banker
MrPLC Member-
Content count
142 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by banker
-
Hi I have a problem. I have a PLC CJ2M with Ethernet/IP comms to some Danfoss drives FC280. I can start and stop the drives, control speed ect. BUT when/if my PLC goes into stop the drives continues. The drives have at controlword with a bit 10 Data valid bit ( most be On otherwise controlword will be ignordet ) When the PLC goes into Stop the Ethernet/IP continues to comm. so if i use DM memory for the comms it will not change. If i use CIO memory i all go 0 and the drive ignor the controlword. What to do. ??? Banker
-
VFD ATV610 Parameters Commissioning
banker replied to kivafishy's topic in Modicon / Telemecanique / Schneider Electric
You can use a browser or there is a software soMove, but for this you will need a special cable. Banker -
Hi Programming a CJ2M in ST is there a oneshot instruction and how to use a timer ? PS I now how to program a oneshot. Banker
-
Use the cross ref. in CX-programmer Banker
-
Split long word for average function in function block
banker replied to paulusB's topic in CX-Programmer
Why not 64 bit real ? -
Ethernet has most better performance
-
Hi You need to start the card 2020.0 , 1, 2, 3 one bit pr channel. Sorry my mistake you have already started the card, but the address for writing is 2021 unit no.2 ch.1 Banker
-
Hi Use the Cross-ref ( ALT -X ) and you can see that the program use D20XXX in the section Bally_Flow_AVG You have a functionblock AVG300 with AT_D20000 Banker
-
The PLC is in run mode.
-
HI Is it possible to have 2 CPU on the same PSU ? Banker PS. only using remote I/O
-
Yes you can install cxs on the same PC as cxone.
-
PrintActivePages(FALSE) scales text and graphics differently
banker replied to Transistor's topic in CX-Supervisor
Hi I got a beta ver 341(3) and I also have isue printing. Banker -
Problem solved By Omron Denmark: Mark all point and press <Enter> Then Press <OK>
-
Hi After updating CXS to ver. 3.4.1 I can't see point address I can see them when I editing but in the list form only the array len. is shown. When I enter a new point I can see the address. Anybody now hove to solve that ? Banker
-
By default the address is 192.168.250.1 Banker
-
Thanks for the suggestion, but I want to avoid a solution with an extra relay. I had this setup with Omron PLC but on profibus, no problem because the comms. stop when the PLC goes into stop. Banker
-
Try i out in the simulater and if not make a convert from 16 binary to INT or use ther >S ¨Banker
-
Hi Kenra What do not match ? the program is a totalizer I7.13 input oneshot. D3174+D3175 is the totalized value. Banker
-
Hi In france but maybe it can help. https://www.youtube.com/watch?v=oP5RQ7BHx5M
-
Hi I think you need Netconfigurator in CXOne
-
Hi In you can run your cxdesigner project in test mode on you PC at connect the project to a PLC. Banker
-
BobB it a function blok
-
You have already ethernet/IP in this CPU.
-
Look in the download section there is a function block for scaling Banker
-
Hi Have tryed the same, solved by creating a new point and then run the project again. Banker