Search the Community

Showing results for tags 'factorytalk - studio5000 - communication - version'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 285 results

  1. I have a button on my HMI that I only want visible under two conditions. One of them is a numerical value and the other is if a bit is on. English translation If Variable 1 = 0 OR BooleanBit is TRUE, then show the button I tried entering the expression in the button's Visibility parameter in Animation as such: {[Program]Variable} = 0 OR {[Program]} However, it does not work on both conditions. It will work if I just use one of them but not as shown above, even if the order is reversed. There must be a trick of how to write an expression that uses multiple values...... any suggestions?
  2. I have a problem when trying to download a program from a FX1S-30MT PLC. I am using a SC-09 USB cable. The software i am using is GX Developer 8. When trying to download the MAIN program the screen in the attachment appears. I tested the download from another PLC of same model and have no problems, therefore the cable is ok, and the laptop is ok. When downloading of the parameters and comments does not give error, just when trying to download MAIN. Also I tested connection with Test Connection button and says communication is ok. Anyone who can help? I have a doubt, how can i see the communication parameters on the PLC side? Thanks a lot
  3. Using its internal Ethernet ports, our 1769-L36ERM processor communicates with 15 other devices inside the same machine. Can a rack mounted Ethernet module be installed to allow communication to/from this processor and an external network containing a SCADA system and RSLogix 5000 workstations? We prefer not to add all 16 devices to our external network and our I/S department does not allow routing devices on the network that they did not install.
  4. Hello I'm looking for a way to setup communication between a PC and a PLC. The PLC is an Allen Bradley compactlogix L30ER i would like to use the existing network which is a Ethernet setup. I've read and tried some OPC/DDE sample project with Excel and I'm wondering if there is a better way to do it. Thanks!
  5. I have a FactoryTalk 8 application that exhibits some weird symptoms when I run it. I have buttons whose "visible" state and "enabled" state are based on HMI tags. The states of these buttons don't update. I have screens that fail to close when the "abort" command is issued. I have vba that connects to a tag group, which fails to retrieve the value and produces an error. Some tag values from the PLC (always direct-addressed, I think) show up correctly, even when other symptoms above are happening. These issues randomly go away sometimes after a restart and the entire application runs fine. Does anybody have a clue what could be doing this? (Using Windows 7 Professional 6.1.7601 Service Pack 1 Build 7601, SE version 8.10.00 (CPR 9 SR 7.4), Internet Explorer 11.0.9600.17633)
  6. connecting ixt4a to a cj1m/cp1l/ns network

    hi everybody i have a network with 2 pieces cj1m and 2 pieces cp1l communicating with a ns15 monitor. everything is fine. i need to connect an ixt4a monitor in that network. my question is : do i have to make new routing tables or it is not neccessary? my routing table for cj1m and cp1l cpus are attached. if then i have to make new routing table so that the cj1m will be able to communicate ixt4a monitor, how am i going to do it for both monitors? Any help will be mostly valuable and appreciated. thanks
  7. CJ1M communication protocol

    Hello, I am not familiar with the Omron PLC's. A PC is connected to the peripheral port of an CJ1M CPU12 PLC. The write command the PC is transmitting to the PLC looks like this (ASCII): "@00WD0070010055*." Can you tell me what kind of communication protocol it is using? It is a public or proprietary protocol? Thank you!
  8. Hello I am having a difficult time with opening FactortyTalk Studio. It was working fine yesterday, but when I tried to open it today. I got an error and it says " SQL Server 2008 Express Instance 'FTVIEWx64TagDB' which is required for FactoryTalk View v6.1 or later cannot be found' Unfortunately, I do not have a contract with Allen-Bradley so I can not get help from them I have attached the error too. Can anyone help me out with this issue? Thanks for reading. Have a good day :)
  9. Hi all, I have built trend for a pressure transducer. It is working fine when the trend is open. However, When I go to different pages and come back to the trend, It loses all the data it was showing before. The HMI is panelview plus 700. What is this path?? Can anyone help me with this Any help would be great. Thanks
  10. Hello, I am trying to communicate with MicroLogix 1100 from CompactLogix. But I keep getting an error and It says connection failure. This is what I have done so far. Can anyone tell me what I am missing? Regards,
  11. Hello everyone, I need to modify furnace ladder diagram to take control of the upper PID limit. The temperature on the furnace is controlled using PID. There is master PLC CJ1GCPU45SP which communicates several slaves CJ1MCPU13. It looks that all the PID parameters are send from the master to slaves over DeviceNet using seven DRM21 modules installed on extension rack. I can see where the values for the PID are entered on the HMI and moved to new location in the master but I don't understand why they are not placed in memory locations used by DeviceNet by default as per DRM-21 manual ( which if I understand correctly are D30000 to D31599). Is it because the DRM21 are mounted on extension rack? I will list all the upper limit locations in master, it is a long list but hopefully will help in resolving this issue: HMI entry location Moved to location in the ladder D16401 __________________ D32023 D16403 __________________ D32047 D16405 __________________ D32071 D16407 __________________ D32095 D16409 __________________ D32323 D16411 __________________ D32347 D16413 __________________ D32371 D16415 __________________ D32395 D16417 __________________ D32623 D16419 __________________ D32647 D16421 __________________ D32671 D16423 __________________ D32695 D16425 __________________ D29923 D16427 __________________ D29947 D16428 __________________ D31723 D16429 __________________ D31756 D16430 __________________ D31757 D16431 __________________ D31758 After they are moved to the D3xxxx location they are not used anymore anywhere in the master PLC so I am assuming they are transmitted over to be used in slaves. Is my reasoning correct? How can I calculate address space used by each DRM-21 card to make sure I am understanding what is transferred where? Thank you.
  12. Good Morning guys, I've been working on the last months in a complex project in Pharmochemical Industry, in this project the customers will need run FactoryTalk SE Client in a Data Collector(Motorola MC3190 with Windows CE and resolution 320x320), so because FT doesn't run in 3rd party Microsoft Windows CE devices/platforms, i will use Remote Desktop Connection from Windows to acess FT in a PC. Until here i didn't have problem, i created one script that detect the resolution of screen and open graphics developed in 320x320. And here comes the problem: FactoryTalk use one ActiveX developed by Rockwell to make Digital Signature, and this pop-up is too big for the resolution of Data Collector(320x320). I couldn't find a way to resize it.... I attached a picture from screen of MC3190. Anyone knows one way to resize the pop-up? If not's possible, have a way to send as a parameter the information to Digital Signature function? Thanks.
  13. This is my company's first time using a Mitsubishi PLC and our partners/clients advised us against using the built-in Ethernet port on the Q03UDE CPU, saying that we should instead use a standalone QJ71E71 Ethernet module. The QJ71E71 costs 1.5x the CPU module so there are significant savings in using the built-in Ethernet. They cited reliability issues but can anyone here back up their claim? We use our PLCs as simple I/O blocks - a PC runs a program which communicates with the PLC and tells it what outputs to fire. There is no actual ladder logic on the PLC. The PC connects directly to the PLC. I wrote a small C# utility that blasts the QX40 and QY80 input/output cards on my stack with random values and reads them back to ensure correct data transfer. The QJ71E71 Ethernet module averages 10 ms for a read or write operation and the Q03UDE averages 3 or 4 ms (much quicker!). So, does anyone have a reason to use the QJ71E71 port instead of the CPU? Thanks
  14. Hi all, So this is more of a theory / how would you attack this problem, question: I'm creating my first HMI and while playing around in FactoryTalk View Studio I noticed I can add objects to a screen. I can add a browser and with some work I can get it to display an HMTL file directly in the screen. So the browser in this case is opening a file stored locally, not something served up from the internet. Which opens up the question, could I write most of my HMI in HTML and Javascript? As a previous developer having the ability to control more of the UI would be amazing and perhaps easier to use/maintain. The only pitfall that I haven't been able to figure out is how to get real time values from the PLC. I'd welcome anyone's input on the idea in general or if someone knows a good method for getting/setting values from the PLC. Thanks!
  15. Hello, I have an annoying problem with communication between Siemens S7 PLC and HMI panel. Here it how it looks like: I am using Siemens S7-315 with 343 Lean ethernet port. This port is used to communication with HMI terminal. Communication is realized through S7-TCP communication protocol. When I was testing the communication in the office everything worked fine and nothing wrong happened. The problem occururs only on the installation. After turning the PLC and HMI on everyting works fine, data is transferred correctly and variables are displyed on HMI. After a few hours the communication is suddenly lost. This is a direct connection between PLC and HMI and there are no other devices in this network. So it is not possible that suddenly there is an address confilct. I made a wireshark analysis (I connected a notebook and hub into the network) and I found out that when the communication is lost HMI terminal is trying to get data from the PLC but it is not responding. It looks like PLC ethernet port is broken. You cannot ping PLC from notebook and HMI. On the other hand you can exchange pings between HMI and notebook. The communication is back again only if you'll restart the PLC. The strangest thing is that I did not have any problem with the communication when I was testing it in the office. The configuration and project of PLC and HMI is excactly the same. The only difference is that on the installation PLC is realizing also a communication throguh Profibus and MPI. I've tried to use different ethernet cables (crossed, non-crossed) but in all cases the situation is the same. Do you know waht can be the cause of such behavoiur? Maybe someone had a similar situaion? In the attachment I send a screenshot from Wireshark which shows the moment when the communication breaks.
  16. Good morning, I'm having an odd issue with CX Programmer and have hit a wall. I'm trying to upload a previous version of a program to an existing PLC (CS1G-H CPU42) and I keep getting the following error when I compile while online: "The read protection properties which are not supported by the connecting target PLC are set. Check the unit version of the PLC." This prevents the program from being uploaded. I have a first revision CS1, manufacture in 2005 from what I can tell. This exact program has been uploaded previously, but a modified version replaced it recently and I need to go back to the older version. Things I have tried so far. without success: - Removed UM Protection - Made sure Task protection is off for all tasks - Check DIP Switch #1, which is write protection, and made sure it is off - Used "Remove Password" and "Release access" functions from the PLC/Protection menu - Used the auto-verification to confirm the configured PLC is correct - Reuploaded a full backup of H & D memory, from the older program I am able to compile the program when offline, but it chokes when online. I am connecting to the PLC via a serial cable. I haven't found any help from the CX Programmer help, or the CS1 programming and operation manual. This error message is nowhere to be found. Anyone has a clue ? I'm at a loss right now. Thank you !
  17. Control G120C via Profibus

    I'm trying to control the speed of a G120C via profibus, but it will trip out when any changes are done to the speed value. The unit was commissioned by another guy, and he doesn't have a clue where to look. We can start and stop the unit, but it will stop at any attempt to change the speed. I was told to look for a parameter allowing it to be controlled remotely, but wich one is it ? As usual when it comes to Siemens, the manual sucks. I'm using a function block for controlling the drives (13), and the older 12 is responding correctly to any change. Anyone here that has a clue what parameter to change ?
  18. Hi, i tried everything i know and what i saw in all forums possible, and i can't resolve that problem. So i came here hoping have anyone can make this "miracle" rsrs This is the problem... Have one application operating with FactoryTalk SE 5.00.00 (CPR 9) in plant made by other enterprise and we will insert a new area on system. So we backup the application coppying this 3 itens: - The file: C:\Documents and Settings\All Users\ApplicationData\Rockwell\RNAServer\Global\Application.RNAD - And the folders: C:\Documents and Settings\All Users\ApplicationData\Rockwell\RNAServer\Global\RnaStore\Application C:\Documents and Settings\All Users\Documents\RSView Enterprise\SE\HMI Projects\Application After i create a VM with Windows XP Professional and same name of existent server, install FactoryTalk SE and replace the file and folders in respectives locals. So i open FT and all most of things restored, but the graphics didn't. I tried add them manually, It appears that is loading, but in the end, no screen was added. Sorry for my english errors... I hope someone can help me.
  19. Hi I have a scenario where I need to setup communication between a Mitsubishi L-series PLC to Schneider Modicon M580. I need to use the onboard ethernet port of the L-series PLC. The protocol I need to use, is Ethernet IP. (socket communication). Can someone please assist?
  20. hi Guys .Tutorial Mr PLC is a Channel in YouTube for many tutorials you will see in this channel tutorials for WinCC Flexible Wincc RUNTIME PROFESSIONAL Wincc RUNTIME Advanced Step 7 SIMATIC MANAGER S7 Communication Profibus MPI ETHERNET ProfiNET TIA Portal this is the demo if you are interesting http://youtu.be/EaSU_HzXGhw my twitter @https://twitter.com/PlcTutorial and please share it
  21. Hi Good Day, I need a suggestion, I have an omron encoder, encoder counter meter (K3NC-NB1A) and communication card RS-232C 25pins (K31-FLK1). My question is, what is the best omron software to read and manipulate the data from the encoder (I have CX-one software but I only use CX-programmer). I want to capture the encoder pulse and convert to velocity, acceleration, deceleration and also energy absorbtion. I have to use mathematical formula such as two times differentiation. I also need to show grapf and display final result that is energy absorbtion reading. Or is it much simple if I use VB / labview / java software? Thank you in advance
  22. Connect OMRON CJ1H to GSM modem

    Hello guys, actually I am new to this Omron PLC. but i have small project to transmit a command to the GSM modem via the RS232 port so it can trigger the modem to send text msg. Can you show me the steps/guide/sample program to accomplish this program coding? I already read some topic in this forum regarding to this PLC RS232 port but still cant get the ideas when to create the ladder program. PLC Type : CJ1H (CPU65H) - RS232 port First input to trigger the GSM send text msg: AT+CMGS="+YOUR HP NUMBER" Second input to trigger GSM send text msg: YOUR TEXT MSG CONTAINS (Ctrl+z to send) Many Thanks, AlexB
  23. Hi. I have a ST-Lite Ethernet base (STL-ETH1) with 1 16 bit digital in card, 3 digital out cards, 2 analog in and 2 analog out cards. I have a Q03UDE CPU (Q PLC) with 1 16bit digital in and 1 digital out card. Now I like to setup the remote I/O (STL-ETH1) mapped to the Q PLC via the ethernet port on the CPU. Is it possible not to use Modbus at all. I don't want to go and buy a Modbus Ethernet card now. Have someone done this before?
  24. Dear Guys, Need help again~~ New to AB software, my client have a HMI server, which is running factorytalk view se and have no client PC. what I want to do is just printing a simple page or text file to printer every 7am. Therefore I created an event to trigger PrintDisplay command every 7am. The event working fine, just that the PrintDisplay command is not allow from server. The error message: "The command 'PrintDisplay' is ignored when issued from the development enviroment or an HMI Server" Any method/idea to overcome this issue? To print out a simple page or even text file automatically in factorytalk view cannot be hard right? many many many thanks in advance
  25. I have 4 Allen Bradley PLCs which are 3 SLCs and 1 CLX This PLCs need to send data to Yokogawa Centum VP DCS. Instead of having and individual Modbus link to DCS, I'm planning to link all 4 PLCs by using Ethernet/IP and plan to buy 1 extra mini PLC which is Micrologix 1400 to become an interface PLC between the 4 PLCs and the DCS. Since the Micrologix 1400 has embedded with an Ethernet port (Ethernet/IP) and Rs485 port for Modbus RTU, the Micrologix 1400 interface PLC will communicate with DCS using Modbus RTU Protocol. Meaning to say, the 4 PLCS will send data to the Yokogawa DCS via interface PLC. The Interface PLC will become translator to translate from Ethernet/IP language to Modbus RTU language. My question to Expert: 1. Is this setup can works? 2. How to send data inter-PLC by using Ethernet /ip ? Is it just need to grab the tagname or there is an address for that? 3.Is Micrologix is capable to communicate with 4 PLCs using Ethernet/IP? Or just only 1 PLC? See the attached photo. Thanks. -Nizam-