Posted 26 Oct 2018 Every time my rsview32 project starts up all the alarms which are set up to alarm on 0 tag value show up on the screen even though the bit in the PLC is not in alarm condition. I believe this is because the communication between RSView32 and PLCs is not established yet and the tags are seen as having value of 0 in the HMI. Is there a way to disable or suppress these tags at startup to give enough time for the RSView to update the values so the false alarms are not being displayed? Share this post Link to post Share on other sites
Posted 29 Dec 2018 Been a while since I worked on RSView 32, but in the manual for setting up tags it has the option of initial value. If you set the initial value to non-zero that should prevent faulting and then when it reads you'll get actual state and it will fault if is needs to. I was reading page 4-5 here {https://literature.rockwellautomation.com/idc/groups/literature/documents/um/vw32-um001_-en-e.pdf} Share this post Link to post Share on other sites