Search the Community

Showing results for tags 'cycle time as data'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 159 results

  1. I have an application I am currently working on where I have a single AB ControlLogix PLC that needs to read data from 12+ Omron CJ2M PLCs.  The Omron PLCs don't need to read any data from the AB.   I have tried several things including the generic .eds file from Omron and the instructions in the document I found on this site:  Omron CJ2 to Rockwell ControlLogix Ethernet/IP Datalink.  The generic .eds file gave me a D6 error on the Omron side and after talking to support it does not seem like the correct path.   When I tried following the instructions for the datalink I ran into several issues.  The first issue was that after configuring my network in the Omron software upon trying to load it I got a unit mismatch message for the 1756-EN2T, the .eds file I have is for a 1765-EN2T but the card shows as a 1756-EN2T/D, so I am concerned that could cause an issue...that being said I can't find any .eds file specifically for the /D revision.  The next thing I noticed was that there doesn't seem to be be a way to link the produced data from the Omron to the AB, the Omron configuration software with the AB .eds files loaded only gave me the option to send data to the Omron which we do not need to do.  I created a generic Ethernet module in my RSLogix program for the Omron PLC and then created a consumed tag and linked that to the module but I do not see where I set up the link on the Omron side for that, so how does it know what addresses to read?? Any help would be greatly appreciated!!!! Thank you!
  2. IFIX Scada communication issues

    I am new to ifix, I am having an issue, I am unable to receive any information, after attempting to fix the fact that the view was only pulling half the data I lost it all, I had a back up saved, but it didn't work on restoring communication, I was getting a cannot connect to node error, but I have fixed that, now all I am getting is question marks. essentially I believe that I have two standalone computers with the ifix software and the communicate directly with various plcs that share information across, either a ring topology or full connected. so the computer I have that is working is setup with scada and the database and MB1 with no network support, the one that is not working is set up the same, my cable connection is a usb to Ethernet and im communicating with a Comm port on the computer. I've tried different comm ports, even contacted GE, they were suppose to have someone call me back but no one has yet. Can anyone give me an idea of what I've got wrong here?
  3. HOSTLINK Problem

     I  am doing  a data collection from  OMRON PLC CP1L through MS excel VBA  use API function. The connection was setuped correct (I think)both in PLC and PC side. The trick things is   when PLC have USB cable connected  the data  was send to PLC and can get feedback through RS232 in normal.(I use portmon moniter the progress,and I can see the data (C-command ).But when I get the USB cable removed  ,The PLC can not get any reponse back.Dose any of you have met that  before?
  4. PAROCK1 for HMI/SCADA View File Now a software solution is available for your Modbus (MB) needs in Rockwell/Allen-Bradley Control Logix or Compact Logix (Clgx) family processors, instead of a traditional 3rd party hardware like Prosoft MVI-56, Molex SST-SR4-CLX-RLL etc.  It is an Add-on instruction (AOI) for PLC/PAC firmware v16 or later, (other solutions are available for pre v16 systems).  For hardware interface, use PLC’s channel 0 (serial) or TCP/IP Interface module(s) to have as many MB TCP/IP devices or serial devices.  (Some limits apply based on system configurations, Comm. settings depending on HW used.) Connect any MB Client/Master or Server/Slave device(s) to your CLgx PLC, including flow computers, analyzers, VFDs, Power Monitors, Level gauges, Smart I/O, etc.  All the MB public/native function codes are supported.  32-Bit integers/floats as single entity are supported with byte and word level swapping. A separate utility automates the data mapping to your PLC logic.  Features -Serial Master (BASIC required Option); TCP; Slave; Redundancy; More than 5000 accumulative registers; MB CFC (Custom/Private Function Code) Support; Data mapping too – Between PAROCK1 & your PLC logic; Packaged with Rockwell; TCP/IP Interface Module; Volume Discounts; Annual Support Requirements -Rockwell/AB-CLgx processor with v16 or later.  Contact PCI for earlier versions. -If using CPU’s Chan0, you cannot use Chan0 for any other user mode activity. You can use it for non-user mode activities -TCP/IP Interface Modules from Rockwell/AB supported, are: -1756-EN2xx ControlLogix® Ethernet/IP communication modules, firmware revision 5.007 or later -1756-EWEB ControlLogix Ethernet/IP web server module, firmware revision 4.006 or later -1768-EWEB CompactLogix Ethernet/IP web server module, firmware revision 1.002 or later -1769-L30ER, 1769-L30ERM, 1769-L30ER-NSE, 1769-L33ER, 1769-L33ERM, and 1769-L36ERM CompactLogix controllers, firmware revision 20.011 or later -1769-L24ER-QB1B, 1769-L24ER-QBFC1B, 1769-L27ERM-QBFC1B CompactLogix controllers, firmware revision 20.011 or later -1769-L16ER, 1769-L18ER, 1769-L18ERM CompactLogix controllers, firmware revision 20.011 or later Other Related Services/Items -Custom PLC Add-on instructions building -PLC upgrades, troubleshooting, applications -PC Windows, iOS5, Linux, Mobile devices Comm. Drivers -Custom development, Technology Transfer Services  -Other Non-AB communication drivers for serial or TCP  -Full control system integration, training, architecture design This driver can be conviniently used with Visual Studio in development of complete large scale complex HMI/SCADA Systems. It can be used to perform advanced reporting MES, analytics, IoT, Big data type apps. One example is available to download here For More Info Overview of Parijat Drivers: Click here  Additional supporting Info about Parijat Drivers:Click here Complete Related Driver options: Click here     Submitter Scadadoctor Submitted 03/10/16 Category Other PLC Demo Software
  5. Excel Add-in for Modbus/TCP Data Logging

    Version 3.11.2.0

    422 downloads

    ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2021 (version 16) spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Modbus/TCP and Modbus RTU/ASCII communications. No OPC, DDE, external drivers, or programming required
  6. View File Excel Add-in for Modbus/TCP Data Logging 3.6.8 ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2016 spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Modbus/TCP and Modbus RTU/ASCII communications. No OPC, DDE, external drivers, or programming required Submitter Automated Solutions Submitted 03/01/16 Category Demo Software
  7. Version 3.11.2.0

    84 downloads

    ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2021 spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for GE / Emerson PACSystems (RXi, RX3i, RX7i), Series 90 (90-30), and VersaMax communications. No OPC, DDE, external drivers, or programming required.
  8. Excel Add-in for Allen-Bradley Data Logging

    Version 3.11.2.0

    518 downloads

    ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2021 (version 16) spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Allen-Bradley ControlLogix, CompactLogix, MicroLogix, Micro800, PLC5, and SLC500 communications. No OPC, DDE, external drivers, or programming required.  
  9. View File Excel Add-in for Allen-Bradley Data Logging ASComm Excel Add-in is a simple to use, non-programmatic way to populate Excel 2007 - 2016 spreadsheets with data from PLCs, instrumentation, and other process hardware. ASComm Excel Add-in uses built-in drivers for Allen-Bradley ControlLogix, CompactLogix, MicroLogix, Micro800, PLC5, and SLC500 communications. No OPC, DDE, external drivers, or programming required.   Submitter Automated Solutions Submitted 03/01/16 Category Demo Software
  10. Hi, I work as an industrial programmer primarily dealing with Allen Bradley, Mitsubishi, and Omron PLC's as well as various peripheral devices. I would like to begin the process of learning computer programming as it pertains to the manufacturing industry. I'd like to learn how to write databases (SQL, etc) and VB apps and eventually I'd like to be able to write applications that can communicate with PLC's and other devices (although the last one would be a ways down the road).  I have very little experience with computer programming so I don't really know where to start. What language should I learn first? What free software is available to learn with? What resources do you recommend I use? I've downloaded Visual Basic Express and found some introductory courses online that I've just started but if there is something else I should've started with I'm open to suggestions. Thanks
  11. Product:             STEP7 Professional V13 Reference:           FB Declaration Static: Data type TON is not allowed here Description: ++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++ Hi, I'm using Step7 Prof V13 SP1 upd7 & WinCC Adv V13 SP1 upd7.    In my project I'm using a 312CPU, Article No.: 6ES7 312-1AE14-0AB0, Version: V3.3 & TP1500 Comfort, Article No.:6AV2 124-0QC02-0AX0, Version:13.0.1.0   My Issue: I've taken previously used FB from my Global library and inserted it into my new Project. In this FB I've declared an IEC Timer (TON) in the static section of the FB. When I go to upload to the PLC after TIA carries out the compilation I get error message 'Data type TON is not allowed here'. I've tried creating a new FB to test and had same issue for CTU,CTD,TOF.   See attached pics This is really strange as it has always functioned before! Has anyone seen or heard of this issue before? I'd appreciate any help, Cheers.
  12. Hello all, I was asked to check if there is a PID real - time software which automatically calculates PID loops parameters and update the PLC registers or HMI ( by OPC server etc.) when the process is working and "breathing". REAL-TIME. Not PID simulator or PID tuner based on measured data, but a software that will calculate and update the PID parameters in real time while maintaning several PID loops simultaneously. Are there any suggestions? Thank you, Olesia
  13.   Dear, I need some help with an application in ml1500 with the RTC . I need an exit is enabled by days of the week . I´m programming in Rslogix500. Program follows the image. If possible help me. Thanks Daniel.
  14. thesis project

    Hello, For my thesis i'm using a beckhoff cx9020,a sunnyboy and a sunnyisland with rs485 communication protocol sma net. One of the things I need to do is to log everything from the sunny devices realtime. and here is where my problem starts. I am using rs485 to communicate with the devices via plc but I don't find any documention for what i need to request or send to get usefull data. does anyone here have an idea? Yours truly Jonas Vanhulle
  15. Data Historian Speed

    I was just curious on which type of data historians are considered fast at retrieving historical data.  For example, if I wanted to trend a tag at a one second interval to review an event that took place a year ago and compare that to the same tag in real-time, what historian does this the fastest?
  16. Can anyone advise if there are data structure #s associated with each of the data types in Logix?  Example if it is a Bool, I believe Logix advises it is a 32 bit number.  But is there an "under the hood" data type reference number for each Logix data type?  I.E.  if it is a Bool, that is a RA data type #1, if it is a DINT, it is a RA data type #2, etc.  
  17. Hey all, I've reviewed a number of threads regarding converting one data type to another and I have something I'm working on that I'm stumped on and haven't found an answer for yet. Without getting into the details, I need to get a DINT bit value from an entered decimal value. A user will enter in a whole number in an entry box and then it needs to get converted to the number of whatever bits that the DINT number holds. For instance: # Entered Variable Bit Value -----0------------------0 -----1------------------1 -----2------------------3 -----3------------------7 -----4-----------------15 etc... I'm looking for a fairly clean way to do this, with perhaps just two or three instruction blocks to handle it, if possible. I can provide a screenshot of the HMI and the logic (4 rungs) if necessary. Any suggestions or advice from the group would be greatly appreciated!
  18. I'm trying to use CX-Server to pull data from my Omron CJ2H PLC directly into Excel. I'm able to pull a single element into excel, but when I try to pull more than one element, I get a huge strand of numbers. Is there a way that I can set up a single point in DDE Manager that'll hold all the elements that I need, then in excel have a formula that will pull out specific memory elements. Specifically I'm trying to pull data from D7200-D7399, and put each element into a separate cell it in a chart that ranges from B3-K22 This is what the formula looks like when I copy a point into excel =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1' I didnt know if I could put something at the end of each string to call out specific elements, but I keep getting "#BadPoint" =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7200' =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7201' ... =CDMDDE|'C:\Users\... ....cdm'!'\New Point 1'!'D7399' Any help would be great
  19. Good day, I´m helping with small project and currently i am stuck because of this problem. And I hope you can help me out. I´m using PowerFlex 525 connected with AB CompactLogix 1769-33ER PLC via EtherNet/IP. Connection is working, I can read and write values from/to 525. To configure both devices i´m using RSLogix 5000. 1) First problem occurs after I loaded configuration to 525 and it´s, that 525 keeps overwriting values of Accel and Decel Time 1. It happens when i directly change parameters in Module Properties (online) or after I upload configuration to device. It happens even if i set parameters directly to 525 with its HMI panel. - I kinda get around this problem when i use Accel/Decel Time 2 for Step logic, but if i send direct reference value motor still jump to it and that is not good, especially when changing direction of rotation. 2) Second problem is that I cant get Speed Sources and Start References right. Usually Is working only option 1 and others are not, or they are doing something else that they should. For better imagination this is what i want to do: I have 3-state switch (left = 1 ON(DigIn TrmBlk 02), 2 OFF; center = 1 OFF, 2 OFF; right = 1 OFF, 2 ON(DigIn TrmBlk 03)), In center position I want to control 525 with EtherNet (already working when: Start 1 AND Speed 1 = EtherNet/IP). In left position I want to control motor directly with Drive Pot and In left position a want to start Step Logic (which i have already set) - Funny thing, If I set Start 1 = Ethernet, Speed 1 = Step, Start 2,3 = DigIn, Speed 2,3 = Drive Pot then in all three position motor goes in Step logic.. Or when i get left and right position working then Ethernet is blocked.. and this kind of things.. I Attach print-screen of my current settings, if you need something more just, tell me. Thank you for your time, and I hope someone will be able to help me.
  20. Hi friends, I am a little new to WinCC. I am using a WinCC RT Advanced license within TIA portal v13.1 I need a little help in my current project as described below. I am attempting to create a faceplate of a solenoid valve,, The "Valve" is a user-defined data-type with the following 4 elements 1. Cmd - or command. - Bool 2. Cls_Fb - or Closed -Feedback -Bool. 3. Aut - or Automatic Mode -Bool 4. FTC - Fails to close -Bool. I tried the following procedure as described in TIA portal help.. Method -1 1. I created a User-defined data type called Valve comprising of the above 4 bool elements. 2. In the graphics I made a image of solenod valve with one rectangle (solenoid) and one polygon for valve body. 3. Under the Faceplate Properties (See figure attached) I inserted a property ang gave it the data-type Valve as above. However, when I drag a property from the 'Contained objects list' to the interface side, it is not getting substituted. such as the Rectangle_1 's background color I try to associate with the interface property Valve.Cmd. It does not get assigned when dragged. Since this does not work I tried another approach, Method -2 I attempted to declare a variable tag of UDT type 'valve' in the faceplate's tab Tags. I found that it is not possible to declare a local variable of User-defined types here. Please guide me how to proceed. Thanks for looking in and best wishes for your success. Regards, Raj S. Iyer
  21. Hi friends, Can anybody tell me when to use a local-Static variable and when to use a Local Temp variable whilst creating a Function-Block in S7 -1500 using TIA portal. Thanks for looking in. Best wishes.
  22. Hey All, I am trying to do some data storing on a PanelView+ and the built in data logging doesn't quite fit my needs. I was looking into the possibility of creating my own ActiveX control for doing this. Is it possible to create custom ActiveX controls for Factory Talk? If so, are there any tutorials for doing so you recommend? Also, are there any sites that have custom ActiveX controls to download? I realize this may not be the easiest thing to do, but if I could create my own I could use it for various machines and would make things a lot simpler in the long run. Thanks
  23. At work we have been having a slightly increasing number of instances where the Micrologix 1400 that is paired with a Panelview C400 resets values when we cycle the power. Originally we thought the solution was a bad battery in the ML1400. This was the case the first few times that it happened. However, we recently had one doing the same thing and when the program was loaded onto another PLC and HMI combo it had the same issue. So either the battery for both just happen to be bad, or there is something in the program that is forcing the values to automatically reset when the power is cycled. I cannot post the program on here but I can tell you that the tags that are being reset are only used in the PLC program once. There are six total that are being reset and they are the high and low range in an SCP function that is used to scale inputs. I will be testing the program myself in house on a bench setup, but I wanted to get this question out there as soon as possible in case it is not an obvious problem. Has anyone seen this before? Any suggestions? If I come up with an answer I will post it. Thanks.
  24. Hello, I am having troubles configuring my Data Station Plus to be able to read my Vacon VFD registers over a Profibus network. The network is configured from an Omron PLC. I have communication but i do not know how to map the tags on Crimson to be able to read what the drives are doing. I am most likely thinking my offset on the tags that i have set are the main problem. Any input/ suggestion would be great thanks Specs on System: -Omron PLC CJ2M w/profibus PRM21 -Omron HMI NS-12 -3 Vacon NX VFD's -Data Station Plus w/profibus module