Mickey

MrPLC Member
  • Content count

    1834
  • Joined

  • Last visited

Posts posted by Mickey


  1. 7 minutes ago, pcmccartney1 said:

    Seems he would have a fault on the module or the PLC5 were the wrong module be installed in the slot and differ from the program?

    But as the others have said, those terminals are not used for the IAD.

    FYI, The PLC5's do not required a I/O configuration. It's documentation only if it's there at all.

    I/O addressing would certainly be a problem.


  2. 1 hour ago, Nancygogogo said:

    Hi Mickey, I did use the same filter equation as yours, and I use 0.1 for the constant, but the output still not stable, as it said in the attached. The smaller the number the more damping. Ohhhh, so probably I can use 0.0001 as my constant? Cause before I thought 0.1 is the smallest number I could use....

    You can, but that is a lot of damping.

    Just play until it helps.


  3. Yo have channel 0 configured for "Percent Value" which has an implied decimal point of 2 places, so your read is 17.5 % full scale.

    You can change that to Engineering Unit X 1 to get a direct temperature reading.Or engineering units x 10 to get a direct temperature  reading with an implied decimal point to 1 place.

    See pdf

    rawdataformat.pdf