Dac1987

MrPLC Member
  • Content count

    7
  • Joined

  • Last visited

Posts posted by Dac1987


  1.  
    This part I understood, my doubt was if I change some configuration on this page and lose communication
    with rslinx and never again can open the program that was my doubt.
    And on that page that you attached in the "General" tab, 
    what value did you put in the "Passthru Link ID (dec)" setting? 
    On channel 1 and channel 0.
    Thanks for the help the idea is getting clearer and clearer.

  2. Right. That's what I want to do, I want to communicate the HMI with the PLC.
    It does not matter if when I need to use the PC I lose communication with the HMI.
    The HMI will only be used to enter values in timers and a fault list.
    And the cable I use to make this communication between PLC and HMI is the same communication cable
    between PLC and PC or do I need to change anything? 
    Thank you very much.

  3. I did a bench test and I was able to connect the HMI with a micrologix 1200. 
    But in SLC 5/03 I will have to make the change in channel 0 (enable it in channel configuration),
    but I have a doubt on the same channel I am using to do the communication with rslinx,
    if I make any changes I run the risk of not being able to open the PLC program anymore? 
    Mr. Joe Thanks for helping me out.