Posted 11 Nov 2011 I have a CJ1W-PTS52 installed with a CJ2M-CPU33 processor. I have attached snips from the I/O table as to the setup. I have checked the wiring with a multimeter to make sure A', B' and b' are correct. The PLC appears to be happy with the sensors - there are 3 - 4 is empty. Getting crazy readings like 63,--- and cannot get the card to read correctly. There is not a lot of info available for the card and that may be the problem as to why I cannot set it up properly. Any ideas where I am going wrong from the I/O table snips? Share this post Link to post Share on other sites
Posted 11 Nov 2011 Hi Bob! Is this the combined temperature input unit? I remember a few weeks ago my colleague called me in the workshop and he was struggling with this one too.. erratic readings although everything seemed connected ok and set correctly.. darn it I don't remember exactly what it was but I believe, it had to do with an unusual procedure to set the DMs using the IO table. I checked and transferred the unit settings through the IO table a hundred times, but only after I first uploaded the units settings, set the parameters and transferred it back, I worked. Or something like that. Call me crazy but try it, upload the settings after you transferred, see if it changed. And if you find out: tell me!! Share this post Link to post Share on other sites
Posted 11 Nov 2011 Hi Bob Never used this specific card, but with similar ones, you need to set the input span to 100%. It's 0% in your screenshots. Cheers, Paul Share this post Link to post Share on other sites
Posted 11 Nov 2011 Then again, a sharp eye can also be your savior Share this post Link to post Share on other sites
Posted 11 Nov 2011 (edited) Thanks for the suggestions. It is just a 4 x RTD input card - no outputs or anything else and is just used for reading RTDs. You then write you code to suit what control you require. I have used them before but have not seen these results before. Will have to investigate further - just puzzling. Edited 11 Nov 2011 by BobB Share this post Link to post Share on other sites
Posted 11 Nov 2011 I don't know if this will help you or not, but this is what it says in the manual: I am guessing that you have already read this, but I thought I would throw it up here just in case. Share this post Link to post Share on other sites
Posted 12 Nov 2011 Thanks Michael Yep been there. I have probably done something stupid I guess and will have to find it. Probably come with a blinding flash when I next go to the job (I hope). Share this post Link to post Share on other sites
Posted 12 Nov 2011 Flash, yes. Blinding, I don't know... Share this post Link to post Share on other sites
Posted 16 Nov 2011 Interesting - set the span to 100% - default - and the conversion bit would not turn on. Checked the data memory area to see it was set up as I wished and it was. Set the span to 10% and it worked. There is not very much explanation as to how this all works and the manual is fairly useless. Perhaps someone from Omron could develop a help document for this card and make it available. Share this post Link to post Share on other sites