pcmccartney1
MrPLC Member-
Content count
908 -
Joined
-
Last visited
Community Reputation
141 ExcellentAbout pcmccartney1
-
Rank
Guru
Profile Information
- Gender Male
- Location Colorado
- Country United States
- Interests Family, Golf, Lacrosse
-
Configure 1734-AENT using Generic Ethernet module
pcmccartney1 replied to JacoRoselt's topic in Allen Bradley / Rockwell Automation
Can you use the discover feature in 5000 to add the AENT and it's modules? -
Communication Issue Between 1756-L81E/B and 1734-AENT/C - Module Fault (Code 16#0203)
pcmccartney1 replied to LuisGonzalez's topic in Allen Bradley / Rockwell Automation
In the last picture, you should be able to click on the Change... button and select fw 7 then download to the PLC again. -
pcmccartney1 liked a post in a topic: Things to estop
-
Help Needed with QUINT4-UPS/24DC/24DC/10/EIP Communication Issue
pcmccartney1 replied to LuisGonzalez's topic in Control Panel Building
Not to sound obtuse, but have you gone to Phoenix's website and downloaded application notes, eds files, etc.? Have you set an IP address in the device? -
Can I use CIP motion over network with third party servo drive
pcmccartney1 replied to Aniket_B's topic in Allen Bradley / Rockwell Automation
Generally, the vendor will supply there own set of motion AOIs. -
VFD #1 and do a firmware upgrade. Because it truly has new components. By the same token, VFD #2 was recently tested for working condition.
-
pcmccartney1 liked a post in a topic: Connecting to Multiple HMI-GP Pro
-
How to enable source protection in several versions of RSLogix 5000?
pcmccartney1 replied to asteroide's topic in Allen Bradley / Rockwell Automation
I could be corrected, but the source protection you are talking about is only for version 20 and later. I presume you want to change the program for use with v17. To do so you will need to open the original in v20, turn off the source protection in the security tab of the controller properties and save to a new name. Then change the controller to v17 and it should convert the program. -
la communication entre un PLC Schneider et un équipement Rockwell
pcmccartney1 replied to Asrarmeryem's topic in Allen Bradley / Rockwell Automation
Also remember that the order of the bits in INTs and DINTs are reversed. -
pcmccartney1 liked a post in a topic: la communication entre un PLC Schneider et un équipement Rockwell
-
Check to see that it's seated properly. If problem still exists, then replace.
-
Studio 5000 v28.03 password protect
pcmccartney1 replied to PaulKim1003's topic in Allen Bradley / Rockwell Automation
The was a change between version 20 and 21. For v20 and older, you would use the Logix CPU Security Tool. For v21 and newer, you use theFactory Talk Security via Factory Talk Administrative Console with an adminsistrative account username and password and the Security tab of the Controller Properties based on the Logical Name. There's an entire manual to download and read to setup Factory Talk Security with Factory Talk Administrative Console. -
pturmel liked a post in a topic: Is there any RSLogix 5000 Memory Analyzing Software?
-
Suggest you download and read the ethernet function manual IB(NA)-0600628ENG-B. Understand that by default the drive parameters are set to be controlled by hardwired inputs and outputs and the HIM (human Interface Module). To control via ethernet, you must parameterize the drive to accept control and frequency reference via the ethernet. Unfortunately, I have no experience with Beijer PLCs or any knowledge of their capabilities and communication protocols. I saw a resource regarding comms via Modbus TCP and CANopen. Once the PLC and VFD are talking, then write code to read and write to the VFD. Different platforms use different terminology, but most use what is called implicit or explicit forms to read and write to the VFD. You'll need to determine what the Beijer capabilities are. Maybe find an example code at either Beijer or Mitsubishi to help you.
-
tanmanx liked a post in a topic: Rsnetworx for devicenet
-
Powerflex 525 driving a flywheel
pcmccartney1 replied to Joe E.'s topic in Allen Bradley / Rockwell Automation
Why is the DB so much hotter than the Machine #1? Also disconcerted about the DC Bus voltage difference. What is the result is you change the wiring to omit the DB thermostats signal? -
aleronick liked a post in a topic: How to read/write drive parameters?
-
L8 Controller Security Features
pcmccartney1 replied to ElectronGuru's topic in Allen Bradley / Rockwell Automation
Haven't looked at RBAC. I do use FT Security for a specific customer (150+ sites) because the process is patented. I've locked it down such that you can't even open the ACD unless you have the specific VM Image (i.e. computer name and ability to login to FT). -
Can't find my PLC on the "Who active" window
pcmccartney1 replied to LuisGonzalez's topic in HMI & SCADA
How did you configure your RSLinx Communications Driver? Which one did you use? Is your computer's NIC setup in the same subnet as the PLC? -
Rav liked a post in a topic: 1769-L33ER Processor not Talking to I/O Modules
-
If this is not applicable, then ignore me. Is the 1769-IT6 compatible or does it have to be a 1762? I presume that you found the module when offline with the 1500.
-
1769-L33ER Processor not Talking to I/O Modules
pcmccartney1 replied to Als's topic in Allen Bradley / Rockwell Automation
Your earlier picture shows the MNet module is already inhibited, so good call on removing it.