SamH

MrPLC Member
  • Content count

    4
  • Joined

  • Last visited

Everything posted by SamH

  1. Currently have NX PLC setup as an OPC UA server and an OPC client setup and communicating.  The issue is only tags that do not have a Data Type are showing up in the OPC client.  I have 2 separate OPC softwares connected to this plc through OPC UA and both are having same issue.  If I setup the OPC as a polling service, then all the tags show up as expected.  Does anyone know if this is a known issue with Omron and their OPC UA server, or is there something that I am doing incorrectly (possibly a setting within Omron that I am not aware of)?
  2. I'm looking for a way to automatically notify through SCADA if a PLC program has changed or a download has occurred.  Does Omron provide a TAG or memory area in the PLC that tracks each time a program is modified/downloaded?  
  3. Tracking program changes

    The majority at either CJ2m, NX-102-1020, or NJ-PD3001.  I would like to do this for all the models