Milosh
MrPLC Member-
Content count
86 -
Joined
-
Last visited
Posts posted by Milosh
-
-
Hi all.
I would like to know if there is possibility to change password for levels dynamically from PT.
Sample:
I want to change Level 1 password. Idea is to create button to access screen which show all levels and their passwords.
This button must have master level authorisation (one password which can't never changed from PT).
Steps:
1. user click on button ALL PASSWORDS
2. user should enter master level password to open screen
3. screen opened, and show all levels and their passwords
4. user click on level 1 for example, and popup screen opens
5. user must enter new password twice, and confirm
6. new password for level 1 was saved.
Best regards,
MK
-
Ok, I understand.
You mean to use CJ2M CPUs with built-in ethernet port. But definitely, Network configurator will be used to configure Ethernet/IP data links.
So, if I have two CJ1M-CPU11-ETH cpus, I should to add EIP modules on both cpu sides?! Right?
-
2 hours ago, BobB said:Use Network Configurator - a part of CX-One.
Ok, I understand, but do I need additional modules, or it can be done via built in ethernet port?!
Do I need to make plc program and use special instructions to make data exchange, or it can be done by configuring data links?!
Thanks in advance...
-
8 hours ago, BobB said:Yes but getting old now. Easier to use 2 x CJ2M-CPU31 and Ethernet between them.
How to make ethernet data exchange?!
-
Ok, but in the best case i Will have 2 CJ1M plcs.
Is there any example of data links between two cpus?!
Do I need CLK modules for this type of communication!?
-
Hi again.
What about controller link, is that possible to make data links between two cj1m controllers?!
-
Not only digital signals, it should to exchange some float setpoint, measurements etc.
Ok, I will try to find some code samples for ethernet ip and modbus tcp.
What about two omron plcs, is there also best solution to use eth. ip?!
Where I can gind some basic samples omron plc-plc communication?
-
Just now, pcmccartney1 said:Festo CPX seems to have many communications protocols including Interbus, DeviceNet, Profibus DP, CAN open, CC-Link, Profinet IO, Ethernet/IP, Modbus TCP, EtherCAT, Sercos, Powerlink, CodeSys.
Omron, depending upon CPU type has many options for several of the types listed above.
In this moment I know that omron plc is cs1m.
1. What is the best protocol (easiest way) to make communication between omron and festo?
2. One solution of my project is to change festo and put one more omron cj1m plc. What is situation here? Which method of communication is the easiest to configure?!
-
Hi all.
Is there any possibility to make communication (data exchange) between Omron CJ plc and Festo CPX?!
If no, how to make data exchange between two Omron CJ plcs?!
Thanks in advance.
-
Hi all.
I tried to start two identical Cx-supervisor runtime projects. Both of them started on different PCs.
I noticed that after some time, some data (circle color) on one PC (runtime) were changed, but on second not. Why?
I tried first to change the screen, and back, but the problem persists.
Then I stop the runtime on "non-refreshed data" PC. After starting again data are changed.
It looks like some refresh problem, but runtime projects are completely identical.
-
Today I have success. I tried to change only last segment of IP address via DM registers without success. But after that I open web page of the module with IP address set before xxx.xxx.xxx.xxx/0 and login with ETHERNET, under Settings->System tab, I changed only last segment of IP address xxx.xxx.xxx.yyy than click on button Set, than Regist and reset the PLC. after that everithing eas ok.
-
Does it need to be in Monitor mode?!
-
Hi all.
When I start Cx-Supervisor runtime v3.4 on startup for some devices are showed dialog with question like:
"Switch device to Monitor mode?"
Why this dialog is displayed? How to scip this question and use default settings?
-
8 hours ago, innoaloe said:Just a guess, but seeing a "Mode 11" message appears, try to double check your IO Table.
Did it say CS1W-ETN21(ETN11 Mode) or CS1W-ETN21(ETN21 Mode)?
There might be a chance that your ETN21 was set up in ETN11 Mode, but now you are accessing it in ETN21 Mode, or vice versa.
In any case, in the IO Table, you can click on the ETN21 unit, then click "Options --> Change ETN21 Mode" to choose the mode suitable for your needs.It is in etn21 mode for sure.
I will try it on site, next week.
-
No, I didn't change node number.
I will try to change ip address via DM or web interface when I go to site next week. But, I wish to know if someone have the similar experience...
-
Did someone try to change IP address via web interface or via DM area?!
-
I tried with serial cable toolbus, cs1h-h cpu64h. First time I success to change, but second time I tried I can't change.
I tried cpu power off, etn21 reset, but it always displays message Transfer failed.
I also tried with Transfer to PLC option, and check IO Table and Special Unit Setup. Special Unit Setup always fails.
-
I have cts-etn021 module, and I change ip address via i/o tabe unit setup, and also set rotary switch to last segment of ip address. Let say ip address is 192.168.106.147 and rotary switch is set to 93. Now when I want to change ip address, from i/o unit table setup, and click on Transfer pc to unit, error is displayed *Transfer failed 11 mode and download failed*
What is the best way to change the ip address of this module?!
Ps. Tried in program/stop mode and also via toolbus, and ethernet.
-
To reply.
Today I tried on site cx-supervisor application, and everything is work correctly. No error !!!
-
Hi all.
Did you solve this problem?!
-
Hi all.
When I start my Cx-Supervisor v3.5 project, in log window I get this message:
[Cx-Server: MANAGER, ERROR, 0x8825]
Cx-server result code converter says that is
Failure: [CDM_ERROR]
Communications Manager Error: [CDM_C_MANAGER]
What could be the reason?! How to fix this?
Same error as in post http://forums.mrplc.com/index.php?/topic/30492-cx-supervisor-runtime-failed/
-
Hi all.
When I try to import symbol(point) from excel which is REAL type, Cx-Supervisor 3.5 displays next message:
Unable to paste Point xxx
The Range/Default field is invalid.
Before that I made real point and export to excel, than I only change the Point name.
-
Thanks a lot all.
I do the NEGL and everything seems to be ok.
-
CS1H-H CPU64. I think that Ishould use NEGL instruction to negate D651 and D655, and than it would be work?
Change password for Level
in CX-Designer
Posted · Edited by Milosh
Yes, that solution with Control flag is good, but I should implement password change part on PT. Is that possible with CX-Designer at all?
I found in manual (attached page), a way for changing password for NS15, but I didn't have PT to test it. Is this right way?