okaneem

MrPLC Member
  • Content count

    7
  • Joined

  • Last visited

Community Reputation

0 Neutral

About okaneem

  • Rank
    Newbie

Profile Information

  • Country Turkey
  1. scaling?

    Dear PdL, Thank you for function block.I am not able to put a value under 0.When I do it a red line occurs on,the left side.I can only do it on monitoring mode.Also could you mention about FLT function.I process input 2001,which is 0-4000,to floating point and write it to D10.And then I would like to divide it.I use /F D10 D12 D14.It is confusing me here.What should I write to D12 to divide D10 by 10 or an other value I decide.Can you help a little bit to understand.? Thank you so much
  2. scaling?

    Hi Friends I would like to scale an analog input 4-20mA to -100/+100.I have 4000 resolution.I dive 4000 by 200,than I minus 100 from that and put it to D10.when it comes to -(under zero) the value goes to 65426.How can I see the number under 0.Also how can I show floating point.Can some one explain it. Thanks I
  3. da08c problem?

    dear pdl, I solve the problem .It is because the loop tester Now everything is OK Thank you so much for your interest. Best regards
  4. da08c problem?

    I use fluke 179 .I connect it directly to A1-A2. no mAmps. even 4mA is not there.I have done what you said.2000.00 is now 1.
  5. da08c problem?

    I should say that I put +24V to A9 and 0V to B9
  6. da08c problem?

    dear Pdl thanks for reply.I already have done what you said.I use Cx programmer 9.4.I do it using PLC I/O table menu by enabling output channels.I also chack it from PLC,They are all 1,I also move D20000 #FF. What else am I doing wrong?
  7. da08c problem?

    Dear friends, I would like to understand how i can get analog output from cj1w-da08c.you can see my settings below.WhenI try to write 2001(an. output1) nothing happens.I put 4000 decimal to 2001 and the others 2002,2003 etc.is ther anything that ı do wrong.please advice. http://www.yukletr.com/download.php?file=659ab1ae8f909b48980a798aa538503c