-
Content count
2639 -
Joined
-
Last visited
Posts posted by Gambit
-
-
You do not need any extra programming in the PLC just the correct (dip) switch setting for your C24 module. -
Can you post the settings from Fix baudrate etc. If you're using the A series protocol make sure you use protocol 1 in the switch setting for the QJ71C24. -
Yes you can use the SC09 or FX-USB-AW to program all these PLC's. The programming software is GX Developer or GX IEC Developer (If available). -
never heard of this problem before. which version are you using? I can test it with 1.03D if you upload your sheet. -
If you are using IEC developer there are FB for INT and FLOAT. you can download them from the Mitsubishi website -
Sounds like you have a problem on the one hand you could count the plates because then the amps are >8. However you expect some plates to go trough without being cleaned which means bruches are running idle so the AMPS won't get above 8. So counting the plates via the AMPS is impossible. Can't you just add a sensor which sees when a plate is at /goes into the Brush location. -
The read out of your analog signal is constant so wouldn't it be easier to generate an alarm if the analog signal is lower than 8 AMPS for a certain amount of time. For instance: ---|AND< D0 K8 amps|----------------(ST0 K.....)--- ---|SM400|--------------------------------(T1 K600)--- ---|T1|-------------------------------------[RST T0]]--- This program will reset the ST0 every 60 seconds but within that time it will count the total time that the signal was below 8 amps. By using a stored timer the timer will not go to zero when the timer is off. it will once it is reactivated it add on from the previous collected time. Remember by default stored timers aren't available in the system Q so you have to set some in the PLC device parameters -
True enough however there is a siemens S7 to Mitsubishi Q converter it's not perfect but it does help! -
When deleteing the software check if the EZSocketGOT directory was also deleted. This part has all the communication for all Mitsubishi products in it. So if you have other mitsubishi software installed this will also be effected. -
Actually I work for the Distributer of Mitsubishi in the netherlands. The module is fairly new so we haven't done many projects yet. The biggest project we have supplied has about 40 MES modules and is growing. so far everything is running fine wihtout any problems. Our customer is very happy wiht the module and was able to implement the MES in record time. You can't do stored procesures with them yet. Hopefully this will be improved in future versions. The best thing is it's so easy anyone can do it even if you do not have any SQL experience. Why not ask your distibuter for a Demo. -
Citect will tell you to use CitectSCADA Reports for this. There are some tools on the Citect website which will convert trend files to CSV. When you have the info in excel you chould be able to make some simple reports -
If you are using a Mitsubishi system Q there is a module called the QJ71MES96. It will connect to serveral databases and is very easy to program. It also has a FLASH card which will buffer the data when to connection to the database is lost. you can connecto it to ACESS MSDE oracle MS SQL servers etc. Also If you're not using a Mitusbishi PLC they've also included this feauture in there ethernetcard for there HMI panels which can connect to most PLC's.1 person likes this -
Boot up while having F1 F2 & F8 pressed to set the terminal in system download mode. Then download a correct version in the terminal. -
You mean the programming cable? or for HMI. The programming cable (SC09) is protected you can't duplicate it. -
I was trying to use a counter with the minute pulse bit (m8014) but i need the same non-retentive operation of a timer. Can't you reset the counter when needed? -
The answer is easy when you want an instruction to use double registers you add a D in front of the instruction in this case DIV => DDIV. The same applies if you want an instruction to be activated once on the rising edge. then you add a P on the end DIV => DIVP or both DDIVP In the basic programming manual one of the first chapters shows you all the varients you can use -
Make an Array of the double words in the GVL. You can pprogram these via arrayname[variable as pointer or Z] array.doc -
In Europe the plan is to release it in June -
Let me put your mind at ease GDII is the package whitch will replace both GX Developer and IEC developer. It's part of a bigger software suite. It's already being used in Japan by large customers . I have one of the beta versions and it lookes ok. unfortunately this version is only for system Q. This PDF will give you more of an idea what Mitsubishi is working on. some of the improvements are multiple communication connections security special Function module in navigator not under tools no setting in I/O assiginment required setting are made via drop down menus instead of 0000100010100 on install for GD GX Sim and config tools simulator start in few seconds etc newsletter_119.pdf -
You probably haven't downloaded the new file to the stadard RAM yet Make sure to select whole range in the bottom of the screen. block conversion?? where do you see that? -
In the parameters use file register and increase the K-points. If the standard memory isn't enough use a mem-card. Before you choose your type of card check if the databook for the differences regarding fileregisters access. -
You've deleted your second I/O server???? both primary and standby I/O Device are on the same I/O server now. The settings should be more like the attachment. TestRig1MrPLC.zip -
Can you make an upload of the project. all i need is the comunnications, cluster,computer settings etc you can delete all pages etc. -
Via the kernel you can find out the status of the I/O devices. only one I/O device should be running. During comp setup you can select to use the kernel. Then during run use ALT space to go to the kernel
Timers in function blocks
in Mitsubishi
Posted · Edited by Gambit