lizard

encoder to fx plc

3 posts in this topic

hi all

bit of info needed,I want to wire up an encoder i have to a fx plc.
i believe/ would like to use hs counter c252 where x0 is A encoder output,x1 is B & x2 rest.

the encoder i have came with following details:

Features:
400 p / r (Single-phase 400 pulses / R, Two phase 4 frequency doubling to 1600 pulses)
Power source: DC5-24V
Shaft: 6 * 13mm / 0.23 * 0.51 ″
Size: 38 * 35.5mm / 1.49 * 1.39 ″
Output: AB 2phase output rectangular orthogonal pulse circuit, the output for the NPN open collector output type
Maximum mechanical speed: 5000 R / min
Response frequency: 0-20KHz
Cable length: 1.5 meters
Notice: AB 2phase output must not be directly connected with VCC, otherwise, will burn the output triode because of
different batches, and may not have the terminal
Package included: 1 X Incremental Rotary Encoder

Connection:
Green = A phase, white = B phase, red = Vcc power supply, black = V0


I gather from this that I connect green - x0,white-x1, red to 24v & black/shield to 0v & rest button x2

I also believe as it is npn output  would I connect 0v to the s/s terminal.(sink?)

what i need to know is if i connect 24v to the s/s terminal would this damage the encoder & if all my above assumptions are correct.

Share this post


Link to post
Share on other sites

Hi lizard,

Yes, your 0V would go to the common on the PLC input. This would be NPN.

http://www.plctalk.net/qanda/showthread.php?t=27796
" The S/S terminal is used to configure the unit inputs for sinking or sourcing signals (all at once).
The inputs themselves are polarity-insensitive and S/S is their common.
When the S/S is connected to the logic ground, the inputs react on sourcing signals (PNP sensors).
When it is connected to the logic power (typically +24VDC) the inputs react on sinking signals (NPN sensors). "

Here is the hardware manual:
https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy992d66301/jy992d66301s.pdf

I hope this helps you out.
Regards,
Garry

 

Share this post


Link to post
Share on other sites

Actually putting 0v to the s/s terminal would be for sourcing logic.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now