Must@@@@

MrPLC Member
  • Content count

    24
  • Joined

  • Last visited

Posts posted by Must@@@@


  1. hello everybody ı have machıne wıth sımatıc s7-1500 wıth tp1200 comfort how can ı upload program from hmı tp 1200 comfort to my laptop wıth tıaportal v17

    ı dıd backup and tempt fıle but ı dont no haw can open fıle


  2. hello everybody

    ı have machıne wıth sımatıc s7-1500 wıth tp1200 comfort how can ı upload program from hmı tp 1200 comfort to my laptop wıth tıaportal v17


  3. I have connected 2 temperature devices with him delta with plc delta by rs485. When I run plc I can see the temperature change on pc but the problem in hmi  it's give errors. Com 2 errors 

    I need someone help me to connect these devices please 


  4. I THINK the analoge to digital conversion is

    Faulty,and this model  is very old,and there is  difficult  to find  one.

    Regards 


  5. I want to know  if the problem  from analoge inputs unit  .if ok 

    What is expected or is the reason for considering that the unit works after the main cutter and restart it several times


  6. Hello Mr Collin

    i use many inputs to analoge inputs 6ES5 466_3la11, now when the machine was running or stopping, all the inputs to the analoge inputs unit ok.  now for porgram the values is ok when no problem, but when the problem happened the inputs not ok inside porgram, but if you test by tester the inputs ok

    Now in the picture  inside Fb1 mw102 the value 5fb is ok when no problem.but when we faced  problem  the value disappeared..

    ٢٠١٩٠٤٣٠_١٦٣٦٣٥.jpg


  7. Hello  everyone 

    we have plc simatic s5 115u cpu944b and analoge output6es5 466_3la11, suddenly the outputs come to zero we close the machine and open many times.then the outputs come again.  is anyone have any idea about this problem please

    Regards 


  8. Thank you Sir, the problem is that I do not have the password plc and at the same time I have a problem with the output of channel number 3 of the da4a module, as you mentioned, ihave connected the output of the first inverter 0_10 v with the input of the second inverter but when the speed for first inverter increas the output 0_10v decrease, therfor I thought if I connect the same input for tow inverters


  9. 1 hour ago, Nightfly said:

    I am assuming you want to give the same speed reference signal to both inverters. If that is the case, then yes, it is possible. Just set the Inverters up to use 4-20mA as the speed input and wire the 4-20mA in series with both inverters. You can often achieve the same result by feeding the 4-20mA output of one inverter into the 4-20mA input of the other (you can also ratio the speeds this way).

     

     

     

     

     

    Regards

     

     

    Yes sir, this is what I meant but the reference is from 0_10 v, if the parallel is connected, the signal is weak


  10. Hi everyone


    I have PLC delta dvp60es2 ,when I connect with software wplsoft v2.37
    The PLC ask me to write PLC ID
    What plc ID I don't know please help me
    Best regards

     

     

     


  11. I have fxg3 and fx3s Mitsubishi PLC and gx developer software ver.7 ,my question what is the suitable software and cable to connected with pc