maccxim

MrPLC Member
  • Content count

    77
  • Joined

  • Last visited

Everything posted by maccxim

  1. Mitsubishi memory card A2SNMCA-30KE

    Which parameters you have to set?? I think you don't need to set nothing, just to install memory device on the socket of cpu module. GX/GX_IEC automatically download/upload project onto AnS memory card. Bye Max
  2. A970GOT is expensive!...AB DARK SIDE tempts me

    Im not an expert about GOT price, my opinion is the A970GOT it's an old product. I know Mitsubishi is starting to sell new GOT 1000 versions. I suggest you to compare AB with this new version of GOT, also about the price. Bye Max
  3. anybody know if there is a internet site where we can upload graphics symbols for HMIs? I use a lot of types of hmi, i.e. Beijer, Mitsubishi, and more. thank you Max
  4. Temporizadores en FX1N

    Si entiendo bien: LD X0 OR Y0 ANI T0 OUT Y0 LD Y0 ANI X0 OUT T0 K10 Ola Max
  5. Temporizadores en FX1N

    Both timer on FX1N are On-Delay timer. range from T0 to T199 are 100ms timers range from T200 to T245 are 10ms timers range from T246 to T249 are 1ms timers and T250 to T255 are 100ms retentive timers. an example: LD X0 OUT T0 K10 LD T0 OUT Y0 Bye Max
  6. Q40CBL-3M Cable

    Yes, Q40CBL-3M it's a cable with 40 pin connector ready made. On one side you have the connector ready made for plc card. On the the other side you have all free cables with colours. If you have the data sheet of this cable give me an e-mail. bye Max
  7. HMI to DVT 510

    I'm not sure but i think Beijer Electronics provide terminals with DVT driver. Try to look on http://www.e-terminals.com/ bye bye Max
  8. FX2N-modem

    Thank you for the informations. I will try Max
  9. FX2N-modem

    I need to connect an US-Robotics modem to an FX2N plc. The modem is the standard V09 56K fax modem of Us Robotics. I installed on FX2N plc the interface FX2N-232-BD, just to connect the modem. Somebody can send me the settings to configure the modem? i.e. AT commands, cable or other ? Best regards Max
  10. GX IEC Developer

    I have both versions: GX Developer and GX IEC. Sorry but i still prefer the GX Developer. It's more easy, more direct to philosophy of Mitsubishi plc. No problem of memory used with small project for FX. With Q serie is possible to create function blocks like IEC version, of course with some limitations. Comparing both versions, i think GX is more faster than IEC vesion expecially on projects debugging or during editing of small projects when you don't need to create functions blocks. Only on last 6.10 release of IEC a lot of problems are solved, but not all. In both case i think it depends which type of automations you have to develope bye Max
  11. QJ71MT91 Modbus

    Somebody know the QJ71MT91 Modbus card. I know it provides only TCP Modbus protocol and not RTU. Somebody has a plc program example for using this card? i.e. Master or slave function. Best regards Max
  12. mitsubishi SFTL

    Try to use PLS instruction with an auxiliary M and use it as shift clock input. Max
  13. FX2 PLC

    I have to use an old model of FX2 cpu (not FX2N!). Qustion: is possible to install special modules of FX plc, such for example FX2AD/FX2DA/... ? thank you Max
  14. A1SJ PROBLEM

    Looking on the network parameters seems everything is ok. Question Did you transfer on the new cpu the nework parameters ? Max\
  15. Coordinated Motion w/ FX1N

    You can use two DDRVA at the same time with different pulse output of course. Also for me the only way for start the 2nd axis is to detect the D8140 register. bye Max
  16. touch panel mitsu

    If i understund your request, it can be possible because on th Got terminal the driver is generic for both FX plcs. Just connect your pc with Got programming cable on the 232 port of terminal. I think you can read the plc program. bye Max
  17. A1SJ PROBLEM

    Have you configured the correct parameters for network on plc master? With Gx developer go to Netw.Parameter. Have you checked the number of local station ? and the B/W map for send-receive? bye Max
  18. Temperature Control module for AnS series

    You can use A1S64TCTT-S1 module. 4 pid channels with autotouning, 4 inputs for temp.detection, 4 transistors output for on/off temp.control. bye Max\
  19. PC to Melsec PLC Not talking!

    Hi I found the same problem time ago with my new notebook. I suggest to use the SC09 cable converter connected between usb-9pn converter and plc port. I'm not sure but i think SC02 have differents pins connection about 5Vdc p.s. Bye Max
  20. GOT hmi with Multilanguage

    Hi everyone I have a question about GOT terminals: With FGOT terminals is possible to implement multilanguage functions? Best regards Max
  21. Q06HCPU download upload problem

    You have cpu Q06H version A or version B ? Version A are very old and have many problems. Check on the Diagnostic/System Monitor/Prod.Info. Regarding different type of memory, normaly everytime i use fash memory i set the plc in auto boot mode, so to copy the full project from flsh to prog.memory at the start up. bye
  22. Programing cable

    Regarding the eprom, i think your are using A1SNMCA8KP eprom memory. I think is not possible to reprogram using cpu port. You need to use an adaptor like A6WA-28P for 28pin circuit and program it using pc. bye Max
  23. I went to Beijer headquarter long time ago. i confirm they produce a lot of type of terminals, more than you can see on catalogues. Specially dedicated for oem partners and if they found good feeling with a product, they transfer the production for general market. If you need ethernet on terminal, i know there is now the new MacE410 with built-in ethernet port. Bye Max
  24. Mitsubishi FX2N-1HC

    If you have two prox switch i think you nedd two FX2N1HC modules because it's a one channel (1/2 phase). I send to you the user manual of FX2N1HC. In this manual you can find a small example of program. bye Max FX2N_1HC.pdf
  25. QC24, Modem

    I need to make modem connection between my pc and two Q00CPU. I have one Westermo TD33 analog modem on remote side. My idea is to use two QJ71C24N serial cards installed on the two plc rack and connect TD33 modem to 232 port of first C24N card. Then connect the 485 ports of both C24N, so to realize a drop connection and chose plc number with GX Developer during modem connection. What do you think ? anybody have expereance or suggestions? best regards Max :-8