[[Template core/front/global/updateWarning is throwing an error. This theme may be out of date. Run the support tool in the AdminCP to restore the default theme.]]
I am tying to connect a PILZ pnoz m1p plc with a Beckhoff CX9020 plc true Ethercat. I have connected a PNOZ mc2.1p ethercat module to the PILZ plc, so there is now connection with the beckhoff plc. Installed the XML to recognize the PILZ in my network = ok
wrote a test program on the PILZ and in twincat3 to test the communication, but this isn't working. The pilz gives a USINT (byte) that i need to convert to bool in my twincat progam. see attachments
i don't see anything changing in my beckhoff PLC, what am i doing wrong? any body have experience with this?
PILZ, beckhoff with ethercat connection, usint to bool
in Other PLCs
Posted · Edited by CarlVW
wasn't done
I am tying to connect a PILZ pnoz m1p plc with a Beckhoff CX9020 plc true Ethercat. I have connected a PNOZ mc2.1p ethercat module to the PILZ plc, so there is now connection with the beckhoff plc. Installed the XML to recognize the PILZ in my network = ok
wrote a test program on the PILZ and in twincat3 to test the communication, but this isn't working. The pilz gives a USINT (byte) that i need to convert to bool in my twincat progam. see attachments
i don't see anything changing in my beckhoff PLC, what am i doing wrong? any body have experience with this?