gtsuport
MrPLC Member-
Content count
1329 -
Joined
-
Last visited
Content Type
Profiles
Forums
Downloads
Calendar
Everything posted by gtsuport
-
Please let your Omron hardware. Thanks, gtsuport
-
M.K You need a cable between the USB adapter and the CS1W-CN118. See attached. GTC99CC.pdf
-
Yep, HDM and RDM instructions, and handheld programmers. The good old days! You know your showing your age Garry.
-
Jay is one of the few on this forum that understands the S6. It was discontinued by Omron in 1993, over 25 years ago!
-
Please see the attached document. CF card is read if Dip Switch 7 is ON. CJ_EasyBackup.pdf
-
You will need to use the cable diagram referred to in my previous post . You will need to jumper pins 4 and 6 as well as pins 7 and 8 on the computer side of the cable. Unless these pins are connected, the software will not be able to communicate. Hope this helps.
-
Welcome to the forum. Check the W342 manual. Omron W342 manual Hope this will help.
-
Are you using the correct cable? See link below for correct pinout. Hope this will help.
-
I noticed the incorrect description also. I would use XFER. Should be a bit easier to understand down the road.
-
Benlawder. Take a look at the DBLL instruction. Not sure if that is what you are looking for.
-
How to exchange data between two omron PLC through series communication
gtsuport replied to seanshen's topic in CX-Programmer
Welcome to the forum. Take a look at PLC Link. Depending on how the RS422 connection is currently being used. Also take a look at Network SEND and Network RECV. Hope this will help. -
Go online with the plc. In the Project Workspace on the left of your screen, Click Memory. A new window should open. Click D on the left side of the screen, you should see a spreadsheet like view open. There should be a PLC option in the pull down menu, choose Transfer from PLC. That should upload the D memory values. The click on File and Save in Project. I think this is correct, I am not currently connected to a processor.
-
Welcome to the forum, You will need to connect to each plc individually to upload its program. Make sure you also upload the Settings and D memory values also. Most likely the two plc's are communicating via PLC Link. PLC Link is configured in the Settings. I hope this helps.
-
Best way to see what is happening would be to use the Watch window and monitor H2 in binary. This should help you see what is going on. H2.00 is set in the rung above the SFT. When the shift input is turned on, H2.00 value is moved to H2.01 and a zero condition would be moved into H2.00 in the shift register. However, if H2.00 is still SET on, you may not see the zero value at that position. Much depends on the rest of the program.
-
This is a bit different, but I can see where it would work. Instead of using the top input for the data for the shift register, if H2.00 is on when 16.01 initiates the shift, a 1 would be moved into the shift register. Not understanding the entire system, not really sure why it was done this way. Hope this will help.
-
That is the same cable you would use to connect to the CS1 DB9 port. You would just need to go to PT / Transfer / Transfer Settings to set up the transfer method. Then PT / Transfer / Transfer from PT.
-
1. See attached cable diagram. Software is CX-Designer. 3. You should not need to change DIP switches. GTC99CC.pdf
-
The PLC should not go to Stop / Program mode when you Transfer From the PLC. Hope this will help.
-
The receive complete bit will energize based on the Settings for the End Code for the serial port. In your Settings, you have the End Code configured as CR + LF. The receive complete bit will only turn on when the CR + LF (0D0A hex) string is received. The other option is to specify a different End Code, or specify the number of bytes to be received. If data is being received (regardless of the indicator led) there should be a value in A393. A393 will reset to zero when the RXD instruction is executed. I hope this will help.
-
Use the FVAL instruction. Please refer to manual W483.
-
There are no ASCII string instructions in the CP1E. Looks like you will need to convert the ASCII string to a Floating Point value (FVAL) then perform a Floating Point Comparison. Hope this helps.
-
Connect Masterflex Peristaltic Pump with CP1L -EM
gtsuport replied to AlbertMessakh's topic in CX-Programmer
I apologize. I did not properly read your plc logic when I reviewed it. Your values are correct. -
Connect Masterflex Peristaltic Pump with CP1L -EM
gtsuport replied to AlbertMessakh's topic in CX-Programmer
It looks to me like your range data is not properly set for the outputs. Please review Manual W462-E1-08 pages 468 and 469. Hope this will help. -
See my response on PLCs.net