SamH
MrPLC Member-
Content count
4 -
Joined
-
Last visited
Posts posted by SamH
-
-
The majority at either CJ2m, NX-102-1020, or NJ-PD3001. I would like to do this for all the models
-
I'm looking for a way to automatically notify through SCADA if a PLC program has changed or a download has occurred. Does Omron provide a TAG or memory area in the PLC that tracks each time a program is modified/downloaded?
OPC UA Tag Data Type Issue
in NJ Series / Sysmac Studio
Posted · Edited by SamH
Currently have NX PLC setup as an OPC UA server and an OPC client setup and communicating. The issue is only tags that do not have a Data Type are showing up in the OPC client. I have 2 separate OPC softwares connected to this plc through OPC UA and both are having same issue. If I setup the OPC as a polling service, then all the tags show up as expected. Does anyone know if this is a known issue with Omron and their OPC UA server, or is there something that I am doing incorrectly (possibly a setting within Omron that I am not aware of)?