jrsiscool
MrPLC Member-
Content count
3 -
Joined
-
Last visited
Posts posted by jrsiscool
-
-
HI I'm using PlC5/20 when I click on setup screen on the BTR block (to view the analog input configuration) i find the following message: No modules exist in the IOconfiguration for this R/G/M however the analog input signals is running properly....i just want enter the setup screen for configuration. I'm assuming that I need to enter I/O module in the I/O configuration? Can I do this without taking PLC to Program mode?
-
HI I'm using PlC5/20 when I click on setup screen on the BTR block (to view the analog input configuration) i find the following message: No modules exist in the IOconfiguration for this R/G/M however the analog input signals is running properly....i just want enter the setup screen for configuration. I'm assuming that I need to enter I/O module in the I/O configuration? Can I do this without taking PLC to Program mode?
Powerflex 700S drives fault on F59 Net Loss DPI P5
in Allen Bradley / Rockwell Automation
Posted
I have an issues with various Powerflex 700S drives tripping out periodically on Net Loss DPI P5 fault (F# 59).
These drives are set up on the same ControlNet network to communicate with the Contrologix 5563 processor.
The drives will reset easily and the process restarted, but it is a nuisance and time is lost resetting the equipment.
Any advice will be appreciated.