-
Content count
2632 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by Gambit
-
Well i did see that the network nr of the GOT for the Drive is set to 1 and for the E700 network 2. This could be the problem
-
This is the mitsubishi example project FR_GT27.GTX
-
Can create e nw lib and just add that shape and post it ?
-
[Important Notice]GX Works3 Ver.1.100E has been discontinued due to a flaw found in the ladder editing function.We apologize for the inconvenience, but please use Ver.1.097B until the revised version is posted.The revised version will be released in late November.
-
I think this could be the problem 9) In the redundant extension base configuration, the module extension parameter used by the module on the extension base unit must be stored in the intelligent function module. If the parameter is stored in the CPU module, an error occurs when the module is turned on or the module status is switched from STOP to RUN. Before writing the module extension parameter to the intelligent function module, set the CPU module to redundant mode.
-
flashing backup LED means the system could not switch. Check SD1642 Did you try settting SM1762 and resetting the system
-
SM1762 Operation setting for access from the standby system to the extension base unit Is this bit set ?
-
Your using Read input registers but it looks like you want to read holding registers ??? D0 but i don't see it set up in your program. I guess you want to use D10 but in your settings it's still D0 D100 has the start adress which should be 0 but in your program it's 0 Try reading 0ne register first instead of three and see if you have an offset of 1,.
-
Your using Read input registers but it looks like you want to read holding registers ??? D0 but i don't see it set up in your program. I guess you want to use D10 but in your settings it's still D0 D100 has the start adress which should be 0 but in your program it's 0 Try reading 0ne register first instead of three and see if you have an offset of 1,.
-
Go for Graphic ver. 2 You can check the differences in de e-manual viewer
-
Which GOT grahic version are you runniing ? You can find this under GOT Type Setting
-
you have two posts
-
New user - seem to be locked out of adding a new row (rung)
Gambit replied to rjr46901's topic in Mitsubishi
Which software are you using ?? Probably you're in monitor mode. I am guessing GX Developer. Try pressing F2 or if you saved your project in monitoring mode Tools -? option -> Don't write to PLC (top right) -
Most likely you have an ethernet TCP connection and the setting between the SCADA and the PLC are different regarding establishing the connection again after there is a failure. I know the System Q on default it will close the port after about 40 min. If the keep alive has been set. Now if the scada has a very small retry settings it will try to open a port which is already open and you're stuck waiting until the port has been closed. Change the settings on either side or maybe change to a UDP connection then you do not have any issues opening and closing ports. But this is a guess... Like @pturmel mentioned some more information is required for a better answer. Which PLC for instance and did you check the ethernet diagnostics from the PLC.
-
You want to enter only 90 right ? All yuou have to do is for the numerocal input to go to the operational Tab. Select Data operation and change the data operation to data expression. For write multiple the Monitor device with 10000 For Monitor divide with the same value
-
This is a connection fot he RJ71EN71 to be a modbus Slave. you only need one. But is you would like a second connection then the port nr should be different But You want to comm with two modbus slaves. You do this in the simple PLC comm settings in GX Works 3. You can find this in the params of the RJ71EN71. Here you can directly acces the Holding Reg etc and copy those to D or vice versa
-
Can you post some screen captures of your settings ?
-
same way you install the project but instead of the project select Boot OS. You should always do this as there might be a difference between the boot os in the GOT and the one the software is expecting
-
If I remember correctly the first time you are prompted to create one. If something went wrong here i would just reinstall the Boot OS and download again
-
I've changed the project a bit with some buttons to create the alarm. there are some alarms just press one of the alarms (double click wiht mouse in simulation mode) and you should see a pop up. See example below Example_Alarm.GTX
-
mitsubishi R08 plc retentive area cleared after power cycling
Gambit replied to Ramkumar's topic in Mitsubishi
which part and can you post your retentive settings -
mitsubishi R08 plc retentive area cleared after power cycling
Gambit replied to Ramkumar's topic in Mitsubishi
Did you connect the battery ?