RussB

MrPLC Member
  • Content count

    653
  • Joined

  • Last visited

Everything posted by RussB

  1. GE CCM Comunication

    You should ask Kepware that question. My guess would be that somewhere in the Kepware setup there is a setting that asks which CPU you are talking to if that is the case try telling it that you have a CPU36x or CPU37x or even a 90-70. It uses the same SNP protocol and has more memory.
  2. iFix screen adjustments

    I don't know the answer but try searching here. http://forums.ge-ip.com/forumdisplay.php?f=80
  3. E-Stop wiring help

    1. Through a transformer. 2. Through a "Safety Relay".
  4. Simple question

    In a GE PLC one would use a Positive transition coil for the first (UpArrow) and a Negatve transition coil for the second (DownArrow), both would in turn activate the %S5(?IIRC) which transitions ON for 1/2 second then OFF for 1/2 second. Other brands will vary.
  5. OPC data from Quickpanel

    I would recommend www.kepware.com Their stand alone OPC Driver is in part what many PLC/PAC/HMI manufactures use today as their embedded OPC driver, including GEIP. If you already have all the needed data in Historian you may be able to use SQL to transfer it to the Fabguard controller.
  6. When you operate a large contractor in by hand and one is not "fast and hard" on the push, there is a good possibility of "single phasing" the circuit for a fraction of a second, which can do harm and cause big sparks.
  7. PLC Rack installations

    I really don't see what difference it makes, just label them clearly. Anyone in there messing with them will have enough smarts to figure it besides and the electrons sure don't care. :) (BTW, I found an "e" back in the corner, did you lose one?)
  8. I'm sure that the manual tell you how many pulses are in a complete revolution of 360 degrees. Tell the controller to move 1/4th of that.
  9. GE Ethernet Global Data

    If you would give us pertinent details we may be able to help. "Turning red" means little if we don't know what software is turning it red and where in the software. Kepware has very good online assistance, diagnostics and telephone support. If the "Red" is in the hardware configuration of PME, it means that the address(es) chosen is either invalid or already used somewhere else. EGD is very simple but it must have proper data lengths entered for the consumed and produced, double check that one is not set too high or too low for what is actually being sent.
  10. GE SNP Communication Configuration

    IIRC, In some of those older systems the "Device ID" was set for the PLC instead of the port. To do this on the older ones you needed to assign the Device ID to the port on the power supply. This is done in the hardware configuration of the CPU. Confusing isn't it? Also inconvenient (imposable) when one needed two Device IDs. :) Try it, that should work. P.S. If you had asked that right away, you would be done already. ;)
  11. GE SNP Communication Configuration

    I am sure that someone can help. What is the question? Which OPC server are you using and what port is it connected to also is it RS-485 or RS-232? What cable are you using? There are several ports and cables to choose from with those two devices. You can find some of the pin configurations here: http://forums.ge-ip....60395#post60395
  12. GE CCM Comunication

    Yes, provided that your data-logging OPC software speaks SNP, it is just another serial protocol. Be aware that there is SNP and SNPx, similar but not exactly the same, you need the same at both ends as in any other serial parameter. Get the documentation relevant to your hardware and OPC software and compare the two. Hardware documentation is here: http://support.ge-ip.com/
  13. GE CCM Comunication

    If your CPU350 and CMM311 are of later version or can be updated to later version, an alternative would be to change to the SNP protocol.
  14. error 8033 invalid scope

  15. Binary Bits

    Confusion #1 - There is no difference as all inputs and outputs are bits and all bits are binary bits, either "ON" or "OFF", "Open" or "Closed" (1 or 0).
  16. GE 9030 Uploading

    Yes, that will work just make sure that the two CPUs are of the same model (part) number.
  17. Quickdesigner version 3.70

    Good, now backup that .prj file so you have it for next time.
  18. Quickdesigner version 3.70

    Only if it was exported as a .prj file on the 1st laptop. IIRC, by default it would be in the "Quick\Data" folder. With version 3.70 CD you can re-install to get 4 days to work with it until you need to "authorize" it, but don't over write your only copy of that app. Also the license can be transferred from 2nd back to 1st.
  19. Need help with Basic Project

    This is what the Red Lion Sixnet RTU was designed to do. http://www.sixnet.com/department/automation-devices-78.cfm?killnav=1&az=0 There are several to choose from.
  20. Enclosure Assembly

    Two of these magnets 1500 Newtons (337.2 lbs) each will hold any but the very largest. 24 VDC at 7 Watts each. http://www.jokabsafetyna.com/2012-04-03-17-39-40/2012-04-03-13-36-23/magne-1-2-magnetic-lock-with-indication?highlight=WyJtYWduZXRpYyIsImxvY2siLCJtYWduZXRpYyBsb2NrIl0=
  21. QuickDesigner

    Contact GEIP: http://support.ge-ip.com/support/index?page=spage&id=ST6&locale=en-US&locale=en_US
  22. quickpanel with quickdesigner to new qp with proficyview

    You can purchase it, here is where to start: http://support.ge-ip.com/support/index?page=spage&id=ST6&locale=en-US&locale=en_US
  23. Proficy Machine Edition demo CD

    See this: http://support.ge-ip.com/support/index?page=spage&id=ST6&locale=en-US&locale=en_US
  24. QUICKPANEL TOTAL PRODUCTS

    You will need to purchase it from your local GEIP dealer, you can locate them here: http://support.ge-ip.com/support/index?page=spage&id=ST6&locale=en-US&locale=en_US
  25. Measurement Systems

    Check out the MTS' Model RF. http://www.mtssensors.com/fileadmin/media/pdfs/R_Series_RF_Flex_Housing.pdf