bijusi2000

MrPLC Member
  • Content count

    9
  • Joined

  • Last visited

Posts posted by bijusi2000


  1. Hi everyone,

    My plc got a fault, then I power down the PLC => remove the battery => Turn on the PLC until fault led off => Power down the PLC once again => Mount the battery and turn on the PLC. After that, I cannot connect the PLC via either Ethernet or COM port. Please tell me how to factory reset the PLC.

     

    Thanks in advance,


  2. Hi everyone,

    Now I used Micromaster 430 controlled by a PLC. I set parameters as follows:

    P0010: 0 

    P0100: 0

    P0700: 2 (using BOP-2)

    P0701: 1 (start)

    P0702:12

    Terminal 3+4: Connected to Analog output of the PLC 

    Terminal 5: connected to 24V via a relay which is controlled by the PLC

    DIP switch1 on (analog input1 with 0-20mA)

    When I turn on the relay to power to terminal 5, the inverter runs about 5 seconds, then stop automatically while terminal 5 is still powered.

    There are no fault and no alarm. I checked the parameter P0947 and P2110 with value 0.

    Especially, when I set P0700 = 1 (using Start button in Panel), the inverter runs well without stop automatically.

    Please give me some solutions.

     


  3. 14 hours ago, Steve Bailey said:

    I'm sorry, but I don't know what you're asking. I have never used the Siemens HMI, so I can't give any guidance on that. Modbus address 400000 should correspond to PLC address %R00001. Modbus address 100000 should correspond to PLC address %I00001. Modbus address 000000 should correspond to PLC address %Q00001. Modbus address 300000 should correspond to PLC address %AI0001.

    This what I need to know. Thank you so much.


  4. 5 hours ago, Steve Bailey said:

    Go to the GE support site. The "landing page" for the CPUE05 is located here:

    https://ge-ip.force.com/communities/en_US/Article/IC200CPUE05-Landing-Page

    Follow the links to the VersaMax user's manual, GFK-1503E which identifies which signals are carried on which pins (Chapter 4).

    You may need to set up a free user account to get to the manual. 

    Many thanks, I will try and give you feedback after testing.


  5. 7 minutes ago, Steve Bailey said:

    Yes.

    You will need the programming software for the PLC. You have to modify the hardware configuration to configure one of the serial ports as a Modbus RTU slave.

    I will try this method. I would like to set CPUE05 Port 2 (RS-485) as Mobus RTU slave and HMI Siemen KTP600 RS422/RS485 as  Modicon RTU master. Is there any wire connection schematic for this?