gclshortt

MrPLC Member
  • Content count

    271
  • Joined

  • Last visited

Community Reputation

33 Excellent

3 Followers

About gclshortt

  • Rank
    Sparky

Profile Information

  • Gender
  • Country Canada

Recent Profile Visitors

3441 profile views
  1. Upload Program from A1SH PLC

    http://suport.siriustrading.ro/02.DocArh/01.PLC/03.Modulare/05.MELSEC%20AnS,QnAS/01.Unitati%20centrale/01.AnS/AnS(J)HCPU%20-%20User's%20Manual%20IB(NA)-66779-N%20(01.11).pdf http://www.plctalk.net/qanda/showthread.php?t=17896 The above information may help you out. Regards, Garry
  2. From PM today: Sysmac C60P

    Another option would be to use a C200H-PRO27-E with a 3G2A5-AP003 and a 2 or 3-meter cable. https://accautomation.ca/purchase-find-parts/omron-c20k-c28k-c40k-c60k/#Peripheral This is still using the handheld but with the cable extension, it is better to work with it. Regards, Garry
  3. 90-30 Timer over 16 minutes

    http://www.plctalk.net/qanda/showthread.php?t=47460The above post mentions a similar application using a timer and a counter to get to minutes.Can you post the logic? Regards, Garry  
  4. Delta HMI Communication error

    What is the distance that you are communicating? Is it that you do not want to change the baud rate, or cannot change it? http://www.plctalk.net/qanda/showthread.php?t=53380 One other thing to do is to check the shield of your cable that you are using. It should only be connected to one end. This is usually the PLC side. Regards, Garry
  5. Up And Down Counter In Omron PLC CP1E

    https://accautomation.ca/omron-cp1h-counters/ The above thread may help you out. Regards, Garry
  6. Delta HMI Communication error

    http://www.plctalk.net/qanda/showthread.php?t=98877 Since this is not a constant error, I would try the following: - Ensure that your communication cable separate from your power wiring. - If the problem still persists, then try lowering the communication baud rate for each device.  Regards, Garry 
  7. wd indicator

    http://www.barr-thorp.com/wp-content/uploads/2011/06/PacDrive-Controller-C400-C400-A8-Operating-Manual.pdf wd (watchdog indicator) Watchdog is a hardware module to monitor the controller. OFF - Normal operation ON  - Fatal error; reset required, reboot system The above is from the manual above. This may help you out. Regards, Garry
  8. FX3GA-60MT Modbus RS485 as Slave

    https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf Look at section  '10.3 Creating Programs for the Slave Station' of the above manual. I hope this will help you out. Regards, Garry
  9. FX-EEPROM-16

    http://www.plctalk.net/qanda/showthread.php?t=3221 This thread may help you out. Regards, Garry
  10. HSC, new interrupt after Z-phase reset

    http://www.plctalk.net/qanda/showthread.php?t=62245 http://www.plctalk.net/qanda/showthread.php?t=32652 The above threads may help you out. Regards, Garry
  11. TrendGraph (Data Logging)

    https://www.myomron.com/index.php?action=kb&article=1639 The above link has the description for the Trend Graph: ' Trend Graph is linked to a data set and displays the values for analysis (coming soon) and User Alarms Viewer shows either current or historical information on alarms (see 'Introduction To NA Alarms' article). ' Regards, Garry  
  12. OMRON PLC

    http://www.plctalk.net/qanda/showthread.php?t=120902 Same question.  You will need to connect each PLC hardware rs232 port to the MOXA separately.  They will have different pinouts for the rs232 ports. Regards, Garry  
  13. An absolute beginner needs help with a PLC!

    http://www.plctalk.net/qanda/showthread.php?t=113901 The above thread may help you out. Regards, Garry
  14. Help Getting Started

    This is not an Omron NJ series, but here is a series on the Omron CP1H. https://accautomation.ca/series/omron-plc-cp1h-series/ I hope this will help you out. Regards, Garry
  15. http://forums.mrplc.com/index.php?/topic/11888-cx-supervisor-hanging/ The above thread may help you out. Regards, Garry