Search the Community

Showing results for tags 'network manager'.

  • Search By Tags

    Type tags separated by commas.
  • Search By Author

Found 72 results

  1. Hi, I am doing a project with three Omron Cj2m cpu.  I dont know how to connect More than one Omron Cj2m Cpu Plc in a same network to communicate each other with a Internal Memory addresses. Can any one help me to understand?
  2. Anyone ever have this happen:   launch Network Config.. Go online, upload the devices that are there:                         The NJ, The NA HMI, and a Ethernet/IP Generic drive (The EDS has been installed) ..  that's what you see above ..Click OK , and a "NO" to start a new list ... and get:                                                                       Really .... DUH! .. where are the devices?                            Anyone have any idea why the 3 devices didn't show up on the network line?     Thanks much... Regards, Michael    
  3. Hi again I browse through half a dozen mitsubishi manuals but turn up nothing for mitsubishi plc cross-communication. In this project there are about six L-06 plc:s. All are on the same ethernet network already, communicating nicely with the SCADA system. Per today information is (temporarily) exchanged via the SCADA system. Here is another hole in my knowledge. Namely how to correctly setup communication between these plc:s. I plan to continuosly exchange some 50 bytes of information. I would be grateful for some pointers and/or perhaps a reference to a manual. Cheers to all of you //
  4. Hi, this is my problem, I created an app on FT Administration Console, in fact, one for network and one for local, I changed the connection to local on Log On FT, but, when I try to define the data points on Step 3 of configuration checklist, only shows me the network app, i select the app, after click OK, the FTTM freezes, anything else happens, I don´t know what am I doing wrong.  
  5. Hello guys, I have the following distribution in a profibus network: S7-315-2 DP(--> Salida del conector)1- Free DP connector2- RS485 repeater3- Periferia ET200S4- Periferia ET200S5- Periferia ET200S6- Periferia ET200S7- Periferia ET200S8- Variador MM440 (Cabinet C)9- Periferia ET200LENDS7-315-2 DP(<-- Entrada del conector)1- Variador MM440 (Cabinet A)2- Variador MM440 (Cabinet A)3- Variador MM440 (Cabinet A)4- Variador MM440 (Cabinet A)5- Variador MM440 (Cabinet A)6- Variador MM440 (Cabinet A)7- Variador MM440 (Cabinet A)8- Variador MM440 (Cabinet A)9- Variador MM440 (Cabinet A)10- Variador MM440 (Cabinet A)11- Variador MM440 (Cabinet A)12- Variador MM440 (Cabinet A)13- Variador MM440 (Cabinet A)14- Variador MM440 (Cabinet A)15- Variador MM440 (Cabinet A)16- Variador MM440 (Cabinet A)17- Variador MM440 (Cabinet A)18- Variador MM440 (Cabinet A)19- Variador MM440 (Armario A)20- Variador MM440 (Cabinet A)21- Variador MM440 (Cabinet A)22- Variador MM440 (Cabinet A)23- Variador MM440 (Cabinet A)24- Variador MM440 (Cabinet A)25- Variador MM440 (Cabinet A)26- Variador MM440 (Cabinet A)27- Variador MM440 (Cabinet A)28- Variador MM440 (Cabinet A)29- Variador MM440 (Cabinet A)30- Variador MM440 (Cabinet A)31- Variador MM440 (Cabinet A)32- Variador MM440 (Cabinet A)33- Variador MM440 (Cabinet A)34- Variador MM440 (Cabinet A)35- Periferia ET200S36- Variador MM440 (Cabinet B)37- Variador MM440 (Cabinet B)38- Servoamplificador E94AYCPM (Cabinet B)END What would be the best way to configure the network? As you can see I have more than 32 nodes in 1 segment and the RS485 repeater is not being used properly. Hope you can help me, Regards!
  6. CJ1M CPU11 how to set IP adress?

    Hello, I have to work now with a cj1m cpu11. I would like to connect it to a ns10 display. My first obvious problem is when i made the project in cx programmer, that unlike in cj2m i wasnt able to select the cpu unit in the IO table and set the ip adress. How do i need to set the ip address? im reading an omron guide, but it is confusing, and so long, i only want to set the ip address :/. Also how can i set the fins network to 2? On the cx-designer i set the network address:2 and the node adress:40. I know that the 40 means the end of ip address. Thats why i want to set the plc. How about the network address 2?  Help is much appreciated. Thanks!
  7. So here's the problem I'm facing. I've recently started working for a company that has two facilities. They have lots of old equipment/PLCs, plus some new stuff. We undertook a project to upgrade the network infrastructure, and replace all the old programming terminals (Some had Windows 2000!) with a new standardized programming terminal, all sharing a common image. We've installed these new computers, and they were working great. Recently, we switched all the licensing to a Hyper-V based server, using FactoryTalk Activation Manager. Right off the hop, there was issues with one of the sites (let's call it site B). Site A is working fine. When you open FactoryTalk Activation manager, it populates the activations from the server in about 1s. The wait times for opening software are pretty normal (For RSLogix 5000, "normal" isn't exactly rapid, but like I said, that's normal). For Site B, the activations take forever to refresh in Activation Manager when opened on a programming terminal. The software takes even longer to open (we're talking about 2-3 minutes). Network wise, Site B is further along than Site A. We've implemented a Stratix layer 3 switch at the top of the network and use area specific VLANs to reduce multicast noise across the network (much of the multicast noise comes from vendor equipment, not PLCs, so I can't control it). This works fine. I can remote in and use TeamViewer/VNC with acceptable performance across the network, so it's not being bogged down to unacceptable levels. However, connection to the activation server is unacceptable. I'm not sure of the culprit (yet). We are continuing network improvements, removing some older 10/100 links and installing Gigabit equipment between the Hyper-V server and the above mentioned Stratix, hopefully that might help. However, that same 10/100 link is the one I use to remote in and use Teamviewer currently, so I can't see how much improvement it will give us for activations (which really should take almost no network traffic). To get activations, I'm just adding the IP address of the Activation Server into FTActivation Manager on the programming terminals. Any ideas, people? Thanks
  8. Version 1.0.0

    102 downloads

    This video about simatic manager s7 300 siemens plc in Hindi/Urdu
  9. Create new project in Simatic Manager View File This video about simatic manager s7 300 siemens plc in Hindi/Urdu Submitter faisal rasool Submitted 04/08/16 Category Manuals, Tutorials
  10. Version 1.0.0

    11 downloads

    Opto22 PAC SNAP UP1 ADS read network settings using Linux or other OS using a serial port terminal app
  11. View File Opto22 SNAP UP1 ADS read network settings using Linux Opto22 PAC SNAP UP1 ADS read network settings using Linux or other OS using a serial port terminal app Submitter Absolutelyautomation Submitted 04/01/16 Category Other PLC Demo Software
  12. Hi all, Quick question about adding ENET modules to a plc. If I have a local network of a HMI, PLC and 1 device all on IP 192.168.255.x and I have another device across the plant with an address of 171.27.19.x, can I add that one device to the PLC and it will recognize it? Is there a way to add a device with a totally different IP address to a PLC that is already set up?
  13. Hello All This is my first Transaction Manager project. I have a working configuration in Transaction Manager 10.20 that successfully writes PLC Data to an SQL 2012 Management Studio DB based upon a trigger event. The only problem I'm having is with writing String Datatypes to my SQL DB. For example, I have a "Serial Number" that is a string variable in my Allen Bradley ControlLogix PLC. In turn, I have the "SerialNumber" field configured in a SQL table as varchar(length 14). The Transaction Manager connector only shows SerialNumber PLC tag as Data[0] thru Data[13] under Data Points. In Transaction Manager I entered 14 in the "Elements" column for Serial Number. I assumed that would be Data[0]..Data[13] But when I trigger my transaction, the SQL Database field for SerialNumber is a value of "11"...which is the string.LEN property, (current string length of Serial Number is 11). How do I configure Transaction Manager to write the actual ascii value for the SerialNumber string to my SQL database instead of the string length? thanks Jay
  14. Hello All This is my first Transaction Manager project. I have a working configuration in Transaction Manager 10.20 that successfully writes PLC Data to an SQL 2012 Management Studio DB based upon a trigger event. The only problem I'm having is with writing String Datatypes to my SQL DB. For example, I have a "Serial Number" that is a string variable in my Allen Bradley ControlLogix PLC. In turn, I have the "SerialNumber" field configured in a SQL table as varchar(length 14). The Transaction Manager connector only shows SerialNumber PLC tag as Data[0] thru Data[13] under Data Points. In Transaction Manager I entered 14 in the "Elements" column for Serial Number. I assumed that would be Data[0]..Data[13] But when I trigger my transaction, the SQL Database field for SerialNumber is a value of "11"...which is the string.LEN property, (current string length of Serial Number is 11). How do I configure Transaction Manager to write the actual ascii value for the SerialNumber string to my SQL database instead of the string length? thanks Jay
  15. Hello everyone, I need to modify furnace ladder diagram to take control of the upper PID limit. The temperature on the furnace is controlled using PID. There is master PLC CJ1GCPU45SP which communicates several slaves CJ1MCPU13. It looks that all the PID parameters are send from the master to slaves over DeviceNet using seven DRM21 modules installed on extension rack. I can see where the values for the PID are entered on the HMI and moved to new location in the master but I don't understand why they are not placed in memory locations used by DeviceNet by default as per DRM-21 manual ( which if I understand correctly are D30000 to D31599). Is it because the DRM21 are mounted on extension rack? I will list all the upper limit locations in master, it is a long list but hopefully will help in resolving this issue: HMI entry location Moved to location in the ladder D16401 __________________ D32023 D16403 __________________ D32047 D16405 __________________ D32071 D16407 __________________ D32095 D16409 __________________ D32323 D16411 __________________ D32347 D16413 __________________ D32371 D16415 __________________ D32395 D16417 __________________ D32623 D16419 __________________ D32647 D16421 __________________ D32671 D16423 __________________ D32695 D16425 __________________ D29923 D16427 __________________ D29947 D16428 __________________ D31723 D16429 __________________ D31756 D16430 __________________ D31757 D16431 __________________ D31758 After they are moved to the D3xxxx location they are not used anymore anywhere in the master PLC so I am assuming they are transmitted over to be used in slaves. Is my reasoning correct? How can I calculate address space used by each DRM-21 card to make sure I am understanding what is transferred where? Thank you.
  16. PCS7 - FF Communication

    Hello Everyone, In PCS7 hardware configuration, I have connected IM153-2 FF link to a profibus master connected with CP443-5 Ext. And afterwards I have connected the field instrument with FF communication with the slave bus on FF link. However I am not able to delete the equipment once connected. The error is showing as the object is locked. How to unlock and delete the objects which were takes for testing purpose. Thanks in Advance, GJ
  17. Hello all, I'm new to this forum, hope I will be able to get some answers on this forum. I'm wotking on maintanance for machines under productiona and I would like to conect one machine to my work PC. But when I try to setup conection with RSLinx, RSLinx don't see my PLC. Problem is that my PC is on network with IP addresses 192.168.8.XXX and machine is on 192.168.0.1 IP address and between is cisco RV180 routher which is set to have LAN address 192.168.8.168 (company network), and WAN is set as 192.168.0.200 (subnet 255.255.255.0, gateway 192.168.0.201, dns 192.168.0.202). When I conect directly 1756 ENBT/A card to my laptop (laptop is set to same range of IP addresses) I can see PLC and everything is working but this way is not practical for me. Is there any way to conect my office PC to PLC, some settings in RSLinx Clasic? Any idea would be helpful. I attached simplified network drawing for easyer understanding. network.pdf Thank you for your time and help, best regards, baric1007
  18. SIMATIC S7-1200 + HMI +network

    I have a Simatic S7-1200 and i have a couple of questions :) I have three analog sensor giving information to the plc. software = Simatic step 7 basic V11 my questions: - can i connect the plc via a cable to a rooter to access the network to use a printer ? -can i connect a SIMATIC HMI KTP400 BASIC COLOR PN via a cable to a rooter to use with the plc via the network? - can i generate a document in the software , add my sensor data and print the document using all of the above ? thanks for all the help :)
  19. Is possible to comunicate an Eaton/Cutler Hammer INCOM/IMPACC network with a Modbus network ? Any experience ? Many thanks in advance.
  20. cx simulator

    hello navigators anyone has ever tried with cx simulator to simulate the network with eternet query from another external PC turns to where cx simulator?
  21. Hi, I have a problem with my BC9020 and hope that someone can help me. I managed to set the IP adress of my PLC in the 10.2.5... add a root, run a program and make the PLC working for a while. I then tried another program, a new one... and now that I want to re-read the first program, Twincat System Manager doesn't allow me to enter in the "run mode" and stays in "config mode". It also has lost the IP address I set (10.2.5.....) and came back to the 172.16.22... (manufacturer settings) I cannot determine if the problem is in the PLC Control or In System Manager... This is my method to change the IP *** IP config *** 1) Reset the PLC First I place the end terminal next to the PLC. I set the DIP switches 1,6,7 to ON, power on the PLC and power off. I set the DIP switches 2,6,7 to ON, power on the PLC and power off. I set the DIP switches 1,2,6,7 to ON, power on the PLC and power off. 2) Set my PLC on the same AMS than my own IP (172.16.22...1.1) 3) In System Manager, add a new route 4) change the setting in I/O Configuration -> I/O Device -> Device 2(BX9000) -> clic on BX9000 define "set IP Address" to Manual define " IP Address" to 10.2.5...., the AMS change automatically. Press the configuration button and then Ctrl+F4 (run mode) This method worked but seems not to be the best... If you have any Ideas ? or questions? Thank you in advance Gregi