Modiconbob

MrPLC Member
  • Content count

    51
  • Joined

  • Last visited

Posts posted by Modiconbob


  1. Yes, there are several options available.Wasan is correct, and this unit/technology is over 40 years old!

    The P180 was never able to record/copy the program, it was only a programming console. The P190 had both capabilities.

    To back up the existing program, it will require a J470 interface, a cable and PC/computer that is capable of running a DOS program. I have all of that equipment and we perform these operations still to assist clients in upgrading their processes.

    You may contact me directly via email to discuss some options to get this operation done for you.

    bobculley@deltaautomation.com

     

    Thanks,

    ModiconBob

     

     


  2. Yes, there are several options available. Crossbow is correct, this unit/technology is over 40 years old!

    The P180 was never able to record/copy the program, it was only a programming console. The P190 had both capabilities.

    To back up the existing program, it will require a J470 interface, a cable and PC/computer that is capable of running a DOS program. I have all of that equipment and we perform these operations still to assist clients in upgrading their processes.

    You may contact me directly via email to discuss some options to get this operation done for you.

    bobculley@deltaautomation.com

     

    Thanks,

    ModiconBob


  3. You do not need to kill power to replace an I/O card. You can replace it "hot".  You only need to kill power on the processor, remote I/O interfaces, power supplies etc.

    The J890 gets updated from the processor on power up. nothing to reload there. Also, no programming changes for replacement card.

    1 person likes this

  4. ProWorx 32 isn't as terrible as it was originally. It's still NOT NXT though! Since it sounds like you will be utilizing it mostly for maintenance purposes now and for the foreseeable future, it shouldn't be too bad to convert. It is as if you will be utilizing a completely different PLC language. There is no similarity between NXT and 32. It just takes some getting used to. The configuration set up screens and traffic copping are a little cumbersome, but again it sounds as though you're not going to be doing program development on these units. The ladder logic screens are not too terribly bad. The comments etc will convert over with some degree of frustration but do work. Schneider really has no other option for it's steadily declining market share....... Good luck! Bob

  5. Modsoft was never designed to work with the 484. In fact, Modicon never produced any PC based 484 software. Taylor had a DOS based program that worked well. Currently there are two ways to get a print out of your 484 logic. One is with the old P190, J470, and the P190 tapes, and a serial printer. The other is to use the Taylor software, a J470 and a regular printer. I have both of these set ups here at my office. If you'd like, email or call me and I'll be glad to assist you. Thanks, Bob

  6. I am in the process of converting a 984B program to a Quantum platform. The 984B has a drum loadable module which is not compatible in the Quantum. I think that I can utilize the SCIF function block as a substitute. However the registers don't line up. Has anyone found a quick way to allocate these registers properly without doing a bunch of cumbersome register moving?

  7. Those are considered obsolet by Modicon, but you can still get replacement parts, spares and repair don eon these unit. If they are not giving you any issues and you don't need the additional features of the newer units, I would continue to utilize them. You may email me directly for more info. Thanks, ModiconBob

  8. This module can be removed under power without any hardware damage to it or the other items in the rack. I do not recommend doing that as the transfer of the register info to and from the cpu will be unpredictible and the results may affect your application adversly. It sounds as though the module is failing intermittently. On the remote I/O interface, is the Ourbus light flashing a regularly spaced error pattern? Or is it flashing intermittently? Does the Ourbus light light coming on coniside with the loos of comm to the B883? Basically the Ourbus light indicates that the interface cannot communicate with one (or more) cards in the rack that are traffic copped.

  9. Modsoft will function for this. ProWorxNXT is great but no longer available. Any 984 software will work with this unit, P190 based, DOS based, etc. The distributor has Proworx32, but it's junk, and it's expensive. Schneider has done a poor job of taking care of their legacy product customers. Email me, I may have some alternative paths to accomplish this.

  10. When you select "online", NXT should request an address for the PLC. Modicon typically defaults to one (1), but it could be anything between 1 & 255. This is the attaching process for NXT. In the much older programs, you had to perform a specific attach routine. The name attach just has stuck around. After NXT allows you to look at the logic when online, you are attached. Again, the cable plays an important part here, especially if you are using a 9 pin to 25 pin adapter on the cable. Not all of these adapters will function correctly. A common problem with them is the not logged in error.