Milosh

MrPLC Member
  • Content count

    76
  • Joined

  • Last visited

Everything posted by Milosh

  1. Hi all. I tried to start two identical Cx-supervisor runtime projects. Both of them started on different PCs. I noticed that after some time, some data (circle color) on one PC (runtime) were changed, but on second not. Why? I tried first to change the screen, and back, but the problem persists. Then I stop the runtime on "non-refreshed data" PC. After starting again data are changed. It looks like some refresh problem, but runtime projects are completely identical. 
  2. Etn021 ip address change problem

    Today I have success. I tried to change only last segment of IP address via DM registers without success. But after that I open web page of the module with IP address set before xxx.xxx.xxx.xxx/0 and login with ETHERNET, under Settings->System tab, I changed only last segment of IP address xxx.xxx.xxx.yyy than click on button Set, than Regist and reset the PLC. after that everithing eas ok.
  3. I have cts-etn021 module, and I change ip address via i/o tabe unit setup, and also set rotary switch to last segment of ip address. Let say ip address is 192.168.106.147 and rotary switch is set to 93. Now when I want to change ip address, from i/o unit table setup, and click on Transfer pc to unit, error is displayed *Transfer failed 11 mode and download failed* What is the best way to change the ip address of this module?! Ps. Tried in program/stop mode and also via toolbus, and ethernet.
  4. CX-Supervisor runtime startup question

    Does it need to be in Monitor mode?!
  5. Hi all. When I start Cx-Supervisor runtime v3.4 on startup for some devices are showed dialog with question like: "Switch device to Monitor mode?" Why this dialog is displayed? How to scip this question and use default settings?
  6. Etn021 ip address change problem

    It is in etn21 mode for sure. I will try it on site, next week.
  7. Etn021 ip address change problem

    No, I didn't change node number. I will try to change ip address via DM or web interface when I go to site next week. But, I wish to know if someone have the similar experience...
  8. Etn021 ip address change problem

    Did someone try to change IP address via web interface or via DM area?!
  9. Etn021 ip address change problem

    I tried with serial cable toolbus, cs1h-h cpu64h. First time I success to change, but second time I tried I can't change. I tried cpu power off, etn21 reset, but it always displays message Transfer failed.   I also tried with Transfer to PLC option, and check IO Table and Special Unit Setup. Special Unit Setup always fails.  
  10. To reply. Today I tried on site cx-supervisor application, and everything is work correctly. No error !!!
  11. Hi all. When I start my Cx-Supervisor v3.5 project, in log window I get this message: [Cx-Server: MANAGER, ERROR, 0x8825] Cx-server result code converter says that is  Failure: [CDM_ERROR] Communications Manager Error: [CDM_C_MANAGER]   What could be the reason?! How to fix this?   Same error as in post http://forums.mrplc.com/index.php?/topic/30492-cx-supervisor-runtime-failed/
  12. CP1H Communication HElp

    Hi all.  Did you solve this problem?!
  13. Point import problem

    Hi all. When I try to import symbol(point) from excel which is REAL type, Cx-Supervisor 3.5 displays next message: Unable to paste Point xxx  The Range/Default field is invalid. Before that I made  real point and export to excel, than I only change the Point name.
  14. APR - OUTPUT VALUE

    Thanks a lot all. I do the NEGL and everything seems to be ok.
  15. APR - OUTPUT VALUE

    Hi all. I have APR function for linear scaling. Sample X0=4000, Y0=80 X1=3000, Y1=82 Which would be the output Y for X=3000?! It should be 80. This function returns X0 if is X<X0?!
  16. APR - OUTPUT VALUE

    CS1H-H CPU64. I think that Ishould use NEGL instruction to negate D651 and D655, and than it would be work?
  17. APR - OUTPUT VALUE

    Thanks a Lot. But what happens if I have floating numbers. Let say. D651 = 4000 and D653 = 80.45?
  18. APR - OUTPUT VALUE

    Thanks a lot. But how to convert these values to be correct. Maybe to use some NEGATE function?!
  19. APR - OUTPUT VALUE

    D650 = #201 D651 = 4000 D653 = 80 D655 = 3000 D657 = 82 APR control word = D650 Source word = 3000 Result word = D760    
  20. Cable pinout, other settings

    Yes, thanks a lot, I just prepera the picture to send. That's it. thanks a lot once again.
  21. Cable pinout, other settings

    Hi all. Which cable I should use to connect cs1h-cpu64h with touch panel nq5-sq10-v2?! I mean pinout. We set host link communication both settings, baud, parity etc. on plc and panel are checked.
  22. Cable pinout, other settings

    Sorry, it is NS5-SQ10-V2 touch panel, and CPU CS1H-H CPU64. On CPU is set Host Link Port to standard and mode Host Link. Also for panel is set in comm. settings Host LInk SERIAL A. Baud is 9600, Data bits 7 parity E and stop bits 2. I think that my colegues use rs232c null modem cable. So I need pinout for this type of cable. Thanks in advance.
  23. Cable pinout, other settings

    It is serial port db9 connector...also serial port A on panel size.
  24. Need Manual for CS1W-CTS21 SSI Interface

    Yes, absolutelly, I have CS1W.
  25. Need Manual for CS1W-CTS21 SSI Interface

    Hi, thanks to all. No this module CS1W-CTS21 not CJ1W... Also I have instruction sheet for CS1W module, and there is section about DIP switches...