Sign in to follow this  
Followers 0
permitivity

24VDC guard door circuit

7 posts in this topic

Hello, I have a really long 24VDC guard door circuit, and I went and calculated how much votlage drop there would be and whether there is still enough voltage at the end of the run to pull in a relay. Could someone look at the why I calculate this to see if it's right? Run: 1900ft of 18 guage wire: <0.00751ohm/feet * 1900ft = 14.3ohms> Relay: 24VDC coil, rated at 6.5W power consumption, so that's about 0.28A. So coil has 24V/.28A=86ohms Total resistance: 24V/ (14.3ohm+86ohm) = .24 amps. So I can expect .24amps on the wire, which is slightly less than the .28A needed to pull in the coil. Does that mean I wouldn't be able to use this relay, or might have to go 120VAC? How much wiggle room is there on these ratings? The relay doesn't list a minimum, simply the rated coil energy. Thanks,

Share this post


Link to post
Share on other sites
You should have taken your math one step further, the amount of voltage across the relay will be a tad over 20v, check the relay rating for the minimum pull-in voltage, if this is <= 20v then you should be OK

Share this post


Link to post
Share on other sites
What safety relay are you using ? Most modern safety relays have discrete inputs that draws very little current.

Share this post


Link to post
Share on other sites
Another possible solution: Most of the newer switching power supplies, can be adjusted up to 28 VDC. Buy a dedicated power supply just for this circuit, and adjust the voltage up until the relay functions as desired.

Share this post


Link to post
Share on other sites
Another possible solution: Change the wire size from 18 to 16 awg and drop the resistance to about .005 ohms/ft.

Share this post


Link to post
Share on other sites
Thanks for the replies: 1. I can not up the voltage of the power supply as it is being used for other things too. 2. The relay is a AB 700S relay. It has the smallest power consumption compared to other industrial relays. 3. I'm using a cable, so the gauge is not easily changed. 4. Weird, but the spec sheet on the relay doesn't list minimum pull in voltage - only power consumption. Is there anything wrong with my math?

Share this post


Link to post
Share on other sites
Just to make sure I've got the right spec sheet... Are you using a 700S-CF? If so, the Operating Voltage for 24VDC is: Pick-up = 16.8 to 30 VDC (see note 1 - 0.7...1.25 x Us) Drop Out = 14.4 to 2.4 VDC (0.1... 0.6 Us) I found this info right above the Coil Consumption rating. HTH! Susan Edited by ssommers

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now
Sign in to follow this  
Followers 0