Siti D
MrPLC Member-
Content count
4 -
Joined
-
Last visited
Posts posted by Siti D
-
-
-
Hi Michael, this is the program that I referred to. There are four subroutines affected while doing the converting.
-
Hi there, I would like to ask you regarding the conversion PLC. Usually, it is not a surprise for us to get the errors occurring for the PLC conversion especially if both PLCs are not in the same compatible programming software. What I mean, currently, we have a lot of older version of PLC such as C20, C40H, C60H etc and these version needed to be converted to the newer version. However, lately we have problem converting the CQM1H to CJ2M, whereas both PLCs using the same programming software, CX-ONE software (ver 9.6).
Most of the errors are displayed like this:
ERROR: Step at rung 161 (6, 1) - SBN not defined - 4
There are 4 errors are listed referring to the same type of errors, that is the SBN not defined.
Is there anyone here ever experienced this? And why is it these two PLCs also got problem for converting? Thanks all.
CONVERT FROM CQM1H TO CJ2M
in CX-Programmer
Posted
Okay I'll check from that. I'll be posted again here later maybe. Thanks again.