problem, how can I use security levels for this group, so that only logging in values can be set? I have found that there is security code selection for this in the screen displays, but not for the buttons.
  21. Good day, I´m helping with small project and currently i am stuck because of this problem. And I hope you can help me out. I´m using PowerFlex 525 connected with AB CompactLogix 1769-33ER PLC via EtherNet/IP. Connection is working, I can read and write values from/to 525. To configure both devices i´m using RSLogix 5000. 1) First problem occurs after I loaded configuration to 525 and it´s, that 525 keeps overwriting values of Accel and Decel Time 1. It happens when i directly change parameters in Module Properties (online) or after I upload configuration to device. It happens even if i set parameters directly to 525 with its HMI panel. - I kinda get around this problem when i use Accel/Decel Time 2 for Step logic, but if i send direct reference value motor still jump to it and that is not good, especially when changing direction of rotation. 2) Second problem is that I cant get Speed Sources and Start References right. Usually Is working only option 1 and others are not, or they are doing something else that they should. For better imagination this is what i want to do: I have 3-state switch (left = 1 ON(DigIn TrmBlk 02), 2 OFF; center = 1 OFF, 2 OFF; right = 1 OFF, 2 ON(DigIn TrmBlk 03)), In center position I want to control 525 with EtherNet (already working when: Start 1 AND Speed 1 = EtherNet/IP). In left position I want to control motor directly with Drive Pot and In left position a want to start Step Logic (which i have already set) - Funny thing, If I set Start 1 = Ethernet, Speed 1 = Step, Start 2,3 = DigIn, Speed 2,3 = Drive Pot then in all three position motor goes in Step logic.. Or when i get left and right position working then Ethernet is blocked.. and this kind of things.. I Attach print-screen of my current settings, if you need something more just, tell me. Thank you for your time, and I hope someone will be able to help me.
  22. I am very new to PLC's, I work in a power plant and we have an ABB DCS. We have some vendors that use PLC's and they try to make them work with our system. Currently I am working on a project were I am trying to add 8 analog outputs to the PLC. I am working with two 1756-L71 controllers (redundant) and the rev for the program that was written 20.01. Basically I have 8 analog inputs that I want to bring to the spare analog outputs that I have. I want to see these inputs in our DCS. I wrote simple logic that at the end of the rung has a move block moving the source which is the input and taking it to the destination which I made an alias tag for the output channel that would correspond. Problem is I can see the source number moving, but the destination number stays at 0. I can type a number into the destination and it will work. I can see my 4-20 signal I am sending out in the DCS. Everything before the move function is true, I have and open contact, and a closed contact and they both are green. This is happening on all eight of my outputs that I am working on. Please help I have learned a lot from this experience but I cannot figure out what has me stuck this time.
  23. Hi all and nice to meet you here! I hope that someone with experience helps me and I hope in future to offer also my help to someone. I am having problem with a Mitsubishi plc with A2N (S1) cpu installed on a machinery. The machinery stayed 20 days switched off and with battery empty as I realised when switched on and the problems come out. I changed the battery but the problem didnt resolved. The plc gave error with stable error led and flashing run led on the cpu. Also an error led stable on a (double role) module of printer and ram. I have to say that I have never used GX developer environment before and it is my first contact with Mitsubishi plcs. Reading some manuals (found on the internet) and by using GX developer I read from plc the faults. Register D9008 was set at 12 error meaning MISSING END INS. I Followed the described flow charts from a2n manual for reseting faults but the situation was the same always as described above. I tried to read the program from plc and succeded to read it. It is a lader with about 6000 lines. Anyway I have no previous experience of the GX development environment but I tried to put the missing END in the program as sugested also by the flow chart in the manual. At this point I have to say that it was automatically added from gx developer as I can remeber from an appeared message. I verified also many times the program on gx developer with the plc and the only difference was that missing END at the last line of ladder program. Anyway I tried to write back to plc the program with correct end but it was not possible. I tried several times. The error mesages took with Gx developer was the following : "THE SAME T/C COIL EXISTS IN PROGRAM (MAIN) AND/OR PROGRAM (MAIN-SFC). THE VALUES ARE SET TO BE THE SAME AS IN THE FIRST FOUND T/C COILFROM THE TOP OF PROGRAM" "THERE IS A DEVICE IN THE PROGRAM (MAIN) THAT IS OUTSIDE OF THE RANGE. CHECK THE PROGRAM AND CORRECT THE DEVICE THAT IS OUTSIDE THE RANGE." Anyway I decided to delete the plc memory. After that the run was stop blinking and the error led went off. Only the error on the printer-ram module was on (This module was changed with a know functioning one witout any variation on behaviour). I thought that problem has gone now that the cpu is empty. I tried again to write the program to the plc but again i take the above mentioned messages. Now I have an empty plc and a program on the Gx developer that cannot be written to plc!!!!!!!!!!!!!!!!!!!!!!!!! I am desperate!!! I do not know how to proceed. I am not knowing the mitsubishi development environment. Other than Gx developer I tried to install the GX simulation but it not works to my computer. At this point I dont know even if the ladder program is somehow corrupted after the described above messages. I can sent the code (GX developer project) and any other information to someone expert, if necessary, to have an opinion. Please help!!! Let me know how to proceed!! I have to write back the code to plc !!!!! Thank you all in advance!! Now i realised that there is SFC that is my problem. Could someone help please? Big part of ladder is in yellow color. How can i proceed?
  24. Hi everybody I'm new here. Can someone please help me? I have a normal single phase traffic light that works fine but, i need it to start and stop with only one input? Any ideas?