Luke.S

MrPLC Member
  • Content count

    110
  • Joined

  • Last visited

Everything posted by Luke.S

  1. Gateway PLC + PC

    Sorry do you mean the A series is already currently connected to a GOT? That must be via serial right? Is that an Fx-3 series? That maybe could replace the A by converting the software to it but it really depends on the complexity of the application. You can definitely get modules including Ethernet for it. If it's Fx-2, that is on the way out but you might still just get modules for it. Does the Q not already have an ethernet port? If not that's easy to add with one of these units:  
  2. CC-link no digital output

    Sorry if this is sounds obvious but I just want to get an idea of where you're at. There's 2 assignments: 1. Assignment of the start IO/ unit no. of the master module to interface with the Q CPU via x or y bits and buffer memory register (in PC Parameter) 2. Assignment of local auto-refresh devices to remote devices  Rww, Rwr, Rx, Ry so you don't need a program to send everything via the buffer memory mentioned above ( in Network->CC-Link Parameters) The module assignment for No.1 will take 32 xy points (2 channels) and this depends on where the module sits in your rack configuration. Above you mention 128 points from 0D00. Does this refer to No.2 the auto refresh assignment? Is this specified for both Rx's and Ry's in your CC-Link settings? What are your cyclic settings for the remote device station? Are enough refresh devices assigned for this? Because no error lights are showing I think your wiring and settings on the remote device are fine. Just one of the above settings aren't quite right, most likely No.2.
  3. Gateway PLC + PC

    Yes. If I couldn't upgrade the A that's what I would do. Connect a GOT 1000 to the A and then you have some options to communicate with Ethernet. Some GOTs can even connect directly to a CC-Link IE fiber network. I would get a GOT2000 model if you can though. GOT1000s are being phased out.
  4. Gateway PLC + PC

    The only fiber networks I know Mitsubishi has that can connect to that gateway PLC is CC-Link IE Control or MELSECNET/H. This should be no problem for the Q. You need CCL-IE or MELSECNET/H network modules on the Q CPU and gateway. Or you can connect straight to a PC with a PCI interface card. The A series is a problem though because it is extremely difficult to get any parts for it now, even second hand. You could use the serial port on the A to send data to the Q which can then be forwarded to the gateway. But the best thing to do would be to upgrade the A to a Q. It's relatively easy to convert the A program so it can be used on a Q and you can support the comms to the gateway. The cost of replacing would probably be small compared to the long downtime you could face if the A stops working.
  5. Please give more details about the configuration of the current system. e.g. How many/type of modules already installed etc.
  6. FX3u Ethernet Card

    You're welcome. I don't know what your application is but this table should help you pick the right one
  7. FX3u Ethernet Card

    The ADP plugs into the left side of the CPU and you access it via special devices (SM/SD) which are detailed in the manual. The ENET is connected to the external bus on the right side and is accessed via buffer memory (e.g. FROM/TO commands). You will need to identify the start I/O number of the module depending on its location on the bus.
  8. GOT 2000 button access

    In the button properties go to the Trigger tab and you can set the switch to only be active when a bit is ON or OFF etc. You can also make it grey out the button when it's not available in the Extended tab -> "set the style.. for a switch in non-operating state."
  9. QJ71E71-100

    Ethernet cable is faulty Melsec communication driver is not installed on the GOT GOT communication settings are incorrect QJ71E71 is not configured correctly as described in manual IP address of GOT is exactly the same as PLC +1 (or +2 or any other number) if there is nothing else on the network. If there are other devices on the network make sure the GOT has a different IP address to all of them and is not using the same port as anything else
  10. need help

    Perhaps I should point out that strictly speaking this topic probably shouldn't be in the Mitsubishi board. But anyway, if you are adjusting the line speed to make each product get enough heating time then maybe you could just average out the current consumption of the heaters over a certain period. That'll give you the average kW usage. A kW just means 1000J/s and  1 kWh =3,600,000 J. So for example if the heater is using an average 1 kW and the product is in the oven 10 seconds at the current line speed then current cost per product is (10,000 J/3,600,000 J)*3.21Rs. You could display it in real time based on real time line speed feedback. Cost_PV=(((oven_length/lineSpeed_PV)*averagekW_PV)/3,600,000)*3.21 If you want it per kg then just divide that cost by the weight of the product. I am assuming that only one product goes through the oven at a time, otherwise it's a bit more complicated but that's the general idea.
  11. Mitsubishi QJ71E71-100 C013 error

    You can see if any ports are already opened there which may be causing conflicts.
  12. need help

    Do you mean 1kWh of electricity to power the heater costs Rs3.21? If it's an electric heater you could measure the current to it with a current transducer on the line, feed that back to the PLC analog input and get a wattage with P=IV. Then if you know the length of the oven you know how long the product was in there: time(s)=length of oven(mm)/speed(mm/s). From that you can get calculate how much of a kWh was used on one product.
  13. Mitsubishi QJ71E71-100 C013 error

    Check the "Open" settings in the Ethernet tab of PC Parameters.
  14. q-series comunnication

    You can do that really easily on the GOT with the logging function. It is on the left tree in GT designer under "Project." You can set it up to sample PLC devices at set intervals or on a one shot etc. and save the log data to files (including CSV which is good for excel). I have done this on physical GOT HMIs but I have never used soft GOT. As its running on a PC I would imagine it can save CSVs directly on the HDD. On the physical GOT you need a USB stick or SD card and to get the data directly on the PC without an "air gap" would require some software implementing MC protocol to communicate with PLC.
  15. EXACT POSITIONING OF SERVO MOTOR

    The "feed current value," "real current value" and "deviation counter value" are probably stored in d0 to d5 + 20n. Where n is the number of the axis -1. (3 32bit values in 6 registers) But I don't know enough about the setup you are using. You need to read through the manuals for your motion controller and look at how it's been configured in the PLC program.
  16. GX Works 3 and Simple Motion

    Do you have it set to display labels and comments in the display settings? I can't spot anything wrong in the screenshots. Maybe have a look at the compiler settings regarding how local labels are handled. Or try calling Mitsubishi support. 
  17. QD70d8 error code 820

    Great that it works. I recommend using SET/RST instead of a timer if you can. When the program gets more complicated and lots of events are going on, it makes it easier to keep track of things and make sure they don't interrupt each other. As you can see in Mitsubishi's example above, M7 gets latched on when it's interlock conditions are met. It stays on until Y18 turns on. That makes sure that another routine couldn't overwrite U1/G52 and maybe cause an accident if some other positioning started when you were expecting a HPR.
  18. GX Works 3 and Simple Motion

    Go to the labels -> M+ labels in the navigation tree on the left. Are module labels registered for the fx5cpu and 40ssc-s? If not then go to the element selection window (probably on the right) and find the modules tab. Right click on the CPU module and MCU modules and select "add labels.." and it should be ok if you recompile everything. Make sure you click the option to register local labels when you add a FB to your ladder as well. Hope that helps.
  19. QD70d8 error code 820

    It looks like the positioning operation fails to start and you are getting error 820 to warn you about that. Under what conditions is M161 reset? From the code you posted above it looks like the RST comes immediately after the positioning start command. In that case it's likely the drive does not have time to respond within one scan of the PLC. The [ZP.PSTRT1 command is turned off before it can complete properly. Try this: *SET M161 *when M161=ON, execute OPR as you are but don't RST M161 yet *RST M161 when M161=ON AND positioningStartOK signal OR positioningStartError signal Also make sure no other commands can be issued to the axis at the same time as M161 is ON. In the programming example, I think X20 is the startOK signal and X18 is the startError signal.   EDIT: Just got a chance to have a proper look at that zp_pstrt instruction and I think the problem is that you MOVP the position no. at the wrong time. Do the MOVP 9001and SET M161 when M160 is pulsed. Then when M161 is ON, execute zp.pstrt and RST   M161. Hope that is more helpful sorry.
  20. When using an auxiliary piece of equipment or a retrofit on, for example, a production line, who's responsibility is it to define the I/O specification between them? The designer of the software in the slave equipment or the administrator of the software in the line master PLC? I am programming a servo system which works in sync with a line. The only input I have to start and stop is an "auto_run" bit from the master. Because there are many possibilities regarding what the servos are doing at any one time and it's over an industrial network, I requested the "Stop," command to be a handshake format. I want to send an acknowledgement back to the master upon actual "zero speed," feedback from the drives. The response was that it is my responsibility to sort it out on my end. I got it to work with just the "auto_run" bit falling edge but I feel like this is the not the most professional way to do it. What if the timing changes or the equipment gets reassigned to a different process in the future? Is it not normal that I require certain I/O to be in a specific format so I can make sure my code is robust? There seems to be a lack of commonly accepted best practice in the PLC field.
  21. drforsythe, thank you for your reply. I suppose I just have to learn from this experience (like with many other things I learnt are harder to change later) and try to get a tentative specification out early on. Even if I don't get any answers, it might get the ball rolling. What makes things tricky for me here is that I'm younger than most of the people I'm working with on this so I have to watch how much I assert myself.
  22. Analog inputs on Mitsubishi plc A series

    I'm pretty sure you need to set the "convertion enable" bits for the channels you are using with a TO command if you haven't already. There should be an example of this program in the manual for that module if you google it.
  23. Positioning Mode (Point Table Methode) Using Servo

    Yes. ~9046 pulses are required to move 1mm. It might not actually work that way though. You might need to tune the drive to improve steady state error, the paper could slip on the roll etc.
  24. Positioning Mode (Point Table Methode) Using Servo

    Yes that is pi π. The circumference of the roll is pi x roll diameter. The circumference = feed of one roll revolution. Sorry if I misunderstand you but do you mean 695.5 is the circumference?  
  25. Positioning Mode (Point Table Methode) Using Servo

    The J4 series have a 22 bit encoder. That's 4,194,304 pulses in one revolution of the motor. The motor rotates 1.5 times for one rotation of the load. That's 6,291,456 pulses. The load has a feed distance per one revolution of 3.14159..x695.5 = 2184.977691mm (assuming you gave us the roller diameter above). Therefore the number of pulses required to feed 1 mm is 6,291,456/2184.977691=2879. Take your target feed value in mm from e.g. HMI and multiply it by 2879 (signed bin32) and send that to the drive.