banker
MrPLC Member-
Content count
142 -
Joined
-
Last visited
Posts posted by banker
-
-
Hi
Programming a CJ2M in ST is there a oneshot instruction and how to use a timer ?
PS I now how to program a oneshot.
Banker
-
Use the cross ref. in CX-programmer
Banker
-
Why not 64 bit real ?
-
Ethernet has most better performance
-
Hi
You need to start the card 2020.0 , 1, 2, 3 one bit pr channel.
Sorry my mistake you have already started the card, but the address for writing is 2021 unit no.2 ch.1
Banker
-
Hi
Use the Cross-ref ( ALT -X ) and you can see that the program use D20XXX in the section Bally_Flow_AVG
You have a functionblock AVG300 with AT_D20000
Banker
2 people like this -
The PLC is in run mode.
-
HI
Is it possible to have 2 CPU on the same PSU ?
Banker
PS. only using remote I/O
-
Yes you can install cxs on the same PC as cxone.
-
Hi
I got a beta ver 341(3) and I also have isue printing.
Banker
-
Problem solved By Omron Denmark: Mark all point and press <Enter> Then Press <OK>
-
Hi
After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address.
Anybody now hove to solve that ?
Banker
-
By default the address is 192.168.250.1
Banker
-
Thanks for the suggestion, but I want to avoid a solution with an extra relay. I had this setup with Omron PLC but on profibus, no problem because the comms. stop when the PLC goes into stop.
Banker
-
Hi
I have a problem. I have a PLC CJ2M with Ethernet/IP comms to some Danfoss drives FC280. I can start and stop the drives, control speed ect. BUT when/if my PLC goes into stop the drives continues. The drives have at controlword with a bit 10 Data valid bit ( most be On otherwise controlword will be ignordet ) When the PLC goes into Stop the Ethernet/IP continues to comm. so if i use DM memory for the comms it will not change. If i use CIO memory i all go 0 and the drive ignor the controlword. What to do. ???
Banker
-
Try i out in the simulater and if not make a convert from 16 binary to INT or use ther >S
¨Banker
-
Hi Kenra
What do not match ? the program is a totalizer I7.13 input oneshot. D3174+D3175 is the totalized value.
Banker
-
-
Hi I think you need Netconfigurator in CXOne
-
Hi
In you can run your cxdesigner project in test mode on you PC at connect the project to a PLC.
Banker
-
BobB it a function blok -
You have already ethernet/IP in this CPU. -
Look in the download section there is a function block for scaling Banker -
Hi Have tryed the same, solved by creating a new point and then run the project again. Banker
VFD ATV610 Parameters Commissioning
in Modicon / Telemecanique / Schneider Electric
Posted
You can use a browser or there is a software soMove, but for this you will need a special cable.
Banker